I was assuming the transfer switch switched everything, but I double
checked after reading your email and it turns out yeah I'm being a
dummy. The xfer switch only switches the hot wires. Neutral is always
connected....so I guess I always have the N-G connection in the main
panel where it should be.
------ Original Message ------
From: "Chuck McCown" <[email protected]>
To: "Animal Farm" <[email protected]>
Sent: 8/15/2016 3:24:36 PM
Subject: Re: [AFMUG] Ground-Neutral bond for generator subpanel
Does the transfer switch just switch the two main hot legs? I assume
so or you would not be asking.
No problem bonding gen neutral to gnd.
But how do your loads get a good bonded neutral when on utility power
if you lift that bond?
I think you are safe in keeping them all connected. With the gen
neutral bonded at the transfer switch, there should not be any risk of
a neutral floating high and back feeding the sub panel.
Am I missing something?
From:Adam Moffett
Sent: Monday, August 15, 2016 1:16 PM
To:Animal Farm
Subject: [AFMUG] Ground-Neutral bond for generator subpanel
I was planning to add a Generac to a site and connect the transfer
switch to a subpanel rather than the main panel. The "utility" input
to the transfer switch would come from a 50-amp breaker in the main
service panel.
I was thinking I would remove the ground-neutral bond in the transfer
switch and the subpanel, and that's fine as long as we're on utility
power. It occurred to me today that when the transfer switch triggers
and we switch to generator power that we'll lose the ground-neutral
bonding in the main panel....and there would no longer be any
ground-neutral bond anywhere until it switches back.
I could easily add a 4ga ground-neutral jumper inside the generator,
but I'm wondering if that's Kosher.
I have an electrician I can ask, but I was hoping somebody here happens
to know whether that's ok.