Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-17 Thread penobscotsolar
Ron,
   I'm going to reiterate what Jeff says here. It is similar to what I had
said in my email. The charge rate must REGULARLY be C10 on the KS 
(5000 series) batteries. This means, on KS 25's, a routine bulk
charging rate of 135 amps. I find that on these types of hybrid
systems, while the batteries might occasionally (sunny day, generator
running, etc.) that kind of charging, they do not regularly see C10. I
think if you gave Jamie Surrette a call he would give you the same
possible assessment.
   I do think the problem is oversulfation, but none of this solves your
problem, I know. We have been installing KS series batteries since they
came out and this necessity of regular C10 charging has been an
integral  part of design for me for many years.

Best,
Daryl




 Ron,



 This reply a little late since I have been off line a few days.  I
 mentioned
 in a similar thread last year that I had an off grid home client I
 designed
 and installed in Idaho back in 1998 that had a Kohler 8.5 kw generator, a
 Trace 4024 inverter, two separate solar arrays and Outback charge
 controllers, and 16 Trojan L-16 batteries.  This system worked
 flawlessly
 for 7 years and only required the generator a few hours per month, then it
 was time to change the batteries.  I replaced the Trojans with the same
 size
 battery made by Surrette and everything went to crap.  They had to run the
 generator hours and hours to get them past an 80% charge and we had lots
 of
 problems with overloading the generator even though we did not make any
 program changes and used the same generator.  The generator was replaced 2
 years later but this system  never worked like it did before the battery
 replacement.



 When researching all this at that time I had talked with Surrette, Trojan,
 and anyone else that might help and this is what I found out.  Of course
 there are just my opinions based on these conversations, but it is my
 understanding that Surrette is a much longer life battery with much less
 water loss when comparing apples and apples, and I was told this was due
 to
 a different lead composition that Surrette uses than any other battery
 manufacturer.  However, this difference requires a much longer
 absorption/taper off charge process or you will never get it past 80%
 charged.  This of course is almost impossible to achieve with a generator
 or
 undersized solar array, and you really need a grid connection to fully
 charge these things.  No doubt these would be great in some standby grid
 connected system but I no longer use them in off grid.  This was also at a
 time when battery manufacturers were just discovering solar so maybe
 battery
 designs have changed.  Again, I think Surrette is a good company and makes
 a
 great battery, but just not sure you can fully recharge them with a
 mid-sized generator.



 I also do not like using parallel battery layouts as its hard to keep one
 string from pulling down the other strings when there is a low performance
 cell so you might do a cell by cell check.



 Good Luck,



 Jeff Yago

 DTI Solar Inc.



 
 
 
 ---

 This is not what I expected after a lengthy EQ. I'm getting them to do
 another one tomorrow after a discharge cycle and charge but I'm really
 beginning to think we have something else going on here, something
 electrical, not chemical. The rapid voltage drop is puzzling.



 To review, it's an Outback 3524 on an Epanel, Whisper 100  controller, 6
 4KS 25 Surrette batteries in 24v configuration - 4.5 years old, .7kw
 solar.
 I know the charging end is undersized but they have been compensating with
 the generator and they get lots of wind in the fall, winter, spring.



 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-17 Thread Richard L Ratico
Todd,

I asked Surrette about their lead calcium batteries this morning, right after
reading your post. Here's their reply:

I'm afraid our flooded calcium line is not yet available. Product testing  went
very well but at this time our present high demand for our other product lines
has prevented us from moving forward on this new product line. At this time
there is no estimated production date for a flooded calcium line.

Bummer.

Dick Ratico
Solarwind Electric
 



--- You wrote:
I digress but... the best battery for grid tie with backup is not lead antimony,
but lead calcuum. Surrette makes these too and they use next to no water and
have a much longer warrantied life.
 
Todd
 
 
 
On Wednesday, November 16, 2011 6:52pm, Jeff Yago jry...@dtisolar.com said:


 
 No doubt these would be great in some standby grid connected system but I no
longer use them in off grid.  This was also at a time when battery manufacturers
were just discovering solar so maybe battery designs have changed. 


Sent from Finest Planet WebMail.

--- end of quote ---
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-17 Thread Mark Frye
Todd,
 
I thought you were totally off-grid. 
 
Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 http://www.berkeleysolar.com/ www.berkeleysolar.com  
 

  _  

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
toddc...@finestplanet.com
Sent: Thursday, November 17, 2011 12:25 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] intermittent battery problem; ...Battery
Sulfation


wow, thanks for the information. hopefully they will have them in production
in 20 years when my current beta set finally dies. cd and others make em,
but they are more expensive.

 

todd

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-17 Thread toddcory

Hi Mark,
 
I have been grid tied (zero energy since 2004) for 15 years. I used to live off 
grid before I moved here to this home 17 years ago.
 
Todd
 
 
 
On Thursday, November 17, 2011 12:36pm, Mark Frye ma...@berkeleysolar.com 
said:



Todd,
 
I thought you were totally  off-grid. 
  
Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 [http://www.berkeleysolar.com/] www.berkeleysolar.com 


From: re-wrenches-boun...@lists.re-wrenches.org  
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of 
toddc...@finestplanet.com
Sent: Thursday, November 17, 2011 12:25  PM
To: RE-wrenches
Subject: Re: [RE-wrenches] intermittent  battery problem; ...Battery Sulfation

wow,  thanks for the information. hopefully they will have them in production 
in 20  years when my current beta set finally dies. cd and others make em, 
but  they are more expensive.
 
todd


Sent from Finest Planet WebMail.
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-16 Thread Ron Young
Hi Larry, no amp hour meter installed yet as the customer is penny pinching. 
We're trying to solve the problem first and I've been out there twice, once to 
do general diagnostics and check all connections, try to load test the 
batteries, and so on; the second time I 'dropped in' to try a different load 
test on the batteries to see if I could replicate the problem and to resolve 
some other problems with a Whisper controller that had given up the ghost when 
disconnected  re-connected to the batteries (all precautions taken). It's a 
seven hour round trip and with time spent on the job makes for an expensive 
service call. I only charged for one call and I have to go back at least once 
more. So customer wanted to save some money on the installation of the 
TriMetric until the spring... sorry for the long winded reply. I know, it's 
false economy. So I'm thinking I'll just put the meter in and tell them to pay 
me when they feel like it. It'll help solve the problem and get some of the 
Wrenches off my back ... ;-)

Ron Young

On 2011-11-13, at 8:26 AM, la...@starlightsolar.com 
la...@starlightsolar.com wrote:

 Ron,
 I stick by my evaluation as seen here: 
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/msg10694.html
 
 The #1 reason for my opinion is that you can NOT drive up voltage on a 
 healthy bank that size in just 5 minutes. It is impossible with a 2500 watt 
 generator.
 
 Here is the pertinent part from my post:
 You mentioned that the the battery drops to 24.5 in the early AM without any 
 heavy loads on. For the 4KS25 battery this equates to about 800AH at the 72 
 hour rate. Then you said that the customer ran a 2500 watt generator for 5 
 minutes and drove the voltage up to 29 volts. Here's the Ah-Ha moment: That 
 is EXACTLY the behavior of a heavily sulfated battery bank. A fast rise in 
 voltage indicates sulfation. It is impossible for that tiny generator, or any 
 charge source they own for that matter, to replace the hundreds of AH it 
 would take to drive a healthy battery up to the absorb voltage of 29 volts. 
 The bank is about 45,000 watt hours (72h rate). There would have to be over 
 20,000 Wh removed to be at that voltage. How many Wh's are replaced in 5 
 minutes by a 2500 watt genny? I'm sure you are getting the picture. 
 
 Also, why have you not installed a battery monitor yet? It will give you 
 eyes into the battery and spare countless hours of time diagnosing the 
 problem.
 
 Larry
 
  Original Message 
 Subject: Re: [RE-wrenches] intermittent battery problem; ...Battery
 Sulfation
 From: Ron Young solarea...@solareagle.com
 Date: Sat, November 12, 2011 9:57 pm
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 
 Folks, this one really has me puzzled. The client has done regular two hour 
 EQ's, at least once a month. When did a site visit and I topped up the 
 electrolyte (they'd been starving the batteries for water but always just 
 above the plates) the problem seemed to go away. They were satisfied that the 
 problem was solved but I wasn't and I told them what I had been hearing from 
 this group - essentially that the batteries needed a deep EQ, discharge, 
 recharge and EQ again two or three times to scrub the sulphates. They 
 declined until just a few days ago when they said the rapid voltage drop was 
 back. Here's a quote:
 
 We had another rapid voltage loss this morning ---it was 25.2 when we got up 
 and it dropped rapidly to 22.8.  We turned on the generator and charged the 
 batteries until our display showed 30.2  for awhile with the generator 
 running.  We turned off the generator and the voltage settled at about 26.4.  
 We turned off all loads and wind and solar.
   
 At 9.15 our batteries were at 26.4
 At 9:16 we turned on an 8W light bulb, a1600W hair dryer, and a 1.5HP (120V 
 5.75A) shop vac
 The display showed a load of 1.9kw
 At 9:40 the inverter shut down---display showed batteries at 18.4
 By 9.47 the display showed the batteries at 25.2the solar and wind were 
 still shut down.
 We turned everything back on (a light, Sunfrost RF16, phone)  and all seems 
 to be normal.
 
