Very common in the Charlotte North Carolina region if I’m understanding the
situation correctly. This sounds like an exception to 503.1.1 which allows
an approved alternative means for fire access due to topography, waterways,
or grade issues. These are outside hose connections or wall hydrants
I have some notes from a NFPA 30 and NFPA 30B class stating that the demand
of the sprinklers installed in racks don't have to be added to the ceiling
sprinkler water demand. I am struggling to find where in each respective
standard the language that allows that. Does anyone know if there is
That is my understanding as well Matt.
Fire area separation IBC 707.3.10
Fire wall separation IBC 706.4
On Thu, Feb 4, 2021 at 2:27 PM Matt Grise via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:
> I was thinking that it was 2 hours to be a separated occupancy in the same
>
I’m referencing the 2015 I Codes. Is there adequate separation per IBC
707.3.10? If not then perhaps it’s been built nonseparated in which IBC
508.3 applies the most restrictive provisions of chapter 9 that apply to
the non separated occupancies to the total nonseparated area. Just a head
up
I am being informed the International Residential Code has a provision
requiring a NFPA 13R system in a single family residence four stories or
more in height. Admittedly, this is the first time I've heard of this in
my career. I am scanning through the IRC and am not able to locate this
In a building recognized as part of separate fire areas, the annex material
in NFPA 14 Section 7.10.1.1 states the the total supply can be calculated
based on the single bldg/ fire area requiring the greatest number of
standpipes. In this scenario, the physical separation between fire areas
is
I am inquiring to see if anyone can provide clarification to the
term "bulk" as it relates to the storage of solid oxidizers in Table
22.37.1.4.1 (2013 ed.). I don't see the term defined in Chapter 3.
Zach Siegrist
___
Sprinklerforum mailing list
Do you mind providing a link to the specific article referenced?
On Mon, Mar 11, 2019 at 11:56 AM Skyler Bilbo
wrote:
> I may do this sometimes, just to get an idea of the water supply, early on
> in a bid, but I would never rely on this for the design of a fire sprinkler
> system. There are a
tion/Tiroly
>
> 24400 Highland Rd CLE 44143
>
> 216-621-8899
>
> 216-570-7030 cell
>
>
>
>
>
>
>
> *From:* Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *Zachary
> Siegrist
> *Sent:* Tuesday, April 0
All,
I am an AHJ and was called to inspect a installation for protection of
carton record storage for a single- level catwalk. The existing ceiling
level protection is an ESFR system. Section 20.5.6.2.1 states that ceiling
sprinklers spaced to cover a maximum of 100 SF shall be standard response
All,
Does the wide obstruction rule apply on a 13D system? I came across a wide
staircase that wraps around the open entry of a huge house. The stair
easily exceeds 4 feet in width and the way its arranged has created a
decent gap in coverage. Contractor has objected and says the wide
What does a voluntary replacement mean as it relates to fire sprinklers? I
understand the difference between voluntary recall vs a mandatory product
recall, but am confused what a voluntary replacement means. Is there a
difference?
Zach
___
903.3.5.1.1 of the IBC, 2012 ed. Is that what you are looking for?
On Wed, Aug 23, 2017 at 10:41 AM wrote:
> Brian,
>
>
>
> I think it’s in NFPA 101 if I remember correctly.
>
>
>
> Cliff Whitfield, SET
>
> President
>
>
>
> Fire Design, Inc.
>
> 184 Comfort Place
>
>
inklers Saves Lives
>
>
>
>
> On Aug 11, 2017, at 6:43 AM, Zachary Siegrist <zachary.siegr...@gmail.com>
> wrote:
>
> I thought I was clear on this definition but I have an FPE and a technical
> representative from a fire sprinkler manufacturer stating they are not
I thought I was clear on this definition but I have an FPE and a technical
representative from a fire sprinkler manufacturer stating they are not
concerned with the opening of cross section area in regards to the 70 %
stipulation in the definitions. They have stated they are only concerned
about
: https://www.linkedin.com/in/travismack
>
>
>
> *From:* Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler.
> org <sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *Zachary
> Siegrist
> *Sent:* Monday, June 26, 2017 3:31 PM
> *To:* Sprinklerfo
Is there a listed residential head guard on the market? I have never came
across one.
