Does the transfer switch just switch the two main hot legs? I assume so or you would not be asking.
No problem bonding gen neutral to gnd. But how do your loads get a good bonded neutral when on utility power if you lift that bond? I think you are safe in keeping them all connected. With the gen neutral bonded at the transfer switch, there should not be any risk of a neutral floating high and back feeding the sub panel. Am I missing something? From: Adam Moffett Sent: Monday, August 15, 2016 1:16 PM To: Animal Farm Subject: [AFMUG] Ground-Neutral bond for generator subpanel I was planning to add a Generac to a site and connect the transfer switch to a subpanel rather than the main panel. The "utility" input to the transfer switch would come from a 50-amp breaker in the main service panel. I was thinking I would remove the ground-neutral bond in the transfer switch and the subpanel, and that's fine as long as we're on utility power. It occurred to me today that when the transfer switch triggers and we switch to generator power that we'll lose the ground-neutral bonding in the main panel....and there would no longer be any ground-neutral bond anywhere until it switches back. I could easily add a 4ga ground-neutral jumper inside the generator, but I'm wondering if that's Kosher. I have an electrician I can ask, but I was hoping somebody here happens to know whether that's ok.