 They agreed to do the EQ process but only have a 3kw generator so we started 
 with 8 hours with the EQ voltage set for 32v (24v system). They completed 
 that yesterday and here's what resulted:
 
 Before starting EQ the batteries were at 25.8, hydrometer reading 1283 with 
 temp. correction
 Began EQ32.6 v
  Buying 1.5 kw
 Hour 1  32.4 v
 1283  with temp. correction   Buying  1.4
 Hour 2  32.4 v
   1285  with temp. correction  Buying 1.5
 Hour 3  32.2 v

Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-16 Thread Ron Young
Hi Daryl. I've got other KS25's in hybrid systems (wind gen  solar) that seem 
to do fine over the last several years. The Ouback 3524 has an 85 amp charger.  
There was no problem getting to 32 v and holding it for eight hours. This has 
been done twice now.  Larry and others attribute the ability to get to 32v to a 
sulphated battery condition and I'm thinking that a healthy battery could get 
to 32v as well, especially one that's been regularly EQ'd... am I wrong?

I'm listening to every opinion here and trying to sort it out but I think John 
may be on the right track with an intermittent failure of one cell. I just 
can't seem to find it.

Ron Young

On 2011-11-13, at 3:51 AM, penobscotso...@midmaine.com wrote:

 Ron,
  What comes to mind for me is that Surrette 5000 series batteries like
 to have a regular charge of C10.  KS25 cells are rated for 1350 ah,
 creating a need for a somewhat regularly occurring charge of 135 amps.
 I do believe the batteries are not ever getting that, except for very
 rare occasions. We have seen this before in undersized systems.
  Is the bulk charge set to 29.6? I would try a couple more eq's over the
 next month to loosen likely sulfation. Get it up to as close to 32
 volts as possible and taper the charge down, then eq at that voltage
 for four or five hours, even more if the client will do it.
  That would be how we would deal with this. It does seem ultimately to
 be sulfation that is the problem.
 
 Daryl DeJoy
 NABCEP Certified PV installer
 Penobscot Solar Design
 
 
 
 
 Folks, this one really has me puzzled. The client has done regular two
 hour EQ's, at least once a month. When did a site visit and I topped up
 the electrolyte (they'd been starving the batteries for water but always
 just above the plates) the problem seemed to go away. They were satisfied
 that the problem was solved but I wasn't and I told them what I had been
 hearing from this group - essentially that the batteries needed a deep EQ,
 discharge, recharge and EQ again two or three times to scrub the
 sulphates. They declined until just a few days ago when they said the
 rapid voltage drop was back. Here's a quote:
 
 We had another rapid voltage loss this morning ---it was 25.2 when we got
 up and it dropped rapidly to 22.8.  We turned on the generator and charged
 the batteries until our display showed 30.2  for awhile with the generator
 running.  We turned off the generator and the voltage settled at about
 26.4.  We turned off all loads and wind and solar.
 
 At 9.15 our batteries were at 26.4
 At 9:16 we turned on an 8W light bulb, a1600W hair dryer, and a 1.5HP
 (120V 5.75A) shop vac
 The display showed a load of 1.9kw
 At 9:40 the inverter shut down---display showed batteries at 18.4
 By 9.47 the display showed the batteries at 25.2the solar and wind
 were still shut down.
 We turned everything back on (a light, Sunfrost RF16, phone)  and all
 seems to be normal.
 
 They agreed to do the EQ process but only have a 3kw generator so we
 started with 8 hours with the EQ voltage set for 32v (24v system). They
 completed that yesterday and here's what resulted:
 
 Before starting EQ the batteries were at 25.8, hydrometer reading 1283
 with temp. correction
 Began EQ32.6 v
  Buying 
 1.5 kw
 Hour 1  32.4 v
  1283  with temp. correction   Buying  1.4
 Hour 2  32.4 v
1285  with temp. correction  Buying 1.5
 Hour 3  32.2 v
  
 Buying 1.7
 Hour 4  32.2 v
1290  with temp correctionBuying 1.8
 HOur 5 32.0 v
   1290   with temp correctionBuying 1.8
 Hour 6  32.0 v
  Buying 
 1.9
 Hour 7  31.8 v
 1292 with temp correctonBuying 1.9
 Hour 8 complete---turned off Gen and turned on loads ---Batteries dropped
 to 25.4 within 30 minutes and stayed there until this morning---fridge was
 running, telephone, internet, wool carding machine, lights.  This morning
 hydrometer reading  was at 1290.
 
 
 
 Then today I just got this email:
 
 Just experienced another rapid voltage drop.  As soon as the voltage hits
 24.8 the voltage drops like a rock if we don't have any input (no solar or
 wind).
 
 This is not what I expected after a lengthy EQ. I'm getting them to do
 another one tomorrow after a discharge cycle and charge but I'm really
 beginning to think we have something else going on here, something
 electrical, not 

Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-16 Thread Larry Crutcher, Starlight Solar Power Systems
We are only on your back until you to do the advisable thing: Sell them a 
battery capacity monitor. It is a hard fact that NO off grid, battery based 
power system should be without a battery capacity monitor. They are cheap (only 
$150!) and not an option. Apparently, it is also hard learned fact. ;-)

Larry Crutcher
Starlight Solar Power Systems




On Nov 16, 2011, at 12:20 AM, Ron Young wrote:

 Hi Larry, no amp hour meter installed yet as the customer is penny pinching. 
 We're trying to solve the problem first and I've been out there twice, once 
 to do general diagnostics and check all connections, try to load test the 
 batteries, and so on; the second time I 'dropped in' to try a different load 
 test on the batteries to see if I could replicate the problem and to resolve 
 some other problems with a Whisper controller that had given up the ghost 
 when disconnected  re-connected to the batteries (all precautions taken). 
 It's a seven hour round trip and with time spent on the job makes for an 
 expensive service call. I only charged for one call and I have to go back at 
 least once more. So customer wanted to save some money on the installation of 
 the TriMetric until the spring... sorry for the long winded reply. I know, 
 it's false economy. So I'm thinking I'll just put the meter in and tell them 
 to pay me when they feel like it. It'll help solve the problem and get some 
 of the Wrenches off my back ... ;-)
 
 Ron Young
 
 On 2011-11-13, at 8:26 AM, la...@starlightsolar.com 
 la...@starlightsolar.com wrote:
 
 Ron,
 I stick by my evaluation as seen here: 
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/msg10694.html
 
 The #1 reason for my opinion is that you can NOT drive up voltage on a 
 healthy bank that size in just 5 minutes. It is impossible with a 2500 watt 
 generator.
 
 Here is the pertinent part from my post:
 You mentioned that the the battery drops to 24.5 in the early AM without any 
 heavy loads on. For the 4KS25 battery this equates to about 800AH at the 72 
 hour rate. Then you said that the customer ran a 2500 watt generator for 5 
 minutes and drove the voltage up to 29 volts. Here's the Ah-Ha moment: That 
 is EXACTLY the behavior of a heavily sulfated battery bank. A fast rise in 
 voltage indicates sulfation. It is impossible for that tiny generator, or 
 any charge source they own for that matter, to replace the hundreds of AH it 
 would take to drive a healthy battery up to the absorb voltage of 29 volts. 
 The bank is about 45,000 watt hours (72h rate). There would have to be over 
 20,000 Wh removed to be at that voltage. How many Wh's are replaced in 5 
 minutes by a 2500 watt genny? I'm sure you are getting the picture. 
 
 Also, why have you not installed a battery monitor yet? It will give you 
 eyes into the battery and spare countless hours of time diagnosing the 
 problem.
 
 Larry
 
  Original Message 
 Subject: Re: [RE-wrenches] intermittent battery problem; ...Battery
 Sulfation
 From: Ron Young solarea...@solareagle.com
 Date: Sat, November 12, 2011 9:57 pm
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 
 Folks, this one really has me puzzled. The client has done regular two hour 
 EQ's, at least once a month. When did a site visit and I topped up the 
 electrolyte (they'd been starving the batteries for water but always just 
 above the plates) the problem seemed to go away. They were satisfied that 
 the problem was solved but I wasn't and I told them what I had been hearing 
 from this group - essentially that the batteries needed a deep EQ, 
 discharge, recharge and EQ again two or three times to scrub the sulphates. 
 They declined until just a few days ago when they said the rapid voltage 
 drop was back. Here's a quote:
 
 We had another rapid voltage loss this morning ---it was 25.2 when we got up 
 and it dropped rapidly to 22.8.  We turned on the generator and charged the 
 batteries until our display showed 30.2  for awhile with the generator 
 running.  We turned off the generator and the voltage settled at about 26.4. 
  We turned off all loads and wind and solar.
   
 At 9.15 our batteries were at 26.4
 At 9:16 we turned on an 8W light bulb, a1600W hair dryer, and a 1.5HP (120V 
 5.75A) shop vac
 The display showed a load of 1.9kw
 At 9:40 the inverter shut down---display showed batteries at 18.4
 By 9.47 the display showed the batteries at 25.2the solar and wind were 
 still shut down.
 We turned everything back on (a light, Sunfrost RF16, phone)  and all seems 
 to be normal.
 
 They agreed to do the EQ process but only have a 3kw generator so we started 
 with 8 hours with the EQ voltage set for 32v (24v system). They completed 
 that yesterday and here's what resulted:
 
 Before starting EQ the batteries were at 25.8, hydrometer reading 1283 with 
 temp. correction
 Began EQ32.6 v

Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-16 Thread Larry Crutcher, Starlight Solar Power Systems
Ron, you have misquoted me so yes you are wrong. It is not about getting to 32 
volts. Go read it again.

