Agreed; just include that underground in your calculations.

-Kyle M

From: Skyler Bilbo <sbi...@wenteplumbing.com>
Sent: Monday, May 6, 2024 2:20 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org>
Subject: [External][Sprinklerforum] Re: Water Supply

Bob,

Based on the information you provided, if it were me, I would include the 2100 
feet of underground piping and fittings in the calcs and make the actual fire 
pump location your source node.  Since pressure loss is exponentially related 
to flow rate, your scenario would likely be OK for anything less than an actual 
demand of 800 GPM, but could be severely lacking if your actual flow demand 
ends up higher than the 800 GPM you selected.  There is more information 
required to make a complete recommendation, but hopefully this is helpful.

It should also be mentioned that based on the information you provided, the 
pressure that is in the underground piping under normal conditions when the 
jockey pump is on could be greater than 175 psi (use the jockey off pressure + 
pressure increase due to elevation).  This may require special considerations 
for your pipe/fitting/equipment selection to handle the higher pressures.


Thanks,
Skyler Bilbo
[https://ci3.googleusercontent.com/mail-sig/AIorK4ypz1ksMJ3EkM_lvlFpvE7Es0BKHztyDLd8192CCAmeOi-AUa-PgQ7QQY-WJuWAGEB3ctSbfrljwe-Q]
1700 S. Raney Street
Effingham, IL 62401
217-819-6404 Direct

sbi...@wenteplumbing.com<mailto:sbi...@wenteplumbing.com>
www.wenteplumbing.com<http://www.wenteplumbing.com/>


On Mon, May 6, 2024 at 3:57 PM Bob Knight 
<b...@firebyknight.com<mailto:b...@firebyknight.com>> wrote:
I have a project where the complete underground plan has not been provided, yet.
What I do have is a fire pump house with a recent fire pump test.
The fire pump house is about 2,100 feet from the project site.  It is elevated 
about 54 feet higher as well.
I do have the underground loop around the building, so I was going to use the 
connection point at the loop for the underground from the pump house as the 
source point.
The pump test shows 152 psi @ 0 gpm and 101 psi @ 1500 gpm.
The elevation gain in pressure is 23.38 psi.
The friction loss through the 2,100 feet of pipe and 16 or so fittings and 
valves, totals 2,372 feet.
This came out to 21.24 psi of friction loss, assuming 800 gpm of flow including 
250 gpm hose.
I'm adding the elevation gain and subtracting the friction loss from the pump 
test.
This leaves me with 154.14 psi @ 0 gpm and 103.14 psi @ 1500 gpm.
I'm just going to use the numbers from the pump test and re-verify everything 
at a future date.
Does this sound reasonable?
--
Thank you,
Bob Knight, CET III
Fire by Knight, LLC
208-318-3057
[FIREBYKNIGHT]

[https://s-install.avcdn.net/ipm/preview/icons/icon-envelope-tick-green-avg-v1.png]<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
Virus-free.www.avg.com<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to