On 5/28/17 10:44 AM, Josh Baird wrote:
Ok - so this is what I was thinking. I thought my breakers were rated for much more current, but it looks like they are only rated for 5A (both AC [1] and BATT [2]).

In short - I need a breaker that can handle more current, correct? I have these breakers at a ton of sites.. can't believe I just noticed they were only rated for 5A. :( In the meantime, I may need to use an external charger to get these batteries charged back up.

[1] http://www.alliedelec.com/altech-corp-2c5um/70076204/


Other than making sure you have the right size breaker for running load, that's a C curve breaker. Ideally for things with high inrush like power supplies and transformers you should prefer a D curve, which have a higher 100ms trip point at 20xRC. The C curve is 10xRC at 100ms.

See the table here:
http://www.altechcorp.com/breakers/R-Series.html

~Seth