On Nov 16, 2011, at 12:20 AM, Ron Young wrote:

 Hi Daryl. I've got other KS25's in hybrid systems (wind gen  solar) that 
 seem to do fine over the last several years. The Ouback 3524 has an 85 amp 
 charger.  There was no problem getting to 32 v and holding it for eight 
 hours. This has been done twice now.  Larry and others attribute the ability 
 to get to 32v to a sulphated battery condition and I'm thinking that a 
 healthy battery could get to 32v as well, especially one that's been 
 regularly EQ'd... am I wrong?
 
 I'm listening to every opinion here and trying to sort it out but I think 
 John may be on the right track with an intermittent failure of one cell. I 
 just can't seem to find it.
 
 Ron Young
 
 On 2011-11-13, at 3:51 AM, penobscotso...@midmaine.com wrote:
 
 Ron,
 What comes to mind for me is that Surrette 5000 series batteries like
 to have a regular charge of C10.  KS25 cells are rated for 1350 ah,
 creating a need for a somewhat regularly occurring charge of 135 amps.
 I do believe the batteries are not ever getting that, except for very
 rare occasions. We have seen this before in undersized systems.
 Is the bulk charge set to 29.6? I would try a couple more eq's over the
 next month to loosen likely sulfation. Get it up to as close to 32
 volts as possible and taper the charge down, then eq at that voltage
 for four or five hours, even more if the client will do it.
 That would be how we would deal with this. It does seem ultimately to
 be sulfation that is the problem.
 
 Daryl DeJoy
 NABCEP Certified PV installer
 Penobscot Solar Design
 
 
 
 
 Folks, this one really has me puzzled. The client has done regular two
 hour EQ's, at least once a month. When did a site visit and I topped up
 the electrolyte (they'd been starving the batteries for water but always
 just above the plates) the problem seemed to go away. They were satisfied
 that the problem was solved but I wasn't and I told them what I had been
 hearing from this group - essentially that the batteries needed a deep EQ,
 discharge, recharge and EQ again two or three times to scrub the
 sulphates. They declined until just a few days ago when they said the
 rapid voltage drop was back. Here's a quote:
 
 We had another rapid voltage loss this morning ---it was 25.2 when we got
 up and it dropped rapidly to 22.8.  We turned on the generator and charged
 the batteries until our display showed 30.2  for awhile with the generator
 running.  We turned off the generator and the voltage settled at about
 26.4.  We turned off all loads and wind and solar.
 
 At 9.15 our batteries were at 26.4
 At 9:16 we turned on an 8W light bulb, a1600W hair dryer, and a 1.5HP
 (120V 5.75A) shop vac
 The display showed a load of 1.9kw
 At 9:40 the inverter shut down---display showed batteries at 18.4
 By 9.47 the display showed the batteries at 25.2the solar and wind
 were still shut down.
 We turned everything back on (a light, Sunfrost RF16, phone)  and all
 seems to be normal.
 
 They agreed to do the EQ process but only have a 3kw generator so we
 started with 8 hours with the EQ voltage set for 32v (24v system). They
 completed that yesterday and here's what resulted:
 
 Before starting EQ the batteries were at 25.8, hydrometer reading 1283
 with temp. correction
 Began EQ32.6 v
 Buying 
 1.5 kw
 Hour 1  32.4 v
 1283  with temp. correction   Buying  1.4
 Hour 2  32.4 v
   1285  with temp. correction  Buying 1.5
 Hour 3  32.2 v
 
 Buying 1.7
 Hour 4  32.2 v
   1290  with temp correctionBuying 1.8
 HOur 5 32.0 v
  1290   with temp correctionBuying 1.8
 Hour 6  32.0 v
 Buying 
 1.9
 Hour 7  31.8 v
1292 with temp correctonBuying 1.9
 Hour 8 complete---turned off Gen and turned on loads ---Batteries dropped
 to 25.4 within 30 minutes and stayed there until this morning---fridge was
 running, telephone, internet, wool carding machine, lights.  This morning
 hydrometer reading  was at 1290.
 
 
 
 Then today I just got this email:
 
 Just experienced another rapid voltage drop.  As soon as the voltage hits
 24.8 the voltage drops like a rock if we don't have any input (no solar or
 wind).
 
 This is not what I expected after a lengthy EQ. I'm getting them to 

Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-16 Thread Ron Young
You're correct Larry, my apologies. Been burning the candle at both ends. 
Thanks for your input.

On 2011-11-16, at 9:04 AM, Larry Crutcher, Starlight Solar Power Systems wrote:

 Ron, you have misquoted me so yes you are wrong. It is not about getting to 
 32 volts. Go read it again.
 
 On Nov 16, 2011, at 12:20 AM, Ron Young wrote:
 
 Hi Daryl. I've got other KS25's in hybrid systems (wind gen  solar) that 
 seem to do fine over the last several years. The Ouback 3524 has an 85 amp 
 charger.  There was no problem getting to 32 v and holding it for eight 
 hours. This has been done twice now.  Larry and others attribute the ability 
 to get to 32v to a sulphated battery condition and I'm thinking that a 
 healthy battery could get to 32v as well, especially one that's been 
 regularly EQ'd... am I wrong?
 
 I'm listening to every opinion here and trying to sort it out but I think 
 John may be on the right track with an intermittent failure of one cell. I 
 just can't seem to find it.
 
 Ron Young
 
 On 2011-11-13, at 3:51 AM, penobscotso...@midmaine.com wrote:
 
 Ron,
 What comes to mind for me is that Surrette 5000 series batteries like
 to have a regular charge of C10.  KS25 cells are rated for 1350 ah,
 creating a need for a somewhat regularly occurring charge of 135 amps.
 I do believe the batteries are not ever getting that, except for very
 rare occasions. We have seen this before in undersized systems.
 Is the bulk charge set to 29.6? I would try a couple more eq's over the
 next month to loosen likely sulfation. Get it up to as close to 32
 volts as possible and taper the charge down, then eq at that voltage
 for four or five hours, even more if the client will do it.
 That would be how we would deal with this. It does seem ultimately to
 be sulfation that is the problem.
 
 Daryl DeJoy
 NABCEP Certified PV installer
 Penobscot Solar Design
 
 
 
 
 Folks, this one really has me puzzled. The client has done regular two
 hour EQ's, at least once a month. When did a site visit and I topped up
 the electrolyte (they'd been starving the batteries for water but always
 just above the plates) the problem seemed to go away. They were satisfied
 that the problem was solved but I wasn't and I told them what I had been
 hearing from this group - essentially that the batteries needed a deep EQ,
 discharge, recharge and EQ again two or three times to scrub the
 sulphates. They declined until just a few days ago when they said the
 rapid voltage drop was back. Here's a quote:
 
 We had another rapid voltage loss this morning ---it was 25.2 when we got
 up and it dropped rapidly to 22.8.  We turned on the generator and charged
 the batteries until our display showed 30.2  for awhile with the generator
 running.  We turned off the generator and the voltage settled at about
 26.4.  We turned off all loads and wind and solar.
 
 At 9.15 our batteries were at 26.4
 At 9:16 we turned on an 8W light bulb, a1600W hair dryer, and a 1.5HP
 (120V 5.75A) shop vac
 The display showed a load of 1.9kw
 At 9:40 the inverter shut down---display showed batteries at 18.4
 By 9.47 the display showed the batteries at 25.2the solar and wind
 were still shut down.
 We turned everything back on (a light, Sunfrost RF16, phone)  and all
 seems to be normal.
 
 They agreed to do the EQ process but only have a 3kw generator so we
 started with 8 hours with the EQ voltage set for 32v (24v system). They
 completed that yesterday and here's what resulted:
 
 Before starting EQ the batteries were at 25.8, hydrometer reading 1283
 with temp. correction
 Began EQ32.6 v
Buying 
 1.5 kw
 Hour 1  32.4 v
1283  with temp. correction   Buying  1.4
 Hour 2  32.4 v
  1285  with temp. correction  Buying 1.5
 Hour 3  32.2 v

 Buying 1.7
 Hour 4  32.2 v
  1290  with temp correctionBuying 1.8
 HOur 5 32.0 v
 1290   with temp correctionBuying 1.8
 Hour 6  32.0 v
Buying 
 1.9
 Hour 7  31.8 v
   1292 with temp correctonBuying 1.9
 Hour 8 complete---turned off Gen and turned on loads ---Batteries dropped
 to 25.4 within 30 minutes and stayed there until this morning---fridge was
 running, telephone, internet, wool carding machine, lights.  This morning
 hydrometer reading  was at 1290.
 
 
 
 Then today I just got this email:
 
 Just experienced another rapid voltage drop.  As 

Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-16 Thread Jeff Yago
Ron,

 

This reply a little late since I have been off line a few days.  I mentioned
in a similar thread last year that I had an off grid home client I designed
and installed in Idaho back in 1998 that had a Kohler 8.5 kw generator, a
Trace 4024 inverter, two separate solar arrays and Outback charge
controllers, and 16 Trojan L-16 batteries.  This system worked flawlessly
for 7 years and only required the generator a few hours per month, then it
was time to change the batteries.  I replaced the Trojans with the same size
battery made by Surrette and everything went to crap.  They had to run the
generator hours and hours to get them past an 80% charge and we had lots of
problems with overloading the generator even though we did not make any
program changes and used the same generator.  The generator was replaced 2
years later but this system  never worked like it did before the battery
replacement.

