i like using gutters, it keeps it clean you can just as easily put the gutter vertical on the side and use close nipples….. Max Balchowsky SEE Systems On Wed, Aug 2, 2023 at 8:04 AM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I see a lot of pictures with

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-04 Thread Michael Morningstar via RE-wrenches
I just checked out the Homegrid batteries. Just throwing this out there. If there is enough ceiling height you could hang them. That's typically how we deal with transformers in commercial and industrial settings. We usually build a permanent gantry out of square tubing, 1/2" rod and strut. Then

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-04 Thread Dave Angelini Offgrid Solar via RE-wrenches
Very nice Install Michael! Was that the project on the xxCloud River we talked about? It looks like you have kept the gutter heat gain down to protect electronics. "the rule of thumb is that every 10°C increase in temperature reduces component life by half"

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-04 Thread Jason Szumlanski via RE-wrenches
Michael, I think your work looks stellar, and I seriously doubt there would be any airflow issues. I plan to use strut to put the inverters out from the wall to deal with the working depth issue, which should also help with airflow. That was part of my thought process - even if the inverters

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-04 Thread Michael Morningstar via RE-wrenches
We handle the 15Ks much like most vfds since both have cooling vents in the rear and knockouts or wiring compartments in the rear. What we do is set the units back so that the rear portion is hanging off of the rear of the gutter. The gutter in this case is held off of the wall for air flow. It

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-04 Thread Jason Szumlanski via RE-wrenches
Thanks, Lou. I missed that 6" bottom spacing requirement in the manual. That could explain a lot of the installation pictures I have seen. On the flip side, we have seen some examples of installations in this thread without this 6-inch spacing, presumably without any adverse effects. Obviously,

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-03 Thread Lou Russo via RE-wrenches
Hello All, Super impressive install, Michael. Almost worth a flight, and a site visit! Back to Jason's initial question If you are using the 15kW Outdoor Sol-Ark they vent from the top and bottom with a required 6" minimum spacing on both the top and bottom. A 12kW Outdoor with 8x8 gutter

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-02 Thread Jerry Shafer via RE-wrenches
Jason In plenty of applications l will use couplers with chase nipples, height is one issue but installed working height is very important. I use a 8"x8"x X gutter and sometimes even off set that from the wall, l have had AHJ not want to see mixed cables LVDC and AC in the same conduit so pass

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-02 Thread Maverick Brown via RE-wrenches
Jason The old Sol-Ark had the PV disconnect and the Wi-Fi adapter connection on the bottom and that needed about six or 8 inches of clearance. The current Sol-Ark has those items on the side of the unit so you don’t need such clearance on the bottom. I installed several Sol-Ark and I use the

[RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-02 Thread Jason Szumlanski via RE-wrenches
I see a lot of pictures with conduit nipples coming out of a gutter that are fairly long. I have a height limit issue and I'm wondering if there are any negative implications of using very short nipples between a wireway below and the inverter. I'm thinking about using close nipples or perhaps