Chances are if you follow that line coming from your house you'll be able to 
trace it back to the electrical box inside...  If that is the case, just take 
the ground lug from your generator run it to the ground from the house and use 
a cable clamp to join the 2 together.  A cable clamp is like a muffler clamp on 
a smaller scale.  It will have a threaded rod bent in a horseshoe shape or some 
are rectangular, threads on both ends and a piece that will come off of the 
threaded rod.  Sandwich the 2 grounds between the rods and the piece that comes 
off, run the washers and then the nuts on and tighten everything up.  This will 
save you hours of frustration and cancel the entertainment for the neighbors.
  ----- Original Message ----- 
  From: Edward Przybylek 
  To: [email protected] 
  Sent: Monday, December 17, 2007 10:56 PM
  Subject: RE: [BlindHandyMan] Generator Grounding Follow-UP


  Hi Ron,

  I went outside and took a look around my electric meter to see if there is
  any kind of grounding cable near the box. Lo and behold, there is a fairly
  thick cable coming out of the side of the house and going into the ground.
  I poked down into the dirt around the cable but was unable to find a rod
  connected to it. If there is a rod, my guess is that it is buried several
  inches below the top of the soil. How would I find out if it is a ground
  cable? Would following the cable on the inside of the house tell me
  anything? If it is a ground cable, is there any reason not to connect to
  this cable and use it as a ground for my generator? How would I connect my
  generator grounding cable to the cable coming out of my home. As always,
  any help greatly appreciated.

  Take care,
  Ed



  _____ 

  From: [email protected] [mailto:[EMAIL PROTECTED]
  On Behalf Of Ron Yearns
  Sent: Monday, December 17, 2007 10:21 PM
  To: [email protected]
  Subject: Re: [BlindHandyMan] Generator Grounding Follow-UP

  Well guys lucky for me and probable unlucky for you all I found my copy of
  the 1996 National Eclectric Code. It had went missing since I had moved. The
  box was marked science and math books. Stranger yet it also contained my
  books on upholstery and furniture repair. Well anyway here is some info on
  the grounding of generators.

  Article 250-83, c discusses rod and pipe electrodes. Yes galvanized pipe of
  three quarters of an inch or larger may be used as well as five eights inch
  diameter copper clad steel rod. Both are required to be a minimun of eight
  feet in length. They are to be driven to a depth of eight feet.. Flush or
  preferable below the finished grade. If rocks prevent this it may be driven
  at an angle between 90 and 45 degrees. If this is not possible it maybe
  buried in a trench no less than 30 inches in depth.

  Note plate electrodes may also be used, but most choose the rods.

  Article 250-94 table shows the smallest copper conductor to ground a service
  with current carrying conductors of number 1 or smaller to be number 8 if
  copper.

  Article 250-92 a speaks to protecting equipment grounding conductors. If
  they are exposed to physical harm all need to be in conduit. If not exposed
  to physical harm then number 6 and larger may be run along the structure and
  secured to it. Number 8 or smaller must be en conduit regardless.

  I found nothing in the Code that would permit using two four foot rods and
  tieing them together. The angle driving or trench permits the full eight
  foot lenth to be used. Best to use one of those methods.

  Now for installing the rod. Don't grab a hammer and try to pound it all the
  way. Dig a hole out away from any building footings. Usually two feet. Make
  the hole about a least a foot deep and big enough you can fasten the clamp
  and wire on the rod. Shove the rod down by hand as far as you can, by
  pumping up and down. Pull the rod out of that hole, pour the hole full of
  wwater. Reinsert the rod after a little time of waiting or maybe refilling
  the hole if the water goes down quickly. Repeat the pumping up and down with
  the rod by hand until it stops going easy. Pull the rod out refill with
  water and keep repeating this process until re moval is too difficult then
  resort to the sledge hammer. Usually you can get the rod down at least four
  to six foot before you need the hammer. This technique is called watter
  jetting and is also used with other equipment for horizontal boring under
  highways and streets for utility lines and pipes.

  Another note if this generator is located close to the main service point on
  the house there may all ready be a rod buired under the meter. It might be
  easier to dig it up until the wire to it is found and you could split bolt
  to it.
  Luck to you,
  Ron
  ----- Original Message ----- 
  From: Edward Przybylek 
  To: BlindHandyMan 
  Sent: Sunday, December 16, 2007 9:13 PM
  Subject: [BlindHandyMan] Generator Grounding Follow-UP

  Hi all,

  After all your replies, I decided to ground my new generator. Better safe
  then sorry. When the manual said that not grounding the generator could
  pose the threat of electricution, it made me decide it was the best course
  of action. I went to Home Depot to purchase the necessary supplies. I
  picked up a lenght of 10 gauge stranded copper wire and then went to search
  for the copper grounding rod. The thing you guys forgot to mention is that
  the freaking rod is 8 feet long. I asked the associate how much of the rod
  I should cut off the 8 foot length to pound into the ground. That's when he
  said "All 8 feet." My first response was "Are you for real!" My soil is 5%
  dirt and 95% rock. Getting 8 feet of anything that deep in my yard is going
  to be a task meant for the Gods and not a mere mortal like myself. The last
  time I pounded any kind of rod into my yard was a galvanized pipe to support
  a newly planted evergreen to help it make it through the winter. It went
  down approximately 3 feet and stopped dead. I mushroomed the top of the
  pipe with a four pound mallet but the pipe went no further. Now you expect
  me to pound an 8 foot copper rod into the ground! Yeah, right. What I'm
  anticipating is a very bent rod and a flurry of filthy words that till make
  the ladies in the neighbor hood blush wildly and hurry their children
  indoors. From now on, gentlemen, make sure you mention the finer points of
  a task before making recommendations. <big smile> Let you know how it
  goes.

  Take care,
  Ed

  [Non-text portions of this message have been removed]