No, I mean you can parallel as many -48VDC input sides as you want, off a bus bar or battery setup, assuming that the wiring is set up right. The 120VAC outputs would of course be totally independent. Depending on your requirements it could be a better solution to a 1+0 "all eggs in one basket" large inverter setup, where if the inverter dies, all AC loads go down. In the sort of arrangement I mentioned the AC loads for things with dual power supplies could be built as 1+1.
On Thu, May 10, 2018 at 7:30 AM, <[email protected]> wrote: > When you say you can parallel as many as you want, but then say to limit > the load on individual units, that does not sound like all the outputs are > combined to me. > > Do you actually combine the outputs in parallel? > > If so you really cannot limit current to individual units, the load will > divide across the inverters based on internal and external impedances. > > *From:* Eric Kuhnke > *Sent:* Wednesday, May 9, 2018 8:10 PM > *To:* [email protected] > *Subject:* Re: [AFMUG] 48 vdc Inverteres for Data Room 6kw ? > > You could also look into individual 1500W meanwell true sine wave > inverters, running in parallel off your 48vdc battery bus. You can parallel > as many as you need. Don't load any individual one with more than 1300W > constant. Wire up the output from each meanwell to 120vac PDUs with > amperage meter inline and distribute from there. > > On Tue, May 8, 2018, 12:58 PM Gino A. Villarini <[email protected]> wrote: > >> Looking for 48 vdc inverters for data room applications in the range of >> 6-8 kw >> >> Can be a all in one system ( charger plus Inverter) , must be always >> online >> >> >> >> *Gino A. Villarini* >> President >> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 >> >>