Electric "can" be more cost effective unless you have to run wires a half kilometer or more. Our first remote POP was not quite a 1/4 mile from the nearest electric source, so we had to trench that distance, run conduit, and run relatively large gauge wires that distance. At that time, the cost of the copper alone exceeded the cost of doing it in solar. Today, the cost of the solar is a fraction of what it was then, and LFP batteries are now cost-competitive with SLA batteries.

That all said, we are at a convenient latitude (37°), and we have a pretty moderate climate, so heating and cooling are not a consideration, and we get at least 6 hours of sun on the shortest day of the year.

bp
<part15sbs{at}gmail{dot}com>

On 8/15/2023 9:38 AM, [email protected] wrote:

I can save you the suspense.  If you have access to electric that’ll be cheaper than solar.  The problem is the need to run 24/7.  You have to design around the December-January months.  I’m in NY State, and at our latitude we only get a few hours of average production per day during those months.  And obviously if it’s snowing for a week you need to be able to ride through that on mostly battery power.  Even with a modest load it takes a silly amount of panels and batteries to stay up 24/7 in the winter.  More than you’d ever be allowed to put on a utility pole.

Talk to your electric co about the smallest service you can get.  Explain what you’re trying to do and that your max load is very low.

NYSEG normally doesn’t do less than 100A, but they made an exception and let us do 60A.  You need a meter can, a service rated panel, a conduit up the pole and a weatherhead.  Then you either have an outdoor outlet, or have an outlet inside your enclosure.  You’ll want the smallest service they’ll let you do because of the wire size on the service cable.  A 20A (if they’d allow it) would only need a 12/3 with ground, and that’s up to 4800 Watts (240x20) so it’s still more than you’d ever need.   A 12/3 is way cheaper than a 100A service entrance cable.

My figure is 8 years old, and obviously there’s been inflation since then, but I went to the same contractor who does electric installs for the cable company and they quoted me about $1000.  Even if it’s 3x that for you today you’d still never beat that with a solar installation even if they’d let you do it.  And I’m not some knee-jerk anti-solar lunatic, I’m just saying I’ve run the numbers and it doesn’t add up.   People do it when they’re off grid, or when the electric service is unreliable in the area, or sometimes just for the PR/marketing power of being “solar powered”.  Those are all fine reasons, but doing it for cost savings isn’t going to work out.

-Adam

*From:* AF <[email protected]> *On Behalf Of *Steve Jones
*Sent:* Tuesday, August 15, 2023 10:27 AM
*To:* AnimalFarm Microwave Users Group <[email protected]>
*Subject:* Re: [AFMUG] battery nerd question

we have a dozen or so, but are looking at pole mount micropops (our own poles). We are losing a grain elevator site because they decommissioned the elevator and theres no real options for the customers in some of the areas. Im just trying to get to something we can get solar power with enough battery to last through overcast. So Im calculating per battery runtimes, then will look at number of batteries we would need to survive vs paying for a ROW meter vs losing the customers. Just have to get to the cost per customer to retain them and the benefit gained per pole

On Tue, Aug 15, 2023 at 8:53 AM Brian Webster <[email protected]> wrote:

    How many of the batteries do you have? Do you need any voltages
    other than the 48 volts? If you have 4 batteries and only need 48
    volts then wire them in series and not have to deal with the
    converter.

    Thank you,

    Brian Webster

    *From:*AF [mailto:[email protected]] *On Behalf Of
    *[email protected]
    *Sent:* Tuesday, August 15, 2023 6:59 AM
    *To:* 'AnimalFarm Microwave Users Group'
    *Subject:* Re: [AFMUG] battery nerd question

    *You’re around C/30 which should be on the high end /of capacity/.

    Lower load usually means a little extra capacity out of the
    battery.  I realized that sentence might have been ambiguous.

    *From:* [email protected] <[email protected]>
    *Sent:* Tuesday, August 15, 2023 6:56 AM
    *To:* 'AnimalFarm Microwave Users Group' <[email protected]>
    *Subject:* RE: [AFMUG] battery nerd question

    You can do the whole thing in Watts.

    12V * 150ah = 1800 Watt-hours

    1800Wh / 50W = 36 hours

    If they’re telling me 95% efficiency, I’d assume 50W out needs 53W
    in (50 / 0.95).

    There’s usually an efficiency curve for the device based on load
    and temperature so it wouldn’t be 95% in all circumstances.  Your
    system should be drawing less than 5A off the battery, and if your
    multimeter has a 10A fuse like most do, then you could put the
    meter in line and actually measure the amperage before and after
    the converter.  Then you’d know for sure.

    And the battery’s total capacity will have a curve based on C-rate
    so there’s some variability there too. Usually it lasts longer
    when you’re drawing lower amperage.  You’re around C/30 which
    should be on the high end.

    Age and maintenance of the battery affect runtime as well.  If I
    want 6 hours of runtime then I plan Ah for 12 hours runtime. When
    my batteries are halfway toasted I’m still getting useful life out
    of them.

    *From:* AF <[email protected]> *On Behalf Of *Steve Jones
    *Sent:* Monday, August 14, 2023 9:57 PM
    *To:* AnimalFarm Microwave Users Group <[email protected]>
    *Subject:* [AFMUG] battery nerd question

    Just trying to cipher runtimes

    I have on hand 150ah 12 volt batteries, so thats what id
    be looking to use.

    Excluding the conversion loss of a 12v to 48v step up converter is
    the math correct here?

    12v 150ah=1800 watt hours
    1800 watt hours at 48v = 37.5ah
    50 watts of radio running 48v = 1.04 amps
    37.5ah @ 1.04 amps = 32.77 hours runtime

    does a step up that claims 95% efficiency mean 95% of the watt hours?

-- AF mailing list
    [email protected]
    http://af.afmug.com/mailman/listinfo/af_af.afmug.com

-- 
AF mailing list
[email protected]
http://af.afmug.com/mailman/listinfo/af_af.afmug.com