No, I mean you can parallel as many -48VDC input sides as you want, off a
bus bar or battery setup, assuming that the wiring is set up right. The
120VAC outputs would of course be totally independent. Depending on your
requirements it could be a better solution to a 1+0 "all eggs in one
basket" large inverter setup, where if the inverter dies, all AC loads go
down. In the sort of arrangement I mentioned the AC loads for things with
dual power supplies could be built as 1+1.

On Thu, May 10, 2018 at 7:30 AM, <[email protected]> wrote:

> When you say you can parallel as many as you want, but then say to limit
> the load on individual units, that does not sound like all the outputs are
> combined to me.
>
> Do you actually combine the outputs in parallel?
>
> If so you really cannot limit current to individual units, the load will
> divide across the inverters based on internal and external impedances.
>
> *From:* Eric Kuhnke
> *Sent:* Wednesday, May 9, 2018 8:10 PM
> *To:* [email protected]
> *Subject:* Re: [AFMUG] 48 vdc Inverteres for Data Room 6kw ?
>
> You could also look into individual 1500W meanwell true sine wave
> inverters, running in parallel off your 48vdc battery bus. You can parallel
> as many as you need. Don't load any individual one with more than 1300W
> constant. Wire up the output from each meanwell to 120vac PDUs with
> amperage meter inline and distribute from there.
>
> On Tue, May 8, 2018, 12:58 PM Gino A. Villarini <[email protected]> wrote:
>
>> Looking for 48 vdc inverters for data room applications in the range of
>> 6-8 kw
>>
>> Can be a all in one system ( charger plus Inverter) , must be always
>> online
>>
>>
>>
>> *Gino A. Villarini*
>> President
>> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>>
>>