That was definitely the case

On Tue, Aug 13, 2019, 12:58 PM Josh Luthman <j...@imaginenetworksllc.com>
wrote:

> Maybe the private power generator was better quality than the public
> government run service?
>
> Josh Luthman
> Office: 937-552-2340
> Direct: 937-552-2343
> 1100 Wayne St
> Suite 1337
> Troy, OH 45373
>
>
> On Tue, Aug 13, 2019 at 11:15 AM Lewis Bergman <lewis.berg...@gmail.com>
> wrote:
>
>> The typical standard is a generator should be able to produce twice the
>> amperage of the load you expect. Maybe thats because genset guys like
>> selling bigger generators but all the docs I have seen from UPS
>> manufacturers state the same thing. They all produce cleaner power at the
>> mid range of what they are capable of.
>>
>> When we had a 100kva genset on a 25kva load you could always tell when it
>> went from power company 408 to genset because all three legs of power would
>> become perfect and in balance for the period it ran. Once it flipped back
>> to mains power they converted back to their normal out of whack state.
>>
>> On Tue, Aug 13, 2019 at 9:25 AM Chuck McCown <ch...@wbmfg.com> wrote:
>>
>>> It will run cooler too.
>>>
>>> Sent from my iPhone
>>>
>>> > On Aug 12, 2019, at 8:53 PM, Adam Moffett <dmmoff...@gmail.com> wrote:
>>> >
>>> > I might be a weirdo, but I figure a 50amp subpanel is 12kva, so I got
>>> a 16kva generator for the 50 amp sub-panel fed by a 50 amp breaker from the
>>> main panel.
>>> >
>>> > The reason for the generator being bigger than the sub-panel is that
>>> you can't put 12kva on the 12kva generator unless you perfectly balance
>>> both hot legs.  Since that won't happen, I bump the generator up a notch.
>>> It's a sub-panel so if someone ever trips the 50amp breaker we'll know
>>> right away that there's more load than the generator could handle rather
>>> than finding out when the power is out and nobody's there.
>>> >
>>> >
>>> >> On 8/12/2019 9:34 AM, Chuck McCown wrote:
>>> >> I would get the one larger than you need with an automatic transfer
>>> switch.  I have had ok luck with geneac units.  You want it large enough to
>>> be able to start the hvac system,
>>> >>
>>> >> Sent from my iPhone
>>> >>
>>> >>> On Aug 11, 2019, at 9:51 PM, Rhys Cuff (Latrobe IT) <
>>> r...@latrobeit.com.au> wrote:
>>> >>>
>>> >>> --_000_98489c14e6d04e6dbe7ba554592e77b2latrobeitcomau_
>>> >>> Content-Type: text/plain; charset="us-ascii"
>>> >>> Content-Transfer-Encoding: quoted-printable
>>> >>>
>>> >>> Hi Guys
>>> >>>
>>> >>> I'm after a small 5kva generator for the server room
>>> >>> Will be feeding a 3kva ups.
>>> >>>
>>> >>> Do you think its required to get an inverter generator?
>>> >>> Being is only going to be used as a charger and the UPS will clean
>>> the powe=
>>> >>> r up.
>>> >>>
>>> >>> Thanks
>>> >>>
>>> >>> Rhys
>>> >>>
>>> >>>
>>> >>>
>>> >>> --_000_98489c14e6d04e6dbe7ba554592e77b2latrobeitcomau_
>>> >>> Content-Type: text/html; charset="us-ascii"
>>> >>> Content-Transfer-Encoding: quoted-printable
>>> >>>
>>> >>> <html xmlns:v=3D"urn:schemas-microsoft-com:vml"
>>> xmlns:o=3D"urn:schemas-micr=
>>> >>> osoft-com:office:office"
>>> xmlns:w=3D"urn:schemas-microsoft-com:office:word" =
>>> >>> xmlns:m=3D"http://schemas.microsoft.com/offi
>>> >
>>> >
>>> > --
>>> > AF mailing list
>>> > AF@af.afmug.com
>>> > http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>>>
>>> --
>>> AF mailing list
>>> AF@af.afmug.com
>>> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>>>
>>
>>
>> --
>> Lewis Bergman
>> 325-439-0533 Cell
>> --
>> AF mailing list
>> AF@af.afmug.com
>> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>>
> --
> AF mailing list
> AF@af.afmug.com
> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>
-- 
AF mailing list
AF@af.afmug.com
http://af.afmug.com/mailman/listinfo/af_af.afmug.com