This is what I do, 5-6kva generator per 2200va UPS.  There are two
generators and two UPS in my case.

I'm not worried about cooling since there's not enough output (the size is
mostly for large battery capacity).  It's in the bottom middle of the
building, the heat just rises right out.

Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373


On Mon, Aug 12, 2019 at 8:16 AM can...@believewireless.net <
p...@believewireless.net> wrote:

> You don't need an inverter generator but you may need to adjust the
> sensitivity in the
> UPS. Our Tripplites work fine but APC needs to be adjusted.
>
> On Sun, Aug 11, 2019 at 11:51 PM Rhys Cuff (Latrobe IT) <
> r...@latrobeit.com.au> wrote:
>
>> Hi Guys
>>
>>
>>
>> I’m after a small 5kva generator for the server room
>>
>> Will be feeding a 3kva ups.
>>
>>
>>
>> Do you think its required to get an inverter generator?
>>
>> Being is only going to be used as a charger and the UPS will clean the
>> power up.
>>
>>
>>
>> Thanks
>>
>>
>>
>> Rhys
>>
>>
>>
>>
>> --