Re: Fire pump test through flow meter

2021-04-19 Thread Fpdcdesign via Sprinklerforum
The question is now moot because they went and tested the pump by actually flowing water and it ran fine. The problem lies in the testing process and that is someone else’s headache. > > On Apr 19, 2021 at 5:05 PM,

RE: Fire pump test through flow meter

2021-04-19 Thread Tom Duross via Sprinklerforum
I bet if there was a partially closed gate, or a check, or a blockage; that might cause it. Are they’re any good resources about testing a fire pump with a flow meter where it feeds back into the suction piping? I have been given a couple of tests with very screwy results. Thanks

RE: Same size orifice in a room

2021-04-19 Thread Travis Mack via Sprinklerforum
The Exhibit 23.10 and the description in the Annex details exactly what I was hoping to use to make sure this method is acceptable. I have used this many times, but just needed to find the section for this one. Thanks to all the forum for the assistance. Travis Mack, CFPS, CWBSP, RME-G, COC,

RE: Same size orifice in a room

2021-04-19 Thread Hinson, Ryan via Sprinklerforum
Same orifice, no. Limits on orifice, yes...in several places such as NFPA 13 (2019) Sections 9.4.4, Chapter 21, Chapter 25, Section 27.2.4.9.2, or word search 'factor'. Same response time per compartment, yes per Section 9.4.3.2. Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell Senior Fire

RE: Same size orifice in a room

2021-04-19 Thread Travis Mack via Sprinklerforum
Because they first submitted and it didn't work. Long story. Was all installed with EC sprinklers. Some things got called into question and now when they change to 5.6k then it works. So, I'm hoping that I can use the Exhibit 23.10 as an acceptable view to state this works and is

RE: Same size orifice in a room

2021-04-19 Thread cliff--- via Sprinklerforum
T Mack, I'm not sure where it's located but I have used smaller orifice sprinklers under a soffit as you describe. I discussed it in depth with the old VP at AFSA and he said it was perfectly acceptable. If I can find my old emails, I'll send them to you off-forum. Cliff Whitfield, SET

Re: Same size orifice in a room

2021-04-19 Thread Fpdcdesign via Sprinklerforum
How do you prove the designer did it to balance flow? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (tel:860-554-7054) (fax) 860-608-4559 (tel:860-608-4559) (cell) > > On Apr

RE: Same size orifice in a room

2021-04-19 Thread Travis Mack via Sprinklerforum
I've had it come up in a review before. An AHJ was arguing with me that I couldn't have a 5.6k sprinkler in an alcove and then EC sprinklers in the corridor. Just ran into similar, but in a very large compartment for a project I am reviewing. Technically, I believe the designer is using it

RE: Same size orifice in a room

2021-04-19 Thread Mike Morey via Sprinklerforum
23.4.4.9 (2016 ed NFPA 13) is the only prohibitions about mixing sprinkler sizes I'm aware of. Mike Morey CFPS 3229 * NICET S.E.T. 123677 Project Manager * Fire Protection Group Shambaugh & Son, LP an EMCOR Company 7614 Opportunity Drive * Fort Wayne, IN * 46825 direct 260.487.7824 / cell

Re: Same size orifice in a room

2021-04-19 Thread Fpdcdesign via Sprinklerforum
I’m not sure there is such a section. I’ve had extended sidewalls in parts of a room and regular pendants in the other. > > On Apr 19, 2021 at 2:24 PM, (mailto:sprinklerforum@lists.firesprinkler.org)> wrote: > > > > I'm trying to locate the

RE: Same size orifice in a room

2021-04-19 Thread Matt Grise via Sprinklerforum
I don't think you are going to find that. You are not allowed to vary the k-factor along a branch line for the purposes of hydraulic balancing, but the heads do not all have to be the same. FM may recommend against it though - you might check data sheet 2-0 Matt -Original Message-

RE: Same size orifice in a room

2021-04-19 Thread Micah Davis via Sprinklerforum
Smarter guys on the forum than me I'm sure will correct me if I am wrong, but I don't think there is a prohibition about mixing orifice sizes. Only mixing thermal sensitivity (QR and SR). NFPA 13 8.3.3.2 Micah Davis Principal Phone1: (904) 800-6782 Phone2: (931) 242-1299 4373 Sycamore Pass

Same size orifice in a room

2021-04-19 Thread Travis Mack via Sprinklerforum
I'm trying to locate the section in the standard about all sprinklers in a compartment to be same orifice. Can anyone help point me in that direction? My searching is not too productive today. Travis Mack, CFPS, CWBSP, RME-G, COC, SET Engineering Manager MFP Design 3356 E Vallejo Ct Gilbert,

Re: "Calculating" a Pipe Scheduled system for Backflow Retro

2021-04-19 Thread J H via Sprinklerforum
Yeah, I've done it before but wanted to see if I had been doing it correctly. I don't like to hydraulically calculate a pipe scheduled system as I've often seen the calcs bust causing even more headache for everyone when it's not necessary if the pipe scheduled 'hand calc' method works - not to

Fire pump test through flow meter

2021-04-19 Thread Fpdcdesign via Sprinklerforum
Are they’re any good resources about testing a fire pump with a flow meter where it feeds back into the suction piping? I have been given a couple of tests with very screwy results. Thanks Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT

Re: Standpipe Testing

2021-04-19 Thread Skyler Bilbo via Sprinklerforum
Hey Tom, Without explaining all of the math, if your system is 10,000 gallons and you already had it full of water (I think you said you could fill to 70 PSI from the city supply), with no air in the system, you would have it pumped up to 200 psi with your little 4 GPM pump in less than 12