Yes, minimum of 16 amps for the AC and 7.5 for the DC.  

And DC  breakers are special, do not use an AC breaker on DC.
 
You can short out both breakers with a jumper for for a short amount of time 
until the batts get a bit of a charge.  Probably only take a few minutes.  

From: Josh Baird 
Sent: Sunday, May 28, 2017 11:44 AM
To: [email protected] 
Subject: Re: [AFMUG] Traco TSP+BCM Question

Ok - so this is what I was thinking.  I thought my breakers were rated for much 
more current, but it looks like they are only rated for 5A (both AC [1] and 
BATT [2]). 

In short - I need a breaker that can handle more current, correct?  I have 
these breakers at a ton of sites.. can't believe I just noticed they were only 
rated for 5A. :(  In the meantime, I may need to use an external charger to get 
these batteries charged back up.

[1] http://www.alliedelec.com/altech-corp-2c5um/70076204/
[2] http://www.alliedelec.com/altech-corp-1c5um/70076445/

On Sun, May 28, 2017 at 1:36 PM, Chuck McCown <[email protected]> wrote:

  360 recommends a 16 amp or greater circuit for the AC.
  And it will only make 7.5 amps.  Almost any batter discharged that much will 
take 100% of that 7.5 amps when starting to charge.  I would set the battery 
circuit breaker to be higher than 7.5 amps to prevent this problem.  

  From: Josh Baird 
  Sent: Sunday, May 28, 2017 11:30 AM
  To: [email protected] 
  Subject: Re: [AFMUG] Traco TSP+BCM Question

  This site has about 180-200W of load.  The TSP power supply is 360W.  I know 
the BCM has about a ~55W overhead for charging, so that should still leave 
plenty of headroom, wouldn't you think?

  On Sun, May 28, 2017 at 1:19 PM, Bill Prince <[email protected]> wrote:

    Might be as simple as your AC circuit is too small for the whole load. The 
key questions are (1) What is the load of your equipment?, and (2) What is the 
bulk charge load on your controller?

    Add those two together to understand what the total load should be.


    bp
    <part15sbs{at}gmail{dot}com> 


    On 5/28/2017 9:19 AM, Josh Baird wrote:

      I have a site with a TSP+BCM 48V combo.  Last night, something caused the 
AC breaker to trip, putting the site on battery.  We didn't see the alert until 
about 12 hours later.  At this point, the batteries were down to ~42V.  When 
our guy arrived on site, he reset the AC breaker, and AC power was restored.  
Immediately, the battery breaker (breaker between positive side of the 
batteries and the BCM) tripped.

      Now, each time that we reset the battery breaker, it causes the AC 
breaker to immediately trip.  At this point, the site is up on AC with no 
battery.  Any ideas what would be causing this?  Do you think the batteries are 
causing the BCM to draw too much current?  Could one (or more) of the batteries 
be dead/bad?  The site *did* run successfully on battery for nearly 12 hours.

      Josh