 

When researching all this at that time I had talked with Surrette, Trojan,
and anyone else that might help and this is what I found out.  Of course
there are just my opinions based on these conversations, but it is my
understanding that Surrette is a much longer life battery with much less
water loss when comparing apples and apples, and I was told this was due to
a different lead composition that Surrette uses than any other battery
manufacturer.  However, this difference requires a much longer
absorption/taper off charge process or you will never get it past 80%
charged.  This of course is almost impossible to achieve with a generator or
undersized solar array, and you really need a grid connection to fully
charge these things.  No doubt these would be great in some standby grid
connected system but I no longer use them in off grid.  This was also at a
time when battery manufacturers were just discovering solar so maybe battery
designs have changed.  Again, I think Surrette is a good company and makes a
great battery, but just not sure you can fully recharge them with a
mid-sized generator.

 

I also do not like using parallel battery layouts as its hard to keep one
string from pulling down the other strings when there is a low performance
cell so you might do a cell by cell check.

 

Good Luck,

 

Jeff Yago

DTI Solar Inc.

 




---

This is not what I expected after a lengthy EQ. I'm getting them to do
another one tomorrow after a discharge cycle and charge but I'm really
beginning to think we have something else going on here, something
electrical, not chemical. The rapid voltage drop is puzzling. 

 

To review, it's an Outback 3524 on an Epanel, Whisper 100  controller, 6
4KS 25 Surrette batteries in 24v configuration - 4.5 years old, .7kw solar.
I know the charging end is undersized but they have been compensating with
the generator and they get lots of wind in the fall, winter, spring.

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-16 Thread toddcory

I digress but... the best battery for grid tie with backup is not lead 
antimony, but lead calcuum. Surrette makes these too and they use next to no 
water and have a much longer warrantied life.
 
Todd
 
 
 
On Wednesday, November 16, 2011 6:52pm, Jeff Yago jry...@dtisolar.com said:


 
 No doubt these would be great in some standby grid connected system but I no 
longer use them in off grid.  This was also at a time when battery 
manufacturers were just discovering solar so maybe battery designs have 
changed. 


Sent from Finest Planet WebMail.
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-14 Thread penobscotsolar
Ron,
   What comes to mind for me is that Surrette 5000 series batteries like
to have a regular charge of C10.  KS25 cells are rated for 1350 ah,
creating a need for a somewhat regularly occurring charge of 135 amps.
I do believe the batteries are not ever getting that, except for very
rare occasions. We have seen this before in undersized systems.
   Is the bulk charge set to 29.6? I would try a couple more eq's over the
next month to loosen likely sulfation. Get it up to as close to 32
volts as possible and taper the charge down, then eq at that voltage
for four or five hours, even more if the client will do it.
   That would be how we would deal with this. It does seem ultimately to
be sulfation that is the problem.

Daryl DeJoy
NABCEP Certified PV installer
Penobscot Solar Design




 Folks, this one really has me puzzled. The client has done regular two
 hour EQ's, at least once a month. When did a site visit and I topped up
 the electrolyte (they'd been starving the batteries for water but always
 just above the plates) the problem seemed to go away. They were satisfied
 that the problem was solved but I wasn't and I told them what I had been
 hearing from this group - essentially that the batteries needed a deep EQ,
 discharge, recharge and EQ again two or three times to scrub the
 sulphates. They declined until just a few days ago when they said the
 rapid voltage drop was back. Here's a quote:

 We had another rapid voltage loss this morning ---it was 25.2 when we got
 up and it dropped rapidly to 22.8.  We turned on the generator and charged
 the batteries until our display showed 30.2  for awhile with the generator
 running.  We turned off the generator and the voltage settled at about
 26.4.  We turned off all loads and wind and solar.

 At 9.15 our batteries were at 26.4
 At 9:16 we turned on an 8W light bulb, a1600W hair dryer, and a 1.5HP
 (120V 5.75A) shop vac
 The display showed a load of 1.9kw
 At 9:40 the inverter shut down---display showed batteries at 18.4
 By 9.47 the display showed the batteries at 25.2the solar and wind
 were still shut down.
 We turned everything back on (a light, Sunfrost RF16, phone)  and all
 seems to be normal.

 They agreed to do the EQ process but only have a 3kw generator so we
 started with 8 hours with the EQ voltage set for 32v (24v system). They
 completed that yesterday and here's what resulted:

 Before starting EQ the batteries were at 25.8, hydrometer reading 1283
 with temp. correction
 Began EQ32.6 v
   Buying 
 1.5 kw
 Hour 1  32.4 v
1283  with temp. correction   Buying  1.4
 Hour 2  32.4 v
  1285  with temp. correction  Buying 1.5
 Hour 3  32.2 v
   
 Buying 1.7
 Hour 4  32.2 v
  1290  with temp correctionBuying 1.8
 HOur 5 32.0 v
 1290   with temp correctionBuying 1.8
 Hour 6  32.0 v
   Buying 
 1.9
 Hour 7  31.8 v
   1292 with temp correctonBuying 1.9
 Hour 8 complete---turned off Gen and turned on loads ---Batteries dropped
 to 25.4 within 30 minutes and stayed there until this morning---fridge was
 running, telephone, internet, wool carding machine, lights.  This morning
 hydrometer reading  was at 1290.



 Then today I just got this email:

 Just experienced another rapid voltage drop.  As soon as the voltage hits
 24.8 the voltage drops like a rock if we don't have any input (no solar or
 wind).

 This is not what I expected after a lengthy EQ. I'm getting them to do
 another one tomorrow after a discharge cycle and charge but I'm really
 beginning to think we have something else going on here, something
 electrical, not chemical. The rapid voltage drop is puzzling.

 To review, it's an Outback 3524 on an Epanel, Whisper 100  controller, 6
 4KS 25 Surrette batteries in 24v configuration - 4.5 years old, .7kw
 solar. I know the charging end is undersized but they have been
 compensating with the generator and they get lots of wind in the fall,
 winter, spring.

 Any more thoughts on this anyone?

 Best Regards,
 Ron Young
 earthRight Products - Solareagle.com
 Alternative Energy Solutions ~ Renewable Energy Products


 On 2011-10-24, at 6:50 AM, Larry Crutcher, Starlight Solar Power Systems
 wrote:

 Hi Ron,
 Accurate SG readings are not simple. Was temperature compensation
 properly employed? Have they been keeping a log book to identify
 

Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-13 Thread jay peltz
Hi Ron,

Here is what I would do.

1. install a amp hr meter
without this you have no idea of what is going in/out.  So when they mention 
the batteries drop rapidly to 22.8, they can now see how many amps are going 
out.
2. record voltages to 2 decimal places of each battery when these anomalies 
occur.

3. record amps into battery when doing eq/charge

and I agree with John,

Jay
Peltz Power


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-13 Thread larry
Ron, I stick by my evaluation as seen here: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/msg10694.htmlThe #1 reason for my opinion is that you can NOT drive up voltage on a healthy bank that size in just 5 minutes. It is impossible with a 2500 watt generator. Here is the pertinent part from my post:You mentioned that the the battery drops to 24.5 in the early AM without any 
heavy loads on. For the 4KS25 battery this equates to about 800AH at the 72 
hour rate. Then you said that the customer ran a 2500 watt generator for 5 
minutes and drove the voltage up to 29 volts. Here's the Ah-Ha moment: That is 
EXACTLY the behavior of a heavily sulfated battery bank. A fast rise in voltage 
indicates sulfation.  It is impossible for that tiny generator, or any charge 
source they own for that matter, to replace the hundreds of AH it would take to 
drive a healthy battery up to the absorb voltage of 29 volts. The bank is about 
45,000 watt hours (72h rate). There would have to be over 20,000 Wh removed to 
be at that voltage. How many Wh's are replaced in 5 minutes by a 2500 watt 
genny? I'm sure you are getting the picture. Also, why have you not installed a battery monitor yet? It will give you "eyes" into the battery and spare countless hours of time diagnosing the problem.Larry


 Original Message 
Subject: Re: [RE-wrenches] intermittent battery problem; ...Battery
Sulfation
From: Ron Young solarea...@solareagle.com
Date: Sat, November 12, 2011 9:57 pm
To: RE-wrenches re-wrenches@lists.re-wrenches.org

