Re: [RE-wrenches] Mate3s error vs. event log

2024-04-03 Thread Dave Angelini Offgrid Solar via RE-wrenches
Hi Kirk, It has been a long time since I used Optics and not sure if this will work but here goes. A few years back Schneider came up with a way to hard wire a tablet for a graphic shot of the system that the user does not have to do anything. It is on 24/7. I have a few older clients that

Re: [RE-wrenches] Mate3s error vs. event log

2024-04-03 Thread Steve Higgins via RE-wrenches
The charge parameters depends on the FNDC settings, so yes, it comes from the FNDC but is triggered by the combination of the Mate or Mate3, again depending on the FNDC Settings: There are three "And/Or" Statements.So, to meet charge parameters, you must satisfy the following. Statement 1 End

Re: [RE-wrenches] Mate3s error vs. event log

2024-04-03 Thread Jay via RE-wrenches
2 things. Maybe you can sell them a service contract and clear/check the events 1x week via optics. I don’t know if there is a way to prioritize events. To me Ive always had good success with the fndc in regards to be pretty accurate for reading %. Getting rid of it seems the wrong way to go. And

Re: [RE-wrenches] Mate3s error vs. event log

2024-04-03 Thread Nick A Lucchese via RE-wrenches
Greetings Kirk, It is my understanding that the “charged parms met” comes from the FNDC since that is the component measuring the current and going by those guidelines in the “Battery Setup” menu assigned to the FNDC port. This would seem like a reasonable test and could be done remotely

Re: [RE-wrenches] Mate3s error vs. event log

2024-04-02 Thread Kirk Herander via RE-wrenches
Hi, Are you saying that this "charged parms met" message is actually coming from the Flexnet? I do have a flexnet in this system. The event log states the originating port to be "M", as from the Mate3s itself. On Tue, Apr 2, 2024 at 1:49 AM Nick A Lucchese via RE-wrenches <

Re: [RE-wrenches] Mate3s error vs. event log

2024-04-01 Thread Nick A Lucchese via RE-wrenches
Hello Kirk, Does the client rely on the fully charged indicator anyway? Perhaps defeat some of the settings that will satisfy the targets of the Flexnet? Maybe set the “charged voltage” to something a few volts higher than your absorption set point and/or take the timer all the way up to 240

[RE-wrenches] Mate3s error vs. event log

2024-04-01 Thread Kirk Herander via RE-wrenches
Hello All, I have a customer with a OB Radian GS8048A, grid tied, which logs a "charged parms met" message regularly. When it does, the event log LED on the 3s starts blinking. My customer thinks it's an error, and calls me. I Wish I could somehow defeat this event, and any non-error, from