RE: When is a Remote FDC required

2021-02-11 Thread Steve Leyton via Sprinklerforum
I think it's totally up to the responding fire department. If there are certain conditions at a particular site that make operational response more challenging for one reason or another, then it may be of strategic value to have the inlet at a particular location, or possibly more than one

Re: When is a Remote FDC required

2021-02-11 Thread Mark Phillips via Sprinklerforum
I believe NFPA 24 would say 40’ for PIV or backflow Check there perhaps. Sent from my mobile device Please excuse spelling, grammar, and auto correction. Mark Phillips Branch Manager Fire Sprinkler Design, Install, Inspections Service, Backflows, Fire Alarm Inspections 832-101 Purser Drive

Re: When is a Remote FDC required

2021-02-11 Thread BRUCE VERHEI via Sprinklerforum
Talk with the fire plans reviewer. > On 02/11/2021 7:41 PM Jerry Van Kolken via Sprinklerforum > wrote: > > > I'm doing a project for Cal State, and I'm trying find the code that would > dictate when an FDC needs to be remotely located away from the building. I > seem to remember a

When is a Remote FDC required

2021-02-11 Thread Jerry Van Kolken via Sprinklerforum
I'm doing a project for Cal State, and I'm trying find the code that would dictate when an FDC needs to be remotely located away from the building. I seem to remember a requirement about needing to be 50' away from the building, but I can't find this anywhere. Can someone point me in the right

Re: [EXTERNAL] RE: Multiple System Calculation

2021-02-11 Thread J H via Sprinklerforum
Not necessarily a contradiction it's just the sloppy wording of the standard causing confusion and delay - the engineer seems to be making the case that 23.4.4.2.4 deals with different hazard classifications but since the two systems are the same hazard then default to calculating the full area

Re: [EXTERNAL] RE: Multiple System Calculation

2021-02-11 Thread Joe Burtell via Sprinklerforum
If the FAQ is true, then what is the point of 23.4.4.2.4? One says it has to be 1500 no matter what and the other says you just apply the extra GPM at the furthest branchline? Don't they contradict each other? Best regards, *Joe Burtell, SET, CFPS* [image: Burtell Fire_Small] Phone | Fax |

RE: [EXTERNAL] RE: Multiple System Calculation

2021-02-11 Thread cliff--- via Sprinklerforum
We need a 'Like' button on the forum. Since we don't have one, Craig is right on the money here. Cliff Whitfield, SET President Fire Design, Inc. 600 W. Bypass Hwy. 19E Suite 202 Burnsville, NC 28714 Ph: 828-284-4772 -Original Message- From: Sprinklerforum On Behalf Of

Re: [EXTERNAL] RE: Multiple System Calculation

2021-02-11 Thread Fpdcdesign via Sprinklerforum
My thoughts exactly, Mr Prahl. > > On Feb 11, 2021 at 3:46 PM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > > > > If I have 4-heads of OH2 in a 500 sf space I have to calc it and size > everything as if I had a 1500 sf design

RE: [EXTERNAL] RE: Multiple System Calculation

2021-02-11 Thread Prahl, Craig/GVL via Sprinklerforum
If I have 4-heads of OH2 in a 500 sf space I have to calc it and size everything as if I had a 1500 sf design area. Where’s the value? What greater level of Life Safety is provided? You should only have to calculate the actual area up to the prescribed area and not add some fictitious value,

RE: Multiple System Calculation

2021-02-11 Thread Bob Knight via Sprinklerforum
Joe, Seems to me that this section specifically allows for your situation, then The next section directs you to the flow issue. 23.4.4.2.4 Where the available floor area for a specific area/ density design criteria, including any extension of area as required by 11.1.2 and Section 12.3, is less

Re: [EXTERNAL] RE: Multiple System Calculation

2021-02-11 Thread J H via Sprinklerforum
I can understand both perspectives and I would do it your way if I were in your shoes, however the engineer does have a valid point per the FAQ in the handbook in section 11.2.3.4.1(1) in the 2013 edition which states: FAQ What is the assigned operating area for subsystems that are smaller than

RE: [EXTERNAL] RE: Multiple System Calculation

2021-02-11 Thread Travis Mack via Sprinklerforum
Tracey Bellamy, I believe, was the one to propose it. It had to deal with a loading dock and then having to grab ESFR sprinklers in the warehouse to get the 1950 sq ft if I recall correctly. I read the report a couple years ago. I see where he was coming from. The intent was good. But, I

Re: Multiple System Calculation

2021-02-11 Thread Joe Burtell via Sprinklerforum
Well, I didn't get far. His response below, any suggestions? Section 23.4.4.2.4 indicates for a “specific area/density design criteria” Not a specific type of sprinkler system. The entire mechanical penthouse, both wet and dry systems, is one area/density design of ordinary hazard. So keep adding

RE: [EXTERNAL] RE: Multiple System Calculation

2021-02-11 Thread Prahl, Craig/GVL via Sprinklerforum
This is something that really needs to be looked at I future editions of NFPA 13. I know we've had this discussion many times. I would love to hear how this came about. It offers no benefit to an owner and only increases cost. Craig Prahl | Jacobs | Group Lead/SME – Fire Protection |

Re: Multiple System Calculation

2021-02-11 Thread Joe Burtell via Sprinklerforum
Thanks, guys, that is what I was thinking as well. Best regards, *Joe Burtell, SET, CFPS* [image: Burtell Fire_Small] Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>* 116 N. 11th Street | Billings, MT 59101 Email: j...@burtellfire.com Web Site: http://www.burtellfire.com

RE: Multiple System Calculation

2021-02-11 Thread Bob Knight via Sprinklerforum
Joe, The AHJ's interpretation sounds incorrect. What is supposed to take place is as follows: 23.4.4.2.5 Where the total design discharge from these operating sprinklers is less than the minimum required discharge determined by multiplying the required design density times the required

RE: Multiple System Calculation

2021-02-11 Thread Jack Carlson via Sprinklerforum
Joe, While the AHJ is referring to 11.1.2, see NFPA 13 (2016)23.4.4.2.4. The annex provides for the steps to increase the flow. Jack W. Carlson, SET -Original Message- From: Sprinklerforum On Behalf Of Joe Burtell via Sprinklerforum Sent: Thursday, February 11, 2021 12:47 PM To:

Multiple System Calculation

2021-02-11 Thread Joe Burtell via Sprinklerforum
I have a situation where an engineer is telling me I have to calculate a wet and dry system together because neither space meets the 1500 s.f minimum. I have a penthouse mechanical room OH 1 (WET) of 1014 s.f. and an adjacent room OH1 (DRY) of 469 s.f. I have calculated each room separate of each