Thanks Drew.

I wasn't mixing my concepts, I was falsely believing APC SmartUPS series and
above were all Online rather than "Line-Interactive" (APC's terminology)
therefore conditioning circuitry was not necessary. So much for me thinking
the server at home had an online supply!

So ...
Online UPS = conditioning not needed due to design
Line Interactive = must have good conditioning circuits/do your
homework/looks like most APC models fit here.

-dbc.

-----Original Message-----
From: Drew Gibson [mailto:[email protected]] 
Sent: April-07-09 5:15 PM
To: David Cook
Cc: [email protected]
Subject: Re: [biz] UPS: power conditioned

 I think you might be mixing two different UPS concepts here.

This can be a contentious subject but if I may be allowed to simplify....

The best UPSs (eg larger and more expensive, say >8KVA) are online, 
full-time. They constantly convert the AC in to DC, feed it to the 
batteries and then draw the load as DC and convert it back to AC to 
supply the load device.

Most of the of UPSs the small to mid-size, affordable UPSs are only 
fully online when the mains power fails and power from the batteries is 
required. There is a short (very short) interval during a power failure 
as the UPS switches the supply from the AC input to battery. Otherwise 
the AC is fed straight through to the load device.

In the first case, power conditioning is done by default as the power is 
always being processed and "conditioned". This is the best type in terms 
of protecting your computers, but hard on the budget.

In the second case, power conditioning has to be added. Most reasonable 
devices will, in fact, condition the power to some extent. They will 
moderate high input voltages, boost sags in the voltage (by drawing from 
battery) and suppress spikes and surges. This type is a little less 
capable in terms of protecting equipment but the lower price makes up 
for that and more.

APC do make both types as do Tripp-Lite and others.

Since phone systems are expected to operate during power outages for 
much longer than regular servers, I would recommend the second type due 
to cost. I would oversize the UPS (they are usually sized by power 
rather than runtime) to get a longer runtime. Both APC and Tripp-Lite 
make units that can have external batteries added for additional 
runtime. The last one I spec'd would run the Asterisk server and the 
VoIP switches for 3-4 hours. (APC 2200XL rackmount, if I remember rightly)

regards,

Drew



David Cook wrote:
> I believe all APC upses qualify in that regard. Conditioning should refer
to
> methods of ensuring that transients and other oddities from the power line
> never reach the equipment plugged into them.
>
> My understanding is that all APC upses (and most other "good" upses) are
of
> the variety that the line power only serves to charge the batteries -
> nothing more. The batteries subsequently feed constant power into the
> inverters which create the 110VAC (hopefully a sine wave) to power the
> equipment. Therefore at no time are the products plugged into the UPS ever
> connected to the line current and therefore not subject to stuff outside
> affecting your equipment.
>
> The analogy used to explain it to me was filling a bucket (batteries) with
> water with a fixed size hole in the bottom (VA rating of the UPS). As long
> as some volume of water is retained in the bucket, you can fill the bucket
> evenly or sporadically but the flow rate out the hole remains the same.
>
> If my understanding of this is full of crap, please let me know :-)
>
> -dbc
>
> -----Original Message-----
> From: Frank Bax [mailto:[email protected]] 
> Sent: April-07-09 3:00 PM
> To: [email protected]
> Subject: [biz] UPS: power conditioned
>
> In the Asterisk book from O'Reilly; it says "Make sure your UPS is power 
> conditioned. If it doesn't say exactly that, it isn't."
>
>
http://astbook.asteriskdocs.org/en/2nd_Edition/asterisk-book-html-chunk/aste
> risk-CHP-2-SECT-2.html#asterisk-CHP-2-SECT-2.1
>
> I don't see this wording on any UPS devices from APC; do they sell one? 
>   If not, who does?
>
> Frank
>
> ---------------------------------------------------------------------
> To unsubscribe, e-mail: [email protected]
> For additional commands, e-mail: [email protected]
>
>
> ---------------------------------------------------------------------
> To unsubscribe, e-mail: [email protected]
> For additional commands, e-mail: [email protected]
>
>
>   


---------------------------------------------------------------------
To unsubscribe, e-mail: [email protected]
For additional commands, e-mail: [email protected]

Reply via email to