I would challenge that inspector's assumption.  It starts becoming precedent if you don't.  I have challenged many rulings, and have lived to tell the tale.  There's a process and you just politely go through the process.  Often just mentioning that I will challenge a particular assumption

Re: [RE-wrenches] EG4 Equipment

2024-02-17 Thread Dan Fink via RE-wrenches
Jay - Despite the exceptions in NEC 480.3 and 706.5 for lead-acid not needing to be Listed, and the maximum capacity exception for lead-acid in IFC 1206.2.8.3, one of our local AHJs is now insisting that ALL residential ESS, including lead-acid, even off-grid with no utility interconnect, must be

Re: [RE-wrenches] EG4 Equipment

2024-02-17 Thread Steve Higgins via RE-wrenches
To this point I'm not aware of a lead battery that is compliant to 9540 or 1973...we are still trying to work out the kinks of these UL codes. This what happens when people try to blanket fix a problem with one technology and apply it across the board without a full understanding of the

Re: [RE-wrenches] EG4 Equipment

2024-02-17 Thread jay via RE-wrenches
A number of people have mentioned strict code compliance. How are lead batteries dealing with this? thanks jay > On Feb 17, 2024, at 12:27 PM, Ray Walters via RE-wrenches > wrote: > > Chris; > > I was definitely moving to the LFP camp for off grid for all the same reasons > you

Re: [RE-wrenches] EG4 Equipment

2024-02-17 Thread Steve Higgins via RE-wrenches
Becareful with the EG4s and AGMs. Last I checked the EG4s couldn't be properly programmed to charge at a high enough voltage to properly charge some of the heavier plated AGM. Surrette and Full river AGMs need to be charged at 58.8 temp compensated to -4mv/deg/c... The EG4s like the Sol Arks

Re: [RE-wrenches] EG4 Equipment

2024-02-17 Thread Darryl Thayer via RE-wrenches
I used to be Lead AGM for Off-grid; I used the Pure Lead Thin Plate for an install 4 years ago from AltE, and it is still working fine. I believe the LiFe is the battery for off-grid and the trick is to find the correct BMS, On Sat, Feb 17, 2024 at 11:43 AM Drake Chamberlin via RE-wrenches <

Re: [RE-wrenches] EG4 Equipment

2024-02-17 Thread Ray Walters via RE-wrenches
Chris; I was definitely moving to the LFP camp for off grid for all the same reasons you mentioned, but I've just had too much trouble, so I'm heading back to lead acid for now.  I missed the acid burned jeans, its a "look". Seriously, you mentioned customers coming back to a lead acid

Re: [RE-wrenches] Tigo RSS Off Grid

2024-02-17 Thread Ray Walters via RE-wrenches
I second using the 48v to 12 v DC DC converter.  I've had success with that, and avoided the issues Jeremy mentioned. Ray Walters Remote Solar On 2/17/2024 9:35 AM, Bradley Bassett via RE-wrenches wrote: I powered a MidNite LSOB transmitter from a Classic AUX, though the receivers didn't work

Re: [RE-wrenches] Tigo RSS Off Grid

2024-02-17 Thread bob--- via RE-wrenches
Hi Jeremy... The Classic AUX outputs will put out about 13 volts and allow up to about 200 mA maximum. That might be enough to power the transmitter. That is only about 2.5 watts so might not work directly. boB Docked at Trinidad/Tobago today.  Great sun here.  Have only seen one PV

Re: [RE-wrenches] EG4 Equipment

2024-02-17 Thread William Miller via RE-wrenches
Drake: I prefer the UnigyII VRLA batteries. Full river 2 volt L-16s are pretty good and they allow one string configuration in larger AH settings. I agree that as features grow so does complexity. However there is no substitute for good remote monitoring and control. I can understand much

Re: [RE-wrenches] EG4 Equipment

2024-02-17 Thread Dave Angelini Offgrid Solar via RE-wrenches
Surrette and Full river AGM's Been berry berry good to me! Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2024-02-17 9:43 am, Drake Chamberlin via RE-wrenches wrote: I fully agree that off

Re: [RE-wrenches] EG4 Equipment

2024-02-17 Thread Drake Chamberlin via RE-wrenches
I fully agree that off grid solar has taken a major downturn. Once the equipment became software based, the reliability dropped. Sure, there are nice features available with these cyber enhanced systems, but the cost in reliability makes being energy independent off the grid hard to accomplish.

Re: [RE-wrenches] Tigo RSS Off Grid

2024-02-17 Thread Bradley Bassett via RE-wrenches
I powered a MidNite LSOB transmitter from a Classic AUX, though the receivers didn't work with the Classic. The Classic is limited to 200ma output and the Tigo and APS transmitters are rated at up to 800ma input, so it might overload the Classic AUX output if they really do draw that much. I

Re: [RE-wrenches] EG4 Equipment

2024-02-17 Thread Jay via RE-wrenches
fortress is making improvements to their firmware for sure. The fortress envy 12 has generator warmup/cool down which is a really important feature  IMO. The eg4 not. Nor does the Deye sol ark. JayOn Feb 16, 2024, at 8:48 PM, Chris Sparadeo via RE-wrenches wrote:Howie,The EG4 18K and the

Re: [RE-wrenches] EG4 Equipment

2024-02-17 Thread Jason Szumlanski via RE-wrenches
Beyond the listing issues, there are also the NFPA 855 maximum energy storage limitations to consider that battery manufacturers and distributors are not considering in their marketing, leading consumers to conclusions that won't work. I have a client who purchased three full racks of EG4 LL as a