Folks, this one really has me puzzled. The client has done regular two hour EQ's, at least once a month. When did a site visit and I topped up the electrolyte (they'd been starving the batteries for water but always just above the plates) the problem seemed to go away. They were satisfied that the problem was solved but I wasn't and I told them what I had been hearing from this group - essentially that the batteries needed a deep EQ, discharge, recharge and EQ again two or three times to scrub the sulphates. They declined until just a few days ago when they said the rapid voltage drop was back. Here's a quote:We had another rapid voltage loss this morning ---it was 25.2 when we got up and it dropped rapidly to 22.8. We turned on the generator and charged the batteries until our display showed 30.2 for awhile with the generator running. We turned off the generator and the voltage settled at about 26.4. We turned off all loads and wind and solar.At 9.15 our batteries were at 26.4At 9:16 we turned on an 8W light bulb, a1600W hair dryer, and a 1.5HP (120V 5.75A) shop vacThe display showed a load of 1.9kwAt 9:40 the inverter shut down---display showed batteries at 18.4By 9.47 the display showed the batteries at 25.2the solar and wind were still shut down.We turned everything back on (a light, Sunfrost RF16, phone) and all seems to be normal.They agreed to do the EQ process but only have a 3kw generator so we started with 8 hours with the EQ voltage set for 32v (24v system). They completed that yesterday and here's what resulted:Before starting EQ the batteries were at 25.8, hydrometer reading 1283 with temp. correctionBegan EQ  32.6 v Buying 1.5 kwHour 1 32.4 v  1283 with temp. correctionBuying 1.4Hour 2 32.4 v   1285 with temp. correction   Buying 1.5Hour 3 32.2 v Buying 1.7Hour 4 32.2 v   1290 with temp correctionBuying 1.8HOur 5 32.0 v   1290  with temp correctionBuying 1.8Hour 6 32.0 v Buying 1.9Hour 7 31.8 v1292 with temp correctonBuying 1.9Hour 8 complete---turned off Gen and turned on loads ---Batteries dropped to 25.4 within 30 minutes and stayed there until this morning---fridge was running, telephone, internet, wool carding machine, lights. This morning hydrometer reading was at 1290. Then today I just got this email:Just experienced another rapid voltage drop. As soon as the voltage hits 24.8 the voltage drops like a rock if we don't have any input (no solar or wind).This is not what I expected after a lengthy EQ. I'm getting them to do another one tomorrow after a discharge cycle and charge but I'm really beginning to think we have something else going on here, something electrical, not chemical. The rapid voltage drop is puzzling.To review, it's an Outback 3524 on an Epanel, Whisper 100  controller, 6 4KS 25 Surrette batteries in 24v configuration - 4.5 years old, .7kw solar. I know the charging end is undersized but they have been compensating with the generator and they get lots of wind in the fall, winter, spring.Any more thoughts on this anyone?Best Regards,Ron YoungearthRigh

Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-11-12 Thread Ron Young
Folks, this one really has me puzzled. The client has done regular two hour 
EQ's, at least once a month. When did a site visit and I topped up the 
electrolyte (they'd been starving the batteries for water but always just above 
the plates) the problem seemed to go away. They were satisfied that the problem 
was solved but I wasn't and I told them what I had been hearing from this group 
- essentially that the batteries needed a deep EQ, discharge, recharge and EQ 
again two or three times to scrub the sulphates. They declined until just a few 
days ago when they said the rapid voltage drop was back. Here's a quote:

We had another rapid voltage loss this morning ---it was 25.2 when we got up 
and it dropped rapidly to 22.8.  We turned on the generator and charged the 
batteries until our display showed 30.2  for awhile with the generator running. 
 We turned off the generator and the voltage settled at about 26.4.  We turned 
off all loads and wind and solar.
  
At 9.15 our batteries were at 26.4
At 9:16 we turned on an 8W light bulb, a1600W hair dryer, and a 1.5HP (120V 
5.75A) shop vac
The display showed a load of 1.9kw
At 9:40 the inverter shut down---display showed batteries at 18.4
By 9.47 the display showed the batteries at 25.2the solar and wind were 
still shut down.
We turned everything back on (a light, Sunfrost RF16, phone)  and all seems to 
be normal.

They agreed to do the EQ process but only have a 3kw generator so we started 
with 8 hours with the EQ voltage set for 32v (24v system). They completed that 
yesterday and here's what resulted:

Before starting EQ the batteries were at 25.8, hydrometer reading 1283 with 
temp. correction
Began EQ32.6 v  
Buying 1.5 kw
Hour 1  32.4 v  
  1283  with temp. correction   Buying  1.4
Hour 2  32.4 v  
1285  with temp. correction  Buying 1.5
Hour 3  32.2 v  
Buying 
1.7
Hour 4  32.2 v  
1290  with temp correctionBuying 1.8
HOur 5 32.0 v   
   1290   with temp correctionBuying 1.8 
Hour 6  32.0 v  
Buying 1.9 
Hour 7  31.8 v  
 1292 with temp correctonBuying 1.9
Hour 8 complete---turned off Gen and turned on loads ---Batteries dropped to 
25.4 within 30 minutes and stayed there until this morning---fridge was 
running, telephone, internet, wool carding machine, lights.  This morning 
hydrometer reading  was at 1290.
 


Then today I just got this email:

Just experienced another rapid voltage drop.  As soon as the voltage hits 24.8 
the voltage drops like a rock if we don't have any input (no solar or wind).

This is not what I expected after a lengthy EQ. I'm getting them to do another 
one tomorrow after a discharge cycle and charge but I'm really beginning to 
think we have something else going on here, something electrical, not chemical. 
The rapid voltage drop is puzzling. 

To review, it's an Outback 3524 on an Epanel, Whisper 100  controller, 6 4KS 
25 Surrette batteries in 24v configuration - 4.5 years old, .7kw solar. I know 
the charging end is undersized but they have been compensating with the 
generator and they get lots of wind in the fall, winter, spring.

Any more thoughts on this anyone?

Best Regards,
Ron Young
earthRight Products - Solareagle.com
Alternative Energy Solutions ~ Renewable Energy Products


On 2011-10-24, at 6:50 AM, Larry Crutcher, Starlight Solar Power Systems wrote:

 Hi Ron,
 Accurate SG readings are not simple. Was temperature compensation properly 
 employed? Have they been keeping a log book to identify changes? How accurate 
 is the hydrometer? How skilled is the person taking the reading? 
 
 Most of the Battery Wrench responses suggest equalization but I don't see 
 from any of your posts that this has been done yet. I suggest this to be the 
 next step and I recommend that you carefully watch voltage and current. This 
 will tell you a lot. I use a Fluke ScopeMeter in the TrendPlot mode and track 
 voltage and current over time. It provides a good visual understanding.
 
 In case others are using this forum to glean information, attached is a chart 
 for illustration of the charge cycle. You should see a constant, somewhat 
 linear rise in voltage until the constant voltage setting is reached. If you 
 see a sudden rise: 

Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-10-24 Thread Ron Young
Hi Larry,

I immediately assumed sulphated battery when I heard the customers description 
a couple of weeks ago but the hydrometer readings didn't jive. Any sulphated 
battery I've encountered, and I defer to your greater experience, has always 
revealed itself with a simple S.G. test and these batteries were reading above 
1.265. I then thought the possibility of a defective hydrometer and had them 
test with another but we just got confirmation of the same thing. 

The weird drop in voltage also isn't explained by your description. Why would 
this just happen without loads or charging present (except maybe the DC 
Sunfrost load) at the same predictable time at 4 a.m. The fact that when the 
generator was turned on and sent a surge of current into the system and the 
problem went away made the detective in me think there had to be another 
explanation. The bank was at rest for several hours through the night and the 
voltage dropout was cured by a brief application of charge current. 

When I arrived on site my discovery that the client was under watering the 
batteries and this chronic condition resulted in a very rich electrolyte, 
reading well above 1.265 - into the 1.280 range made me think that was the 
problem and it seems to have gone away now that the electrolyte level was 
raised and the batteries given a good charge. But it still nags at me that 
something else is lurking in the shadows. Your description of the sulphate 
converting to a crystalline form has me worried because if this is the case 
this expensive battery bank is in danger. I would have to camp out at the site 
and monitor the charging over a day or so. I'm going to forward some of your 
comments and those of others that have generously offered suggestions and we'll 
see if I can convince the client who now believes everything is A-Ok.

Best Regards,
Ron Young
earthRight Products - Solareagle.com
Alternative Energy Solutions ~ Renewable Energy Products

On 2011-10-22, at 12:06 PM, Larry Crutcher, Starlight Solar Power Systems wrote:

 Hi Ron,
 
 As many on this list have suggested, it sounds like a sulfated battery 
 condition. In your last message you revealed something to me that absolutely 
 confirms this but perhaps you didn't recognize it. 
 
 Battery voltage readings are deceiving because they do not indicate capacity. 
 25.7 volts sounds like a fully charged 24 volt bank, but is it? Only if the 
 battery was at rest for 5-6 hours could you have some confidence that the 
 bank was full at this voltage. But this is not the case because the bank is 
 in daily use, always charging or discharging. However, there is one useful 
 indication that voltage can be used for: detecting a sulfated battery. 
 
 You mentioned that the the battery drops to 24.5 in the early AM without any 
 heavy loads on. For the 4KS25 battery this equates to about 800AH at the 72 
 hour rate. Then you said that the customer ran a 2500 watt generator for 5 
 minutes and drove the voltage up to 29 volts. Here's the Ah-Ha moment: That 
 is EXACTLY the behavior of a heavily sulfated battery bank. A fast rise in 
 voltage indicates sulfation.  It is impossible for that tiny generator, or 
 any charge source they own for that matter, to replace the hundreds of AH it 
 would take to drive a healthy battery up to the absorb voltage of 29 volts. 
 The bank is about 45,000 watt hours (72h rate). There would have to be over 
 20,000 Wh removed to be at that voltage. How many Wh's are replaced in 5 
 minutes by a 2500 watt genny? I'm sure you are getting the picture. 
 
 Why did this happen to these expensive batteries? Glad you asked. Battery 
 plates are not uniformly efficient in the electrochemical process leaving 
 some portions with lead sulfate even after 8 hours of charging. Unless these 
 portions are cleared off regularly by achieving 100% SoC and occasional, 
 thorough equalization, the amorphous sulfate will convert to a crystalline 
 form and grow. 99% charge, if not corrected in time, will always cause 
 premature battery failure. 
 
