We either get pre-terminated Commscope cable from Best-tronics (just call
them!) or Shireen hybrid cable from Streakwave, etc.

On Thu, Jun 20, 2019 at 4:06 PM Sterling Jacobson <[email protected]>
wrote:

> Awesome info, thanks!!
>
>
>
> Where are you getting the Shireen hybrid fiber cable and what is the part
> number for that?
>
>
>
> Definitely need that.
>
>
>
> *From:* AF <[email protected]> *On Behalf Of * Josh Baird
> *Sent:* Thursday, June 20, 2019 1:58 PM
> *To:* AnimalFarm Microwave Users Group <[email protected]>
> *Subject:* Re: [AFMUG] UPS and DC to DC conversion
>
>
>
> Our typical setup medium sized sites is:
>
>
>
> Traco TSP-360-148 (360W @ 48V)
>
> Traco TSP-BCM48A (we usually put a string of 4 12-33ah 12V batteries on
> these)
>
>
>
> For very small sites, where we only need (or can fit) 1 12V battery, but
> still require 48VDC, we do:
>
>
> Meanwell SDR-240-48
>
> Traco TSP-BCMU (good for ~220W, can output either 24VDC or 48VDC with a
> single 12VDC battery.. we usually put a single 18-33ah battery on these)
>
>
>
> Voltage drop obviously depends on length of the run, but you should be
> able to easily calculate that.  We usually adjust our PSU's (at the bottom)
> to ~54VDC and we typically see ~49-51VDC at the top.  Yes, you can tweak
> the output of both the Meanwell and the Traco to compensate for voltage
> drop if needed.
>
>
>
> We use a Shireen hybrid fiber cable which has a 12AWG pair for DC.  We use
> these up to 200ft or so.
>
>
>
> On Thu, Jun 20, 2019 at 3:47 PM Sterling Jacobson <[email protected]>
> wrote:
>
> So what’s the Traco parts list for that?
>
>
>
> I don’t do this stuff normally, so excited to get started and try it out.
>
>
>
> If I’m pushing 48v up top to a roof, what’s the voltage drop?
>
>
>
> I assume these DC units can somehow be tweaked so that output can
> accommodate for voltage drop.
>
>
>
> What size wire is everyone using typically for this, usually 30-100 ft max
> length?
>
>
>
> I’m assuming it’s something like 10 AWG? At 48v and 5A and 50’ is maybe
> 47.5v at the end?
>
> So I would push 49 or 50v just to be safe?
>
>
>
> *From:* AF <[email protected]> *On Behalf Of *Josh Baird
> *Sent:* Wednesday, June 19, 2019 8:19 AM
> *To:* AnimalFarm Microwave Users Group <[email protected]>
> *Subject:* Re: [AFMUG] UPS and DC to DC conversion
>
>
>
> FWIW - we have lots of EdgePoint S16's that are powered by Traco BCM/TSP
> combos @ ~54V with no issues.
>
>
>
> I agree with others - your battery plant should be 48VDC.
>
>
>
> On Wed, Jun 19, 2019 at 10:15 AM Sterling Jacobson <[email protected]>
> wrote:
>
> Yeah, I’ll probably just use 48v battery array in series and float higher.
>
>
>
> That particular device can do 48v, it just may shut down POE if it gets
> lower than 48v.
>
>
>
> *From:* AF <[email protected]> *On Behalf Of *[email protected]
> *Sent:* Wednesday, June 19, 2019 8:11 AM
> *To:* AnimalFarm Microwave Users Group <[email protected]>
> *Subject:* Re: [AFMUG] UPS and DC to DC conversion
>
>
>
> Why not run your system at 54 volts?  If the radio freaks out above 54,
> just set it at 54 and you should be fine.  Battery strings don’t exceed the
> float voltage of the rectifier.  If you are worried about it float at 53.75
> volts.
>
>
>
> *From:* Sterling Jacobson
>
> *Sent:* Tuesday, June 18, 2019 11:19 PM
>
> *To:* AnimalFarm Microwave Users Group
>
> *Subject:* Re: [AFMUG] UPS and DC to DC conversion
>
>
>
> Having a hard time figuring out the exact part/price for something like
> this.
>
>
>
> Which Meanwell part would take 48v and make it 50v or 54v 5A?
>
>
>
> *From:* AF <[email protected]> *On Behalf Of *Adam Moffett
> *Sent:* Tuesday, June 18, 2019 10:21 PM
> *To:* [email protected]
> *Subject:* Re: [AFMUG] UPS and DC to DC conversion
>
>
>
> That's weird to me.  Any telecom equipment made for 48v I would have
> assumed they intended it to be used with a rectifier, and consequently I
> would assume it'd be ok up to at least 56v continuous; and maybe more like
> 60-70v for a short duration.  But yeah, DC-DC converter is the fix.
