Hello Chris,
I think you will find that the generator interaction with the Sol-Ark is
very basic and you won't have much flexibility to do this.
As far as ancillary equipment to do a load start, one idea that comes to
mind is a Victron shunt, Cerbo and GX device. I'm brainstorming a little
bit
I would trigger genset on Soc. Is that what you are doing?
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[2]https://offgridsolar1.com/ [3] [2]
e-mail offgridso...@sti.net
text 209 813 0060
On 2023-09-25 9:20 am, Chris Daum via RE-wrenches wrote:
Hi folks:
We have a
Generators are load responsive. They can not be back feed, one approach is
to take heavy loads and have the inverter drop these loading heav load
situations. bring these loads on line with a PLC
On Mon, Sep 25, 2023 at 11:22 AM Chris Daum via RE-wrenches <
re-wrenches@lists.re-wrenches.org>
Hi folks:
We have a situation where the Sol-Ark 12kW Inverter isn't able to adequately
manage the loads and perform auto-gen start other than low battery level.
And despite thorough understanding of the customer's initial loads, after
he's bought the system, he's continued to add more and