 Undersized RE charging systems, or perhaps oversized batteries, is the 
 culprit that contributes to this all too frequent phenomenon of chronic 
 undercharging. I say contribute because there are other factors. Fact: it can 
 take 10-12 hours to fully charge a lead acid battery. Fact: The time element 
 of battery charging is a highly misunderstood part. With only a few daily 
 sun-hours to work with, how do we get a battery charged with PV solar? 
 Properly sizing the PV array to the battery AND consumption is critical. One 
 method I think is essential for nearly all PV systems is use a generator and 
 charger, appropriately sized to the battery. By bulk charging early in the AM 
 you can reduce the finish time to perhaps 5-6 hours of constant voltage 
 charging, something easily done with a PV system.
 
 Ron, you might be able to recover some capacity in this bank if the sulfate 
 has not formed hard crystals by now. 

Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-10-24 Thread Allan Sindelar
Ron,
You have made a connection that I would not have made, and while I may be
wrong here, it has got me thinking. I have never equated low water level
with SG, nor have I ever read in battery maintenance guides that I should
maintain a particular water level before measuring SG. I'm not convinced
that electrolyte level has any connection with measured SG, although it
would seem logical on the surface. I have always thought that if the correct
concentration of acid was installed at the factory and not lost thereafter
(such as due to a spill or chronic overfilling), the SC is only a function
of SOC. I'm interested in others' opinions here.

Allan
Positive Energy

On Mon, Oct 24, 2011 at 1:49 AM, Ron Young solarea...@solareagle.comwrote:

 Hi Larry,

 I immediately assumed sulphated battery when I heard the customers
 description a couple of weeks ago but the hydrometer readings didn't jive.
 Any sulphated battery I've encountered, and I defer to your greater
 experience, has always revealed itself with a simple S.G. test and these
 batteries were reading above 1.265. I then thought the possibility of a
 defective hydrometer and had them test with another but we just got
 confirmation of the same thing.

 The weird drop in voltage also isn't explained by your description. Why
 would this just happen without loads or charging present (except maybe the
 DC Sunfrost load) at the same predictable time at 4 a.m. The fact that when
 the generator was turned on and sent a surge of current into the system and
 the problem went away made the detective in me think there had to be another
 explanation. The bank was at rest for several hours through the night and
 the voltage dropout was cured by a brief application of charge current.

 When I arrived on site my discovery that the client was under watering the
 batteries and this chronic condition resulted in a very rich electrolyte,
 reading well above 1.265 - into the 1.280 range made me think that was the
 problem and it seems to have gone away now that the electrolyte level was
 raised and the batteries given a good charge. But it still nags at me that
 something else is lurking in the shadows. Your description of the sulphate
 converting to a crystalline form has me worried because if this is the case
 this expensive battery bank is in danger. I would have to camp out at the
 site and monitor the charging over a day or so. I'm going to forward some of
 your comments and those of others that have generously offered suggestions
 and we'll see if I can convince the client who now believes everything is
 A-Ok.

 Best Regards,
 *Ron Young*
 earthRight Products - Solareagle.com
 Alternative Energy Solutions ~ Renewable Energy Products

 On 2011-10-22, at 12:06 PM, Larry Crutcher, Starlight Solar Power Systems
 wrote:

 Hi Ron,

 As many on this list have suggested, it sounds like a sulfated battery
 condition. In your last message you revealed something to me that absolutely
 confirms this but perhaps you didn't recognize it.

 Battery voltage readings are deceiving because they do not indicate
 capacity. 25.7 volts sounds like a fully charged 24 volt bank, but is it?
 Only if the battery was at rest for 5-6 hours could you have some confidence
 that the bank was full at this voltage. But this is not the case because the
 bank is in daily use, always charging or discharging. However, there is one
 useful indication that voltage can be used for: detecting a sulfated
 battery.

 You mentioned that the the battery drops to 24.5 in the early AM without
 any heavy loads on. For the 4KS25 battery this equates to about 800AH at the
 72 hour rate. Then you said that the customer ran a 2500 watt generator for
 5 minutes and drove the voltage up to 29 volts. Here's the Ah-Ha moment:
 That is EXACTLY the behavior of a heavily sulfated battery bank. A fast rise
 in voltage indicates sulfation.  It is impossible for that tiny generator,
 or any charge source they own for that matter, to replace the hundreds of AH
 it would take to drive a healthy battery up to the absorb voltage of 29
 volts. The bank is about 45,000 watt hours (72h rate). There would have to
 be over 20,000 Wh removed to be at that voltage. How many Wh's are replaced
 in 5 minutes by a 2500 watt genny? I'm sure you are getting the picture.

 Why did this happen to these expensive batteries? Glad you asked. Battery
 plates are not uniformly efficient in the electrochemical process leaving
 some portions with lead sulfate even after 8 hours of charging. Unless these
 portions are cleared off regularly by achieving 100% SoC and occasional,
 thorough equalization, the amorphous sulfate will convert to a crystalline
 form and grow. 99% charge, if not corrected in time, will always cause
 premature battery failure.

 Undersized RE charging systems, or perhaps oversized batteries, is the
 culprit that contributes to this all too frequent phenomenon of chronic
 undercharging. I say contribute because there are other 

Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-10-24 Thread Maverick Brown [Maverick Solar]
Ron,

Sorry to beat a dead horse, but a Pentametric will reveal what happens at 4am 
(or any other time). At a minimum all you need is the sending unit, 2-3 shunts 
and the serial converter. You then use your laptop to download and analyze what 
happened in the past few days, etc. of course, the display unit can show the 
customer details as well. 

The Pentametric can also monitor SOC and has a relay that can start the 
generator or turn on a Start the Genny Now indicator.

As for sulfated batteries, I think SG will be higher with less water in the 
batteries for a given state of charge. That's just my gut talking not some 
advanced Molarity vs SG vs concentration calculation that I can vaguely 
remember doing.

The bottom line, you still don't know if the customer will bounce another 
energy check since they are not keeping a check register to know the daily 
balance. 

Thank you,

Maverick


Maverick Brown
BSEET, NABCEP Certified Solar PV Installer ®
President  CEO
Maverick Solar Enterprises, Inc.
Office: 512-919-4493
Cell:512-460-9825

Sent from an iPhone. 

On Oct 24, 2011, at 2:49 AM, Ron Young solarea...@solareagle.com wrote:

 Hi Larry,
 
 I immediately assumed sulphated battery when I heard the customers 
 description a couple of weeks ago but the hydrometer readings didn't jive. 
 Any sulphated battery I've encountered, and I defer to your greater 
 experience, has always revealed itself with a simple S.G. test and these 
 batteries were reading above 1.265. I then thought the possibility of a 
 defective hydrometer and had them test with another but we just got 
 confirmation of the same thing. 
 
 The weird drop in voltage also isn't explained by your description. Why would 
 this just happen without loads or charging present (except maybe the DC 
 Sunfrost load) at the same predictable time at 4 a.m. The fact that when the 
 generator was turned on and sent a surge of current into the system and the 
 problem went away made the detective in me think there had to be another 
 explanation. The bank was at rest for several hours through the night and the 
 voltage dropout was cured by a brief application of charge current. 
 
 When I arrived on site my discovery that the client was under watering the 
 batteries and this chronic condition resulted in a very rich electrolyte, 
 reading well above 1.265 - into the 1.280 range made me think that was the 
 problem and it seems to have gone away now that the electrolyte level was 
 raised and the batteries given a good charge. But it still nags at me that 
 something else is lurking in the shadows. Your description of the sulphate 
 converting to a crystalline form has me worried because if this is the case 
 this expensive battery bank is in danger. I would have to camp out at the 
 site and monitor the charging over a day or so. I'm going to forward some of 
 your comments and those of others that have generously offered suggestions 
 and we'll see if I can convince the client who now believes everything is 
 A-Ok.
 
 Best Regards,
 Ron Young
 earthRight Products - Solareagle.com
 Alternative Energy Solutions ~ Renewable Energy Products
 
 On 2011-10-22, at 12:06 PM, Larry Crutcher, Starlight Solar Power Systems 
 wrote:
 
 Hi Ron,
 
 As many on this list have suggested, it sounds like a sulfated battery 
 condition. In your last message you revealed something to me that absolutely 
 confirms this but perhaps you didn't recognize it. 
 
 Battery voltage readings are deceiving because they do not indicate 
 capacity. 25.7 volts sounds like a fully charged 24 volt bank, but is it? 
 Only if the battery was at rest for 5-6 hours could you have some confidence 
 that the bank was full at this voltage. But this is not the case because the 
 bank is in daily use, always charging or discharging. However, there is one 
 useful indication that voltage can be used for: detecting a sulfated 
 battery. 
 
 You mentioned that the the battery drops to 24.5 in the early AM without any 
 heavy loads on. For the 4KS25 battery this equates to about 800AH at the 72 
 hour rate. Then you said that the customer ran a 2500 watt generator for 5 
 minutes and drove the voltage up to 29 volts. Here's the Ah-Ha moment: That 
 is EXACTLY the behavior of a heavily sulfated battery bank. A fast rise in 
 voltage indicates sulfation.  It is impossible for that tiny generator, or 
 any charge source they own for that matter, to replace the hundreds of AH it 
 would take to drive a healthy battery up to the absorb voltage of 29 volts. 
 The bank is about 45,000 watt hours (72h rate). There would have to be over 
 20,000 Wh removed to be at that voltage. How many Wh's are replaced in 5 
 minutes by a 2500 watt genny? I'm sure you are getting the picture. 
 
