Re: [RE-wrenches] Grid Tied Inverter back feed to Generator

2023-12-02 Thread Jason Szumlanski via RE-wrenches
AC coupling the Enphase IQ8 microinverters with a generator and no batteries is a supported setup with their System Controller 2 or 3G. The "Sunlight Only Backup" system in this configuration starts the generator automatically during a grid outage, but generator power will only be used if the

Re: [RE-wrenches] Grid Tied Inverter back feed to Generator

2023-12-01 Thread Dave Angelini Offgrid Solar via RE-wrenches
Picture tells one alot also. You can't have 2 or more sources without isolation, batteries or not. Cheers! Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://offgridsolar1.com/ [2] [1] e-mail offgridso...@sti.net text 209 813 0060 On 2023-12-01 4:16 pm, Jerry Shafer

Re: [RE-wrenches] Grid Tied Inverter back feed to Generator

2023-12-01 Thread Jerry Shafer via RE-wrenches
Wrenches Without batteries uou do not want to do this, l have tested small generators to excite larger solar inverters to run constant loads but if the inverters out power the loads then the smoke comes out so not advisable But hey thats just a guy that has been in the business for many years. Fun

Re: [RE-wrenches] Grid Tied Inverter back feed to Generator

2023-12-01 Thread Eric Smiley via RE-wrenches
We were called to repair a system where this happened. All the micro inverters were fried and so was the generator. It caused a voltage rise that the monitoring system recorded at 348 V before it went down, when the PV ran the generator as a motor. *Eric Smiley,* Design Manager e...@vecoop.ca

Re: [RE-wrenches] Grid Tied Inverter back feed to Generator

2023-12-01 Thread Dave Tedeyan via RE-wrenches
Jeremy, It is my understanding that if the generator wakes up the grid tied inverter and loads are more than the solar then maybe nothing bad would happen. Although I would never do that because you don't have any control over the loads. And if the solar production is more than the loads, then

[RE-wrenches] Grid Tied Inverter back feed to Generator

2023-11-30 Thread Jeremy Rodriguez via RE-wrenches
Has anyone experienced a grid tie inverter back feed a whole house backup generator after a utility outage? What can happen ? Jeremy Rodriguez Solar Installation / Design All Solar, Inc. 1453 M St. Penrose Colorado 81240 Sent by Jeremy's iPhone. Sorry for typos and shorthand.