The only real reason I can see for using an LVD, is if the voltage going to
low is going to cause problems... for example, ePMP radios have a feature
where they can be reset to defaults with a power cycle sequence - I have
seen that get triggered by the voltage going to low (probably actually
because the PoE device that was powering them started shutting down). I
don't see it really mattering that much for saving batteries... if it's
happening often enough that it's going to significantly damage the
batteries, you obviously need a lot bigger batteries, or a generator.

On Thu, Aug 8, 2019 at 9:58 AM <[email protected]> wrote:

> My problem with LVDs over the years has been the hysterisis.  Power has
> been back on for an hour but the voltage is still not high enough for the
> LVD to power everything back up.  I never saw any difference in battery
> life in sites with LVD and non LVD.  Generators are the way to go.
>
> *From:* Ken Hohhof
> *Sent:* Thursday, August 8, 2019 8:22 AM
> *To:* 'AnimalFarm Microwave Users Group'
> *Subject:* Re: [AFMUG] LVD
>
>
> Another approach if you can’t get out there fast enough with a portable
> generator would be strategic load shedding.  Often we see that 90% of the
> customers are also without power so we’re getting no benefit by keeping the
> APs running, but maybe we’d like to keep the backhauls up so other sites
> aren’t affected.
>
>
>
> My observation is once you get to the LVD trip point, the rate at which
> the battery voltage is dropping has accelerated and there’s not much
> runtime left anyway.  Also I worry about equipment getting into a locked up
> state if the DC voltage got too low but didn’t cleanly go off and back on.
>
>
>
> Normally we try to have enough battery runtime that we can get there with
> a generator.  There are extreme circumstances though, like widespread power
> outages, or we’ve had ice storms that took down power wires but also made
> the roads impassable for 24 hours.
>
>
>
> I do sometimes wish battery management systems with built in LVDs would
> let us adjust the trip point a little lower, like maybe 19 or 20 volts
> instead of 21.
>
>
>
>
>
> *From:* AF <[email protected]> *On Behalf Of *Chuck McCown
>
>
> *Sent:* Thursday, August 8, 2019 8:57 AM
> *To:* AnimalFarm Microwave Users Group <[email protected]>
> *Subject:* Re: [AFMUG] LVD
>
>
>
> Philosophical question.  With infrequent outages I would prefer to keep
> people on line for as long as possible,  So no lvd or set it below where
> the equipment ceases to function.
>
>
>
> If you have protracted outages get a generator.  I don’t see a use for lvd
> equipment unless it is in a remote area and powering non critical gear.
>
> Sent from my iPhone
>
>
> On Aug 8, 2019, at 1:12 AM, [email protected] <
> [email protected]> wrote:
>
> At what point would you want to enable an LVD on a 12V and 24V system?
>
> --
> AF mailing list
> [email protected]
> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>
> ------------------------------
> --