Hi everyone, Does anyone have positive or negative experience with REC modules? Specifically failure rate, and how the company acts when an RMA is necessary. Thank you David Quattro CA License # 954020. C-10, C-46 ph (415) 312-2661 www.quattrosolar.com

Re: [RE-wrenches] 120 Vac and 12Vdc mixed distribution system

2024-05-03 Thread david quattro via RE-wrenches
I think SolArk makes an 8K 120V-only version David On Fri, May 3, 2024 at 3:13 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > For this application I was originally thinking about a 48V inverter with > 120V output, but there are not many options in the size

Re: [RE-wrenches] Anybody else caught up with the Lumos urgent recall?

2024-04-22 Thread david quattro via RE-wrenches
wow. Sounds like a class action lawsuit if they’re not careful. I’ve never heard of any module manufacturer pay for lost production, but they need to cover parts and labor or they will be sued, and they will lose. ___ List sponsored by Redwood

Re: [RE-wrenches] midnite new inverter

2024-04-10 Thread david quattro via RE-wrenches
OK thanks for the correction. It's confusing to me because the external chassis is identical ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver

Re: [RE-wrenches] midnite new inverter

2024-04-10 Thread david quattro via RE-wrenches
I have not installed an Fortress yet, but I know they are made by Deye (same Chinese original manufacturer as SolArk inverters) Here is a link for an excellent instructional by Steve Higgins @ Rolls - https://www.youtube.com/watch?v=RJqBULN9MgI=ygUWcm9sbHMgc3VycmV0dGUgaGlnZ2lucw%3D%3D This assumes

Re: [RE-wrenches] Plaques

2024-03-30 Thread david quattro via RE-wrenches
Generic stickers are easily gotten but site-specific placards are often required. I recommend Tony ::: Tony Nguyen We send him a PDF doct and the size/font requirements. within a couple days I receive a perfect red placard with white lettering, 3M sticky on the back, at very reasonable pricing.

Re: [RE-wrenches] Enohase tech support

2024-03-15 Thread david quattro via RE-wrenches
Jason, Very helpful. Thank you I wonder why, after years of calling tech support, nobody at Enphase told me the S is a replacement for the R. it took a compatriot installer/integrator to care enough. On Fri, Mar 15, 2024 at 2:51 PM Jason Szumlanski < ja...@floridasolardesigngroup.com> wrote: >

Re: [RE-wrenches] Enohase tech support

2024-03-15 Thread david quattro via RE-wrenches
wow, your experience is worse than anything I've ever heard of from Enphase tech support. My experience with them is this: they know their old Envoys are garbage (the M-Series are failing left and right now). The executives made the decision that they will no longer manufacture new M-Envoys. I

Re: [RE-wrenches] 30% ITC

2024-02-28 Thread david quattro via RE-wrenches
I thought the primary goal of the federal ITC was to address climate change. Thus as a citizen of Earth, increased PV adoption is success regardless of whatever financial implications arise from a taxpayer perspective. ___ List sponsored by

Re: [RE-wrenches] Fwd: Re: $300 + transmission fee!

2024-02-26 Thread david quattro via RE-wrenches
Hi William, I’ve never done this but talked to the electrical/electronic engineer who did:: he took all the CT current, and voltage inputs and ran them into a small cheap Linux PC, which was easy to find support and used a common programming language. These guys only used it for a custom

Re: [RE-wrenches] Fwd: Re: $300 + transmission fee!

2024-02-26 Thread david quattro via RE-wrenches
Jay, there are three major utilities in CA. I don’t know much about LADPW nor SDGE. PGE executes demand charges depending on the ‘rate schedule’ applied to a specific meter. Customers can request to change their rate schedule, sometimes with significant financial savings just doing that.

[RE-wrenches] LG Battery charger instruction

2024-02-20 Thread david quattro via RE-wrenches
Hi Tom, a few years ago I decided to buy my own LG battery charger because we needed the damn thing so often. Now I only use it once or twice per year, because I stopped installing LG batteries. Here is the instruction I have which works on my charger (same charger as the LG-sanctioned :: the

Re: [RE-wrenches] No payment for Sunpower warranty service vendor credits?

2024-02-13 Thread david quattro via RE-wrenches
Yes SolArk can be programmed to sell the battery energy in specific time windows David Quattro CA License # 954020. C-10, C-46 ph (415) 312-2661 www.quattrosolar.com On Tue, Feb 13, 2024 at 3:37 PM Darryl Thayer via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Advice, please; I

Re: [RE-wrenches] Automatic load control

2023-12-15 Thread david quattro via RE-wrenches
SPAN Panel, or you can try Generac 7006 automatic load shed device (100A) https://apelectric.com/generac-7006-smart-management-module/ Or G7000 (50Amp) I’ve heard they work with other inverters, not just GENERAC only, but of course you’d have no warranty when mixing brands. David On Thu, Dec

Re: [RE-wrenches] Radian Question

2023-10-30 Thread david quattro via RE-wrenches
I’m not familiar with Outback defaults but most inverters I’ve dealt with have a grid tolerance of 10% +/- so 216 to 264VAC. On Mon, Oct 30, 2023 at 6:57 AM Drake Chamberlin via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Hi Jay, > > The inverter won't even connect to the grid.

