Gave up flooded years ago.  Had a few sites where the APC exploded the
batteries.  Even when that didn't happen, I got tired of the yearly battery
check and fill at all the sites.  When I started my own company I switched
to AGM and never looked back.  They are amazing.  Also, we don't use APCs
anymore except at a couple of large sites where we use the 3000XL, which
has a much better charging system.

On Fri, Jan 5, 2018 at 6:38 AM, David M <[email protected]> wrote:

> there is always an evaporation issue with flooded..
>
> They have to be maintained on a regular schedule in order to have extended
> life beyond 5 yrs
>
> AGM/GEL expensive but reliable with little maintenance. Give em a good
> home and little venting and get
>
> 7 to 10 with those.
>
>
>
>
>
> On 1/4/2018 3:47 PM, Robert Andrews wrote:
>
>> Sounds like a problem with the Charge controller being incorrectly set.
>> If this is on-grid, I would lower the voltage the charge controller is
>> maintaining and make sure it is set to NOT do any equalize cycles.
>>
>> Then flooded should be better.  Of course if the environment is causing
>> evaporation that is a different problem.
>>
>> I didn't find telecom batteries were worth the expense.  So if I dumped
>> wet, I would probably go with sealed Marine..
>>
>> Best,
>>     Robert
>>
>> On 01/04/2018 01:38 PM, TJ Trout wrote:
>>
>>> I have been really liking flooded batteries over the last 10 years or so
>>> because I am able to service the battery and extend the life but I am
>>> finding that on sites that I forget to add distilled water at least twice a
>>> year sometimes the batteries dry out due to the charge controller over
>>> gassing the batteries.
>>>
>>> Right now I'm trying to decide between Walmart deep Cycles, rack mount
>>> telecom batteries or just sealed RV Marine deep cycle batteries.
>>>
>>> What is the best bang-for-the-buck currently considering the life span
>>> and capacity ?
>>>
>>> Thanks
>>>
>>> TJ
>>>
>>
>

Reply via email to