 Why did this happen to these expensive batteries? Glad you asked. Battery 
 plates are not uniformly efficient in the electrochemical process leaving 
 some portions with lead sulfate even after 8 hours of 

Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-10-24 Thread Exeltech
There are yet other issues to consider relative to specific gravity.

#1:
I believe temperature has been mentioned already, but merits revisiting:

Specific gravity varies somewhat with the temperature of the electrolyte.  Some 
of the
more sophisticated measurement equipment takes temperature into account.  Lower
cost models don't.  However, temperature can be included in your calculations 
by use
of a simple thermometer to measure approximate battery temperature at the time
the SG readings are taken, then factored into the readings.  Cold batteries 
will yield
higher SG readings than warm ones.


#2:
Another concern is stratification.  Acid is more dense than water and thus 
sinks to
the bottom of the battery.  For more accurate readings, electrolyte must be 
stirred
to thoroughly re-mix the solution *before* samples are taken for SG measurement.
Given the construction of batteries, this is difficult (but not impossible) to 
do.  Failing
that, and using just an initial sample of electrolyte from the top of a cell, 
SG readings
from the top may be lower than actual values.

Jamie Surrette recommends adding distilled water to bring the electrolyte level 
up
to the manufacturer's recommended level, then charging the battery to a point of
light-to-moderate outgassing (with all precautions, of course) for a couple of 
hours.
After the battery has rested for as long as possible (24 hours suggested), 
*then*
take a SG reading.  Hydrogen and oxygen get trapped in the electrolyte and will
cause errors in any SG readings taken immediately after such a charging period.

Since this is an off-grid home, one option might be to charge with the generator
as late into the evening as possible, then take SG readings the next morning
before any significant loads are applied.  May be a Friday night/Saturday AM
event if the owner works during the week.


Dan


--- On Mon, 10/24/11, Allan Sindelar al...@positiveenergysolar.com wrote:

From: Allan Sindelar al...@positiveenergysolar.com
Subject: Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Date: Monday, October 24, 2011, 5:35 AM

Ron,You have made a connection that I would not have made, and while I may be 
wrong here, it has got me thinking. I have never equated low water level with 
SG, nor have I ever read in battery maintenance guides that I should maintain a 
particular water level before measuring SG. I'm not convinced that electrolyte 
level has any connection with measured SG, although it would seem logical on 
the surface. I have always thought that if the correct concentration of acid 
was installed at the factory and not lost thereafter (such as due to a spill or 
chronic overfilling), the SC is only a function of SOC. I'm interested in 
others' opinions here.

AllanPositive Energy
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-10-24 Thread Larry Crutcher, Starlight Solar Power Systems
Hi Ron,Accurate SG readings are not simple. Was temperature compensation properly employed? Have they been keeping a log book to identify changes? How accurate is the hydrometer? How skilled is the person taking the reading?Most of the Battery Wrench responses suggest equalization but I don't see from any of your posts that this has been done yet. I suggest this to be the next step and I recommend that you carefully watch voltage and current. This will tell you a lot. I use a Fluke ScopeMeter in the TrendPlot mode and track voltage and current over time. It provides a good visual understanding.In case others are using this forum to glean information, attached is a chart for illustration of the charge cycle. You should see a constant, somewhat linear rise in voltage until the constant voltage setting is reached. If you see a sudden rise: suspect sulfation. If you see a quick reduction in current: suspect sulfation. The current should drop to about 8-10 amps at the constant voltage towards the end of charge cycle. The health and DoD will determine the time this takes, expect many hours. Begin equalization.
A couple other points: Is the MX absorb voltage at 29.6V? Did you program the MX controller for an extended absorb time (advanced menu, absorb time limits)? The default setting is poor for large batteries. I use 90 minutes minimum and 4 hours max. This can greatly reduce the possibility of undercharging the battery but it may use more water. The timer (ChgT) will determine how long it stays in absorb each day.Larry CrutcherStarlight Solar Power Systems
On Oct 24, 2011, at 12:49 AM, Ron Young wrote:Hi Larry,I immediately assumed sulphated battery when I heard the customers description a couple of weeks ago but the hydrometer readings didn't jive. Any sulphated battery I've encountered, and I defer to your greater experience, has always revealed itself with a simple S.G. test and these batteries were reading above 1.265. I then thought the possibility of a defective hydrometer and had them test with another but we just got confirmation of the same thing.The weird drop in voltage also isn't explained by your description. Why would this just happen without loads or charging present (except maybe the DC Sunfrost load) at the same predictable time at 4 a.m. The fact that when the generator was turned on and sent a surge of current into the system and the problem went away made the detective in me think there had to be another explanation. The bank was at rest for several hours through the night and the voltage dropout was cured by a brief application of charge current.When I arrived on site my discovery that the client was under watering the batteries and this chronic condition resulted in a very rich electrolyte, reading well above 1.265 - into the 1.280 range made me think that was the problem and it seems to have gone away now that the electrolyte level was raised and the batteries given a good charge. But it still nags at me that something else is lurking in the shadows. Your description of the sulphate converting to a crystalline form has me worried because if this is the case this expensive battery bank is in danger. I would have to camp out at the site and monitor the charging over a day or so. I'm going to forward some of your comments and those of others that have generously offered suggestions and we'll see if I can convince the client who now believes everything is A-Ok.Best Regards,Ron YoungearthRight Products - Solareagle.comAlternative Energy Solutions ~ Renewable Energy Products___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-10-23 Thread Darryl Thayer
Thanks Larry, this is one of the best explanations I have seen.  I am saving it 
for my customers and students.  I would emphasize the C/20 (as you said) or a 
little less for perhaps C/30 for this long term equalize or desulfation. Too 
fast an equaliziation can loosen (blow the plate material off the plates) .  (I 
built a 60 hZ desulfator and have used it twice in 40 years, it seems to work)  
 
Thanks again great piece of writing and explanation, everyone should read
Darryl



From: Larry Crutcher, Starlight Solar Power Systems la...@starlightsolar.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Saturday, October 22, 2011 2:06 PM
Subject: Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation


Hi Ron,

As many on this list have suggested, it sounds like a sulfated battery 
condition. In your last message you revealed something to me that absolutely 
confirms this but perhaps you didn't recognize it. 

Battery voltage readings are deceiving because they do not indicate capacity. 
25.7 volts sounds like a fully charged 24 volt bank, but is it? Only if the 
battery was at rest for 5-6 hours could you have some confidence that the bank 
was full at this voltage. But this is not the case because the bank is in daily 
use, always charging or discharging. However, there is one useful indication 
that voltage can be used for: detecting a sulfated battery. 

You mentioned that the the battery drops to 24.5 in the early AM without any 
heavy loads on. For the 4KS25 battery this equates to about 800AH at the 72 
hour rate. Then you said that the customer ran a 2500 watt generator for 5 
minutes and drove the voltage up to 29 volts. Here's the Ah-Ha moment: That is 
EXACTLY the behavior of a heavily sulfated battery bank. A fast rise in voltage 
indicates sulfation.  It is impossible for that tiny generator, or any charge 
source they own for that matter, to replace the hundreds of AH it would take to 
drive a healthy battery up to the absorb voltage of 29 volts. The bank is about 
45,000 watt hours (72h rate). There would have to be over 20,000 Wh removed to 
be at that voltage. How many Wh's are replaced in 5 minutes by a 2500 watt 
genny? I'm sure you are getting the picture. 

Why did this happen to these expensive batteries? Glad you asked. Battery 
plates are not uniformly efficient in the electrochemical process leaving some 
portions with lead sulfate even after 8 hours of charging. Unless these 
portions are cleared off regularly by achieving 100% SoC and occasional, 
thorough equalization, the amorphous sulfate will convert to a crystalline 
form and grow. 99% charge, if not corrected in time, will always cause 
premature battery failure. 

Undersized RE charging systems, or perhaps oversized batteries, is the culprit 
that contributes to this all too frequent phenomenon of chronic undercharging. 
I say contribute because there are other factors. Fact: it can take 10-12 hours 
to fully charge a lead acid battery. Fact: The time element of battery charging 
is a highly misunderstood part. With only a few daily sun-hours to work with, 
how do we get a battery charged with PV solar? Properly sizing the PV array to 
the battery AND consumption is critical. One method I think is essential for 
nearly all PV systems is use a generator and charger, appropriately sized to 
the battery. By bulk charging early in the AM you can reduce the finish time to 
perhaps 5-6 hours of constant voltage charging, something easily done with a PV 
system.

Ron, you might be able to recover some capacity in this bank if the sulfate has 
not formed hard crystals by now. You can try a very long charge time, up to 24 
hours, at high voltage, about 31 volts. You will need a larger generator. 
Monitor the temperature and reduce current if they get up to 125F internal. In 
our shop I have recovered sulfated batteries with high voltage charging, as 
much as 3Vpc (do not do this with any loads connected), at reduced current, 
about C*.05, and a 1 kHz pulser that I built. My findings over the years is the 
current will begin to rise very slowly, peak then drop if the recovery is 
working.

Sorry that this post is getting so long. There's just so much. OK, one last 
thing. In my last post to you I recommended a battery AH monitor. This problem 
could have been detected and perhaps prevented if they had one. 