>
> On 6/18/2019 11:36 PM, Sean Heskett wrote:
>
> You need to use a DC-DC converter for sensitive equipment like that.
> Meanwell has a good selection.
>
>
>
> On Tue, Jun 18, 2019 at 8:12 PM Sterling Jacobson <[email protected]>
> wrote:
>
> Apparently the UBNT EP-S16 freaks out if it goes above 54v.
>
> Is there any way to assure it doesn’t float/charge above 54v, or maybe
> even just 50v?
>
>
>
> *From:* AF <[email protected]> *On Behalf Of *TJ Trout
> *Sent:* Tuesday, June 18, 2019 7:26 PM
> *To:* AnimalFarm Microwave Users Group <[email protected]>
> *Subject:* Re: [AFMUG] UPS and DC to DC conversion
>
>
>
> contact talley or tessco for a price, don't trust what you see on google,
> it's like 50% less
>
>
>
> On Tue, Jun 18, 2019 at 6:25 PM TJ Trout <[email protected]> wrote:
>
> all 48v systems for battery power will float at 54v, it's also adjustable
> via the battery chemistry
>
>
>
> On Tue, Jun 18, 2019 at 3:33 PM Sterling Jacobson <[email protected]>
> wrote:
>
> Ok, cool.
>
>
>
> So can the 7bc2 be adjusted slightly to output 50v instead of just 48v?
>
>
>
> There will be some loss going 100’  or so, right?
>
>
>
>
>
> *From:* AF <[email protected]> *On Behalf Of *TJ Trout
> *Sent:* Tuesday, June 18, 2019 4:23 PM
> *To:* AnimalFarm Microwave Users Group <[email protected]>
> *Subject:* Re: [AFMUG] UPS and DC to DC conversion
>
>
>
> 12-54v is inefficient, if you want 200ah of battery use 4x50ah batteries
> for a 48v string
>
> ICT24048-7BC2 360W 54v AC-DC + LVD + Charger
> ICT-TMP - Temp sensor for charge compensation if batt's outside
> ICT-WMB - Wall mount bracket
> SITE Monitor - Voltage monitoring
>
> Or
>
> Alternativly;
>
> 48v din mount PSU
> 48v 'dc ups' to charge batt's and provide LVD
> OR
> 48v din 'dc ups' with integrated psu + lvd + charger (i.e. DIN-UPS 48-5
> cheaper options available)
>
>
>
> On Tue, Jun 18, 2019 at 2:50 PM Sterling Jacobson <[email protected]>
> wrote:
>
> I’m trying to put a “box” system together for our house POP sites and need
> help with the DIN stuff and UPS.
>
>
>
> Can you guys give me an idea or example of the following?
>
>
>
> I want to take standard AC 15A in from a breaker outside the box.
>
> And using maybe one or two 12v 105AH AGM batteries, supply 50v 6A up the
> side of the house.
>
>
>
> I have never ordered DIN parts like this, guess I don’t have to use DIN,
> but would be nice.
>
>
>
> Having a problem finding a DC to DC converter that takes 12v and
> upconverts to 50v 5-6A.
>
>
>
> Is this the cost effective method? Something like this:
>
>
>
> Monitoring         Sitemonitor Base Unit II SMON Base
> II                                                     1.00
> $100.00                $100.00
>
> UPS Monitor      Sitemonitor Int MorningStar MeterBus  SMON
> MorningStar         1.00        $60.00                 $60.00
>
> UPS Charge         MorningStar Sunsaver
> Dual
> 1.00        $165.00                $165.00
>
> Battery AGM Deep Cycle 105AH NPP
> FT12-105AH
> 2.00        $225.00                $450.00
>
> DIN Parts like DC fuse/breakers and trunk
> stuff
> 1.00        $100.00                $100.00
>
> DC 12v to 50v
> 5A
> 1.00        $150.00                $150.00
>
> --
> AF mailing list
> [email protected]
> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>
> --
> AF mailing list
> [email protected]
> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>
> --
> AF mailing list
> [email protected]
> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>
>
>
>
> ------------------------------
>
> --
> AF mailing list
> [email protected]
> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>
> --
> AF mailing list
> [email protected]
> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>
> --
> AF mailing list
> [email protected]
> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>
> --
> AF mailing list
> [email protected]
> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>
-- 
AF mailing list
[email protected]
http://af.afmug.com/mailman/listinfo/af_af.afmug.com

Reply via email to