RE: Calculating Parallel fire pumps

2021-06-21 Thread Prahl, Craig/GVL via Sprinklerforum
Yeah, that pretty much describes the proposed setup. Two primary pumps at 1500 each to meet a 2900 gpm demand. Third pump in the house is for redundancy. Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler Road Greenville, South

RE: Calculating Parallel fire pumps

2021-06-21 Thread Travis Mack via Sprinklerforum
We've done this where there is a need for redundant pumps. Let's assume you need a 3000 gpm pump. A second 3000 gpm pump is quite expensive. The contractors had us set it up as (2) 1500 gpm pumps for a 3000 gpm total capacity. Then, you need a redundant pump in case one is down, so then you

RE: [EXTERNAL] RE: Calculating Parallel fire pumps

2021-06-21 Thread Prahl, Craig/GVL via Sprinklerforum
That would be awesome. Yes, by all means feel free to use that descriptor. I deal constantly with those who think the only difference between Process equipment and Fire protection is that we paint our stuff red. Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | craig.pr...@jacobs.com

RE: Calculating Parallel fire pumps

2021-06-21 Thread Prahl, Craig/GVL via Sprinklerforum
What's the logic? Who knows. I know how this should be done and this isn't going to accomplish anything except just to complicate the design. The issue is, one building we have exceeds the 150% out of a single pump so with what they want to use, one pump won't make it unless we actually

RE: Calculating Parallel fire pumps

2021-06-21 Thread cliff--- via Sprinklerforum
Craig, We use AutoSprink and I'd be happy to see if I can do that calc for you. Not sure but think it can be done. You can contact me off forum to discuss. The main question I have is, can I use your description of the fire protection expert in future correspondences? I deal with folks like

RE: Calculating Parallel fire pumps

2021-06-21 Thread Matt Grise via Sprinklerforum
What is the goal of having 2 pumps? If you want full redundancy, could you just calculate the system one pump at a time? It seems like having them both running would be a better-case scenario that would result in added safety. Are they trying to get by with 2 smaller pumps? I think AutoSprink

Calculating Parallel fire pumps

2021-06-21 Thread Prahl, Craig/GVL via Sprinklerforum
We have a project in one of the Arab states. We are following a little bit of the UFC and some of the local codes. The owner wants two pumps selected at 50% of the required capacity instead of one pump as we would normally provide. His thought is that pump 1 comes on and runs at 50% of it's