The tanks are like these:

http://www.mscivilengineers.com/images/12.jpg

I'm not sure what the bottom looks like, though.  I'll have to go out and
check them.  So, you ran #6 all the way down the tank and bonded it inside
of your enclosure/cabinet/whatever?

On Mon, Sep 28, 2015 at 10:31 AM, Mark Radabaugh <[email protected]> wrote:

> What type of tank?
>
> The hydropillar and waterspherioid style are generally well grounded.
>
> I have seen some of the steel tank on a concrete pedestal style where the
> tank is not directly grounded to the pedestal but has a ‘spark gap’ between
> the tank and the base.  I’m not sure if the purpose was to distribute the
> strike around the tank into the rebar in the column, or if it was an
> attempt to isolate the steel for corrosion reasons.   The tank we are on
> like that consistently has the most lightning damage.   I eventually ran a
> #6 copper from the top of the tank to the railing and down inside to tie
> everything together.  It’s improved the situation considerably but it’s
> still not perfect.
>
> Mark Radabaugh
> Amplex
> 27800 Lemoyne, Ste F
> Millbury, OH 43447
> 419-837-5015 x1021
> [email protected]
>
> On Sep 28, 2015, at 10:19 AM, Adam Moffett <[email protected]> wrote:
>
> Yeah, I would think the tank itself is ground.
>
> On 9/28/2015 10:16 AM, Chuck McCown wrote:
>
> Common point grounding at the power ground would be the NEC answer.
>
> I would do that for power grounds and surge suppressor grounds because
> most surges come via the power lines.
>
> For antenna mounting grounds etc, I would make sure they were in good
> contact (bonded, perhaps with a separate bonding wire) to the tank or
> railing or whatever metal structure you are attaching to.
>
> *From:* Josh Baird <[email protected]>
> *Sent:* Monday, September 28, 2015 8:13 AM
> *To:* [email protected]
> *Subject:* [AFMUG] Grounding strategies for water tanks
>
> We are going to be installing on several water tanks that do not have any
> other carriers on them.  I'm assuming there is probably not a ground ring
> or system in place at these sites.  The electrical service is likely
> grounded independently using a ground rod at the pole.
>
> These sites will have batteries and a charger at the bottom and fiber/DC
> up the tower. Admittingly, I'm fairly (ok, very) stupid when it comes to
> grounding systems.  I understand that everything *should* be bonded
> together.  However, if the tank it's self doesn't have a sufficient
> grounding system already in place, what is the best strategy here?
>
> Thanks,
>
> Josh
>
>
>
>
>
>

Reply via email to