Larry Crutcher
Starlight Solar Power Systems


 

On Oct 21, 2011, at 11:39 AM, Ron Young wrote:

Hi Maverick  everyone,


I visited the site a couple of days ago and load tested the batteries, checked 
individual voltages in the string of six Surrette 4KS25's (4.3v each), checked 
all connections etc. The client told me that when they would go to bed battery 
volts read 25.7. Through the night this would seem to stay steady. About 4 
a.m. as far as they could tell the voltage would drop to about 24.5. This 
happened without a load present and with no charging present (calm

Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-10-23 Thread Larry Crutcher, Starlight Solar Power Systems
Thank you Darryl.
The important thing is internal temperature. Any current up to the 
manufacturers specification can be used but C/20 means I usually don't need to 
baby sit the battery temp during long term recovery attempts. Adjust 
accordingly.

One thing I didn't mention is that it's not harmful to deficit charge a battery 
for a few days or perhaps a couple weeks as long as the battery gets a 100% 
charge within that time frame. This may require more frequent equalization. 

Larry 



On Oct 23, 2011, at 6:22 AM, Darryl Thayer wrote:

 Thanks Larry, this is one of the best explanations I have seen.  I am saving 
 it for my customers and students.  I would emphasize the C/20 (as you said) 
 or a little less for perhaps C/30 for this long term equalize or desulfation. 
 Too fast an equaliziation can loosen (blow the plate material off the plates) 
 .  (I built a 60 hZ desulfator and have used it twice in 40 years, it seems 
 to work) 
  
 Thanks again great piece of writing and explanation, everyone should read
 Darryl
 From: Larry Crutcher, Starlight Solar Power Systems 
 la...@starlightsolar.com
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Sent: Saturday, October 22, 2011 2:06 PM
 Subject: Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation
 
 Hi Ron,
 
 As many on this list have suggested, it sounds like a sulfated battery 
 condition. In your last message you revealed something to me that absolutely 
 confirms this but perhaps you didn't recognize it. 
 
 Battery voltage readings are deceiving because they do not indicate capacity. 
 25.7 volts sounds like a fully charged 24 volt bank, but is it? Only if the 
 battery was at rest for 5-6 hours could you have some confidence that the 
 bank was full at this voltage. But this is not the case because the bank is 
 in daily use, always charging or discharging. However, there is one useful 
 indication that voltage can be used for: detecting a sulfated battery. 
 
 You mentioned that the the battery drops to 24.5 in the early AM without any 
 heavy loads on. For the 4KS25 battery this equates to about 800AH at the 72 
 hour rate. Then you said that the customer ran a 2500 watt generator for 5 
 minutes and drove the voltage up to 29 volts. Here's the Ah-Ha moment: That 
 is EXACTLY the behavior of a heavily sulfated battery bank. A fast rise in 
 voltage indicates sulfation.  It is impossible for that tiny generator, or 
 any charge source they own for that matter, to replace the hundreds of AH it 
 would take to drive a healthy battery up to the absorb voltage of 29 volts. 
 The bank is about 45,000 watt hours (72h rate). There would have to be over 
 20,000 Wh removed to be at that voltage. How many Wh's are replaced in 5 
 minutes by a 2500 watt genny? I'm sure you are getting the picture. 
 
 Why did this happen to these expensive batteries? Glad you asked. Battery 
 plates are not uniformly efficient in the electrochemical process leaving 
 some portions with lead sulfate even after 8 hours of charging. Unless these 
 portions are cleared off regularly by achieving 100% SoC and occasional, 
 thorough equalization, the amorphous sulfate will convert to a crystalline 
 form and grow. 99% charge, if not corrected in time, will always cause 
 premature battery failure. 
 
 Undersized RE charging systems, or perhaps oversized batteries, is the 
 culprit that contributes to this all too frequent phenomenon of chronic 
 undercharging. I say contribute because there are other factors. Fact: it can 
 take 10-12 hours to fully charge a lead acid battery. Fact: The time element 
 of battery charging is a highly misunderstood part. With only a few daily 
 sun-hours to work with, how do we get a battery charged with PV solar? 
 Properly sizing the PV array to the battery AND consumption is critical. One 
 method I think is essential for nearly all PV systems is use a generator and 
 charger, appropriately sized to the battery. By bulk charging early in the AM 
 you can reduce the finish time to perhaps 5-6 hours of constant voltage 
 charging, something easily done with a PV system.
 
 Ron, you might be able to recover some capacity in this bank if the sulfate 
 has not formed hard crystals by now. You can try a very long charge time, up 
 to 24 hours, at high voltage, about 31 volts. You will need a larger 
 generator. Monitor the temperature and reduce current if they get up to 125F 
 internal. In our shop I have recovered sulfated batteries with high voltage 
 charging, as much as 3Vpc (do not do this with any loads connected), at 
 reduced current, about C*.05, and a 1 kHz pulser that I built. My findings 
 over the years is the current will begin to rise very slowly, peak then drop 
 if the recovery is working.
 
 Sorry that this post is getting so long. There's just so much. OK, one last 
 thing. In my last post to you I recommended a battery AH monitor. This 
 problem could have been detected and perhaps prevented if they had one

Re: [RE-wrenches] intermittent battery problem; ...Battery Sulfation

2011-10-22 Thread Larry Crutcher, Starlight Solar Power Systems
Hi Ron,

As many on this list have suggested, it sounds like a sulfated battery 
condition. In your last message you revealed something to me that absolutely 
confirms this but perhaps you didn't recognize it. 

Battery voltage readings are deceiving because they do not indicate capacity. 
25.7 volts sounds like a fully charged 24 volt bank, but is it? Only if the 
battery was at rest for 5-6 hours could you have some confidence that the bank 
was full at this voltage. But this is not the case because the bank is in daily 
use, always charging or discharging. However, there is one useful indication 
that voltage can be used for: detecting a sulfated battery. 

You mentioned that the the battery drops to 24.5 in the early AM without any 
heavy loads on. For the 4KS25 battery this equates to about 800AH at the 72 
hour rate. Then you said that the customer ran a 2500 watt generator for 5 
minutes and drove the voltage up to 29 volts. Here's the Ah-Ha moment: That is 
EXACTLY the behavior of a heavily sulfated battery bank. A fast rise in voltage 
indicates sulfation.  It is impossible for that tiny generator, or any charge 
source they own for that matter, to replace the hundreds of AH it would take to 
drive a healthy battery up to the absorb voltage of 29 volts. The bank is about 
45,000 watt hours (72h rate). There would have to be over 20,000 Wh removed to 
be at that voltage. How many Wh's are replaced in 5 minutes by a 2500 watt 
genny? I'm sure you are getting the picture. 

Why did this happen to these expensive batteries? Glad you asked. Battery 
plates are not uniformly efficient in the electrochemical process leaving some 
portions with lead sulfate even after 8 hours of charging. Unless these 
portions are cleared off regularly by achieving 100% SoC and occasional, 
thorough equalization, the amorphous sulfate will convert to a crystalline form 
and grow. 99% charge, if not corrected in time, will always cause premature 
battery failure. 

Undersized RE charging systems, or perhaps oversized batteries, is the culprit 
that contributes to this all too frequent phenomenon of chronic undercharging. 
I say contribute because there are other factors. Fact: it can take 10-12 hours 
to fully charge a lead acid battery. Fact: The time element of battery charging 
is a highly misunderstood part. With only a few daily sun-hours to work with, 
how do we get a battery charged with PV solar? Properly sizing the PV array to 
the battery AND consumption is critical. One method I think is essential for 
nearly all PV systems is use a generator and charger, appropriately sized to 
the battery. By bulk charging early in the AM you can reduce the finish time to 
perhaps 5-6 hours of constant voltage charging, something easily done with a PV 
system.

Ron, you might be able to recover some capacity in this bank if the sulfate has 
not formed hard crystals by now. You can try a very long charge time, up to 24 
hours, at high voltage, about 31 volts. You will need a larger generator. 
Monitor the temperature and reduce current if they get up to 125F internal. In 
our shop I have recovered sulfated batteries with high voltage charging, as 
much as 3Vpc (do not do this with any loads connected), at reduced current, 
about C*.05, and a 1 kHz pulser that I built. My findings over the years is the 
current will begin to rise very slowly, peak then drop if the recovery is 
working.

Sorry that this post is getting so long. There's just so much. OK, one last 
thing. In my last post to you I recommended a battery AH monitor. This problem 
could have been detected and perhaps prevented if they had one. 

Larry Crutcher
Starlight Solar Power Systems




On Oct 21, 2011, at 11:39 AM, Ron Young wrote:

 Hi Maverick  everyone,
 
 I visited the site a couple of days ago and load tested the batteries, 
 checked individual voltages in the string of six Surrette 4KS25's (4.3v 
 each), checked all connections etc. The client told me that when they would 
 go to bed battery volts read 25.7. Through the night this would seem to stay 
 steady. About 4 a.m. as far as they could tell the voltage would drop to 
 about 24.5. This happened without a load present and with no charging present 
 (calm, no wind, no sun). They would start up the generator for five minutes 
 in the morning and see the voltage come up to just above 29v then turn off 
 the generator (a small Honda 2500) and the voltage would settly at 25.7 and 
 remain there most of the day even when using their light loads, some lights, 
 phone system, laptop and the Sunfrost.
 
 When checking the batteries I noticed they needed watering and mentioned this 
 to the customer. The electrolyte was just over the plastic screen above the 
 plates by about 1/4 inch. He said he had just watered them and always kept 
 them filled. I replied that they were low and when he looked he said no, 
 that's where I keep them! When I checked the specific gravity reading it was 
 very rich reading