A floor Control Valve at each level is an NFPA 13 Requirement.  Either they’re 
installed or the system doesn’t pass inspection and no C of O.

A FCV at each level just makes sense when it comes to future servicing of the 
system and not having to drain down all levels for a simple repair.

A change order is due outlining the written requirement.

Craig Prahl | Jacobs | Fire Protection SME – Special Hazards | 
craig.pr...@jacobs.com<mailto:craig.pr...@jacobs.com> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS


From: Rick Matsuda <rick26...@gmail.com>
Sent: Tuesday, April 9, 2024 9:00 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org>
Subject: [EXTERNAL] [Sprinklerforum] Re: Floor Control Valves

Maybe you can “convince” the owner to install four control valves, one for each 
floor and one for the attic.
Tell him that if the system has only one control valve and it has to be shut 
off for any reason, then he will be required to evacuate the entire building or 
pay for a “fire watch” on each floor until the system is returned to service.

I don’t know if there is any code justification for this reasoning…it’s just my 
off-the-wall thought.
Rick Matsuda

On Apr 9, 2024, at 7:52 AM, 
bcap...@firesprinkler.org<mailto:bcap...@firesprinkler.org> wrote:

A lot depends on the year of the standard being applied, but YES an AHJ can 
(and should) require things that make sense for his/her community and the 
methods used or planned for fire and EMS responses.  In this case, you are on 
solid footing because NFPA 13 (2019 edition) section 16.9.11.1 requires floor 
control valves in multistory buildings exceeding two stories in height.

This requirement was added to NFPA 13 in the 2013 edition (section 8.16.1.5)




[https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1]
Bob Caputo, CFPS
President
American Fire Sprinkler Association
c:     760-908-7753
p:
214-349-5965 ext124
w:
firesprinkler.org<https://urldefense.com/v3/__http:/firesprinkler.org/__;!!B5cixuoO7ltTeg!CCUYhDtfWTlgR_5LUvsZubHFnZX7RjBvVjzbuNpHai-0HQgnxKeuITDo-6r11npheB_4kcQQHhi5byOM1nXm$>
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/facebook_sig.png]<https://urldefense.com/v3/__https:/www.facebook.com/firesprinkler.org/__;!!B5cixuoO7ltTeg!CCUYhDtfWTlgR_5LUvsZubHFnZX7RjBvVjzbuNpHai-0HQgnxKeuITDo-6r11npheB_4kcQQHhi5b5y_I45n$>
  
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/twitter_sig.png] 
<https://urldefense.com/v3/__https:/twitter.com/afsa/status/1039528345367732224__;!!B5cixuoO7ltTeg!CCUYhDtfWTlgR_5LUvsZubHFnZX7RjBvVjzbuNpHai-0HQgnxKeuITDo-6r11npheB_4kcQQHhi5b26u9rXz$>
   
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/linkedin_sig.png]
 
<https://urldefense.com/v3/__https:/www.linkedin.com/company/american-fire-sprinkler-association-afsa-/__;!!B5cixuoO7ltTeg!CCUYhDtfWTlgR_5LUvsZubHFnZX7RjBvVjzbuNpHai-0HQgnxKeuITDo-6r11npheB_4kcQQHhi5b4fQt9rY$>
   
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/instagram_sig.png]
 
<https://urldefense.com/v3/__https:/www.instagram.com/firesprinklerorg/__;!!B5cixuoO7ltTeg!CCUYhDtfWTlgR_5LUvsZubHFnZX7RjBvVjzbuNpHai-0HQgnxKeuITDo-6r11npheB_4kcQQHhi5b_cSQsbk$>

Top-Notch Training for ITM Technicians!

AFSA has taken ITM) training to the next level with three new courses: 
Beginning 
ITM<https://urldefense.com/v3/__https:/www.firesprinkler.org/programs/beginning-itm-workshop/__;!!B5cixuoO7ltTeg!CCUYhDtfWTlgR_5LUvsZubHFnZX7RjBvVjzbuNpHai-0HQgnxKeuITDo-6r11npheB_4kcQQHhi5b6f7Y_3K$>,
 Intermediate 
ITM<https://urldefense.com/v3/__https:/www.firesprinkler.org/programs/intermediate-itm-workshop/__;!!B5cixuoO7ltTeg!CCUYhDtfWTlgR_5LUvsZubHFnZX7RjBvVjzbuNpHai-0HQgnxKeuITDo-6r11npheB_4kcQQHhi5b8EEAxVv$>,
 and Fire Pump 
ITM<https://urldefense.com/v3/__https:/www.firesprinkler.org/programs/fire-pump-itm-workshop/__;!!B5cixuoO7ltTeg!CCUYhDtfWTlgR_5LUvsZubHFnZX7RjBvVjzbuNpHai-0HQgnxKeuITDo-6r11npheB_4kcQQHhi5b0ZnQ44r$>.
 Each workshop offers CEUs, CPDs, and contact hours. Expand your business and 
increase your employees’ knowledge and skill set with these training 
opportunities!

From: chris.jo...@ci.urbana.oh.us<mailto:chris.jo...@ci.urbana.oh.us> 
<chris.jo...@ci.urbana.oh.us<mailto:chris.jo...@ci.urbana.oh.us>>
Sent: Tuesday, April 9, 2024 6:57 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Floor Control Valves


I have a 3 story older building being renovated with sprinkler system being 
added. My question is can AHJ require a floor control valve to be added to each 
floor. Plans only show 1 floor control valve for the first floor. 1st floor 
being business, 2nd and 3rd floor being residential and attic space being 
sprinklered also. Concern of freeze and break in attic on older building and to 
be able to isolate a floor after a fire.



Thanks

Chris Jones, Fire Marshal

Urbana Fire Division

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!B5cixuoO7ltTeg!CCUYhDtfWTlgR_5LUvsZubHFnZX7RjBvVjzbuNpHai-0HQgnxKeuITDo-6r11npheB_4kcQQHhi5b4gcBewt$>
To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to