Zach
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
>
>
> *From:* Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org]
>
> *On Behalf Of *Zachary Siegrist
>
>
> *Sent:* Friday, June 09, 2017 10:58 AM
>
>
> *To:* sprinklerforum@lists.firesprinkler.org
>
>
> *Subject:
>
> The foregoing is my opinion only and is not intended to represent the NFPA
> 14 Technical Committee, nor serve as an interpretation of the standard.
>
>
>
>
>
> Steve Leyton
>
>
> Protection Design & Consulting
>
>
> San Diego, CA
>
>
>
I am seeing a master PRV for the first time. I am reviewing the nine
criteria in NFPA 14 and am stumbling around one of them. What is the
intent of the equally sized bypass mentioned in item four? Is there a
requirement for an additional PRV in the bypass since the pressure won't be
reduced?
I have a job where the heads ( ordinary temp) are less than 1 ft 0 in from
the edge of a downward discharge diffuser throughout the space. The
contractor has supplied me letter from the HVAC company stating that the
air discharged out of the diffusers are less than 100F and therefore the
heads do
I don't have an NFPA 20 in front of me this evening, but I recall there
being a provision for ventilation in a fire pump room. Can anyone advise
if this requirement is for both diesel and electric pumps?
Zach
___
Sprinklerforum mailing list
I have a contractor submitting a detail to protect unheated storage closets
off the balcony ( minimal in size) with a dry pendant extending
down at a 45 degree angle as shown in figure 8.15.7 in the 2013 edition.
My take is that this section applies to exterior projections including
I'm not seeing anything in NFPA 14 not allowing the concealment on
standpipe piping. However, I feel this may create a problem with the 5
year dry standpipe system hydrostatic test required per NFPA25. 6.3.2.3 of
NFPA25 states that inside standpipe piping shall show no leakage. If the
piping is
:tm...@mfpdesign.com
> <javascript:_e(%7B%7D,'cvml','email:tm...@mfpdesign.com');>
> http://www.mfpdesign.comhttps://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> LinkedIn: https://www.linkedin.com
The blazemaster technical handbook states that cpvc pipe and fittings are
not approved for installation in combustible concealed specs requiring
sprinklers, as referenced in nfpa 13 unless protected by sprinklers
specifically listed for this application. Further on down, the handbook
talks about
To add to what John said, I think the only way to break this up into two
buildings is to install a true fire wall out of table IBC 706.4. Breaking
this up into fire areas out of IBC 707 just defines fire areas and the code
will not recognize it as two buildings.
Zach
On Tuesday, August 30,
All, how does one calculate loss through a master pressure reducing valve?
I am an AHJ and didnt receive a data sheet in the submittal. Is there a
fixed loss such as through backflows?
Zach
___
Sprinklerforum mailing list
Thank you for chiming in on this subject. I did end up rejecting the
plans. The duct wasn't the only portion of the paint spray application
using HSW. Thanks again.
On Thursday, August 11, 2016, Roland Huggins
wrote:
> OK Boys and Girls. This horse is dead and
I was taught that sidewall sprinklers cannot be used in an extra hazard
application. At least that is what I recall. Additionally, the protection
areas and maximum spacing table for sidewall heads do not have any
information for extra hazard occupancies. I am reviewing a set of plans for
a paint
>> a max of 1200 and the system requires a 1500 gpm pump, then a tank is going
>> to be required. That is my assumption at least.
>>
>> Travis Mack, SET
>>
>> MFP Design, LLC
>>
>> 2508 E Lodgepole Drive
>>
>> Gilbert, AZ 85298
>>
&
gt;
>> CH2MHILL Extension 77540
>> craig.pr...@ch2m.com
>> <javascript:_e(%7B%7D,'cvml','craig.pr...@ch2m.com');>
>>
>>
>>
>> *From:* Sprinklerforum [
>> mailto:sprinklerforum-boun...@lists.firesprinkler.org
>> <javascript:
ILL Extension 77540
> craig.pr...@ch2m.com
> <javascript:_e(%7B%7D,'cvml','craig.pr...@ch2m.com');>
>
>
>
> *From:* Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org
> <javascript:_e(%7B%7D,'cvml','sprinklerforum-boun...@lists.firesprinkler.or
All,
I came across my first antifreeze system today in an existing application.
I know there is no current listing of antifreeze for use in new
applications which partially explains why I have never seen an antifreeze
system before. The install was consistent with the arrangement of supply
piping