Re: [RE-wrenches] Cleaning PV mods

2023-10-23 Thread david quattro via RE-wrenches
The encapsulant between the glass and the aluminum might be degraded by a surfactant. It’s probably a low risk if you use a gentle soap, but I heard that somewhere about 15 years ago so I thought I’d mention it. I also heard that pressure washers are too strong and can ruin the encapsulant

Re: [RE-wrenches] Line Side Tap

2023-10-13 Thread david quattro via RE-wrenches
Dana in your first example it looks like 120A of solar is pushing onto a 100A utility meter, over #3 copper which cannot handle 120A. But I might be missing something. On Fri, Oct 13, 2023 at 6:29 AM Dana Orzel via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Repost of 2 types of

Re: [RE-wrenches] Line Side Tap

2023-10-12 Thread david quattro via RE-wrenches
Drake I think you’re right and they’re wrong, as long as the 200A bus is protected by a 200A breaker, and as long as the Utility meter and utility conductors remain 400 David On Thu, Oct 12, 2023 at 5:06 PM Drake Chamberlin via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > We have

Re: [RE-wrenches] Fronius USA available 2023 & 2024 ?

2023-08-26 Thread david quattro via RE-wrenches
If you’re dealing with PG Utility, Fronius decided a few years ago not to play along anymore. PGE constantly changes the requirements for the inverter manufacturers, and what they call Smart Inverters. from what I understand this is mostly for solar curtailment when the grid is saturated. I

Re: [RE-wrenches] Hawaiian Tie in

2023-08-08 Thread david quattro via RE-wrenches
Type 1: You’ll be limited to 100A solar because the Utility conductors you’re attaching to are 100A. The Utility tap needs to immediately go to a fused disconnect switch, generally within 6ft (sometimes 10ft) and within line of sight of the meter. Fuses need AIC rating equivalent to that of the

Re: [RE-wrenches] SolarEdge Car Charger

2023-07-25 Thread david quattro via RE-wrenches
I haven’t installed a Solaredge in years so my info might not be up to date, but I remember that the EV Charger units couldn’t be commissioned without an active internet connection. The early models had high failure rate, but that was within the first year or two that they offered the EV

Re: [RE-wrenches] Damaged PV module cells

2023-07-16 Thread david quattro via RE-wrenches
The cells are cracking. The metal traces are victim (not the cause) along the crack lines-- David Quattro CA License # 954020. C-10, C-46 ph (415) 312-2661 www.quattrosolar.com ___ List sponsored by Redwood Alliance Pay optional member dues here:

Re: [RE-wrenches] Lithium battery recommendation

2023-07-13 Thread david quattro via RE-wrenches
SimpliPhi has given me zero problems over about a dozen systems. so far I have only used the 3.8kWh units that are not capable of closed loop communication. On Thu, Jul 13, 2023 at 9:34 PM Carl Hansen via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Peter, > >I've also

Re: [RE-wrenches] LG Chem RESU10H Battery Question

2023-06-30 Thread david quattro via RE-wrenches
Hi David and David, it’s me David Since no lights come on when you turn the breakers on, it sounds like the battery is deeply discharged. I bought a specialized charger for the RESU10H. If you want to borrow it let me know. David Quattro On Fri, Jun 30, 2023 at 10:40 AM Dave Angelini

Re: [RE-wrenches] High current dc combiner vibration

2023-06-30 Thread david quattro via RE-wrenches
Ferrite cores can be used for the battery cables to pass through to reduce common mode current On Fri, Jun 30, 2023 at 3:59 AM Kirk Herander via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I have -15- sets of 4/0 cable (1 per 32 kwh stack) into the combiner. They > are paired and

Re: [RE-wrenches] Remote load shedding

2023-06-27 Thread david quattro via RE-wrenches
GENERAC also makes a 100 amp version of the SMM On Tue, Jun 27, 2023 at 3:12 AM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I'm interested in this also. This is becoming increasingly necessary as we > install "whole home" backup systems, but we need to dump a

Re: [RE-wrenches] Fronius primo fan

2023-06-15 Thread david quattro via RE-wrenches
Hi Jay, in my experience most fans are readily available, you just have to pull the old fan and get a part number from its nameplate. Or you can probably order one from Fronius tech support. Worst case I experienced was on an old SHARP inverter (3 MPPT's), it was supposed to be 3-wire fan, but