Is the Generator actually grounded ?  most small generators are not.

Are you running AC Powered equipment ? you could always convert to DC right at 
the tower and bring it over to your side.

You can always use a surge protector on the AC line as well.

Regards.

Faisal Imtiaz
Snappy Internet & Telecom
7266 SW 48 Street
Miami, FL 33155
Tel: 305 663 5518 x 232

Help-desk: (305)663-5518 Option 2 or Email: [email protected] 

----- Original Message -----
> From: "Adam Moffett" <[email protected]>
> To: [email protected]
> Sent: Monday, June 8, 2015 5:57:20 PM
> Subject: [AFMUG] More Grounding stuff
> 
> I'm at a site where two towers are about 250' apart.  There's a 2"
> conduit between the two towers, with nothing in it but a fiber optic
> cable.  My tower does not have a generator, but the other one does. The
> guy at the other tower offered to let me run electric off of a breaker
> on his transfer panel so I could have a generator protected circuit.
> This sounds great in theory, but I have a bad feeling about it because
> (obviously) we have two separate electric services now and two separate
> grounding systems.
> 
> If I don't bond the grounds together it seems like different potentials
> at each site could equalize by passing energy through the ground/neutral
> wire of this theoretical power line, and it would get there via my
> equipment and blow something up in the process.
> 
> ....but on the other hand, is bonding the grounds together something
> that's actually ok to do?
> 

Reply via email to