as for connecting the two ground wires togeather he should have 
someone see if there is a coating of paint or the like on the house wire.
if there is nothing will ground.
jim
At 05:10 AM 12/18/2007, you wrote:

>Chances are if you follow that line coming from your house you'll be 
>able to trace it back to the electrical box inside... If that is the 
>case, just take the ground lug from your generator run it to the 
>ground from the house and use a cable clamp to join the 2 together. 
>A cable clamp is like a muffler clamp on a smaller scale. It will 
>have a threaded rod bent in a horseshoe shape or some are 
>rectangular, threads on both ends and a piece that will come off of 
>the threaded rod. Sandwich the 2 grounds between the rods and the 
>piece that comes off, run the washers and then the nuts on and 
>tighten everything up. This will save you hours of frustration and 
>cancel the entertainment for the neighbors.
>----- Original Message -----
>From: Edward Przybylek
>To: <mailto:blindhandyman%40yahoogroups.com>[email protected]
>Sent: Monday, December 17, 2007 10:56 PM
>Subject: RE: [BlindHandyMan] Generator Grounding Follow-UP
>
>Hi Ron,
>
>I went outside and took a look around my electric meter to see if there is
>any kind of grounding cable near the box. Lo and behold, there is a fairly
>thick cable coming out of the side of the house and going into the ground.
>I poked down into the dirt around the cable but was unable to find a rod
>connected to it. If there is a rod, my guess is that it is buried several
>inches below the top of the soil. How would I find out if it is a ground
>cable? Would following the cable on the inside of the house tell me
>anything? If it is a ground cable, is there any reason not to connect to
>this cable and use it as a ground for my generator? How would I connect my
>generator grounding cable to the cable coming out of my home. As always,
>any help greatly appreciated.
>
>Take care,
>Ed
>
>_____
>
>From: 
><mailto:blindhandyman%40yahoogroups.com>[email protected] 
>  [mailto:[EMAIL PROTECTED]
>On Behalf Of Ron Yearns
>Sent: Monday, December 17, 2007 10:21 PM
>To: <mailto:blindhandyman%40yahoogroups.com>[email protected]
>Subject: Re: [BlindHandyMan] Generator Grounding Follow-UP
>
>Well guys lucky for me and probable unlucky for you all I found my copy of
>the 1996 National Eclectric Code. It had went missing since I had moved. The
>box was marked science and math books. Stranger yet it also contained my
>books on upholstery and furniture repair. Well anyway here is some info on
>the grounding of generators.
>
>Article 250-83, c discusses rod and pipe electrodes. Yes galvanized pipe of
>three quarters of an inch or larger may be used as well as five eights inch
>diameter copper clad steel rod. Both are required to be a minimun of eight
>feet in length. They are to be driven to a depth of eight feet.. Flush or
>preferable below the finished grade. If rocks prevent this it may be driven
>at an angle between 90 and 45 degrees. If this is not possible it maybe
>buried in a trench no less than 30 inches in depth.
>
>Note plate electrodes may also be used, but most choose the rods.
>
>Article 250-94 table shows the smallest copper conductor to ground a service
>with current carrying conductors of number 1 or smaller to be number 8 if
>copper.
>
>Article 250-92 a speaks to protecting equipment grounding conductors. If
>they are exposed to physical harm all need to be in conduit. If not exposed
>to physical harm then number 6 and larger may be run along the structure and
>secured to it. Number 8 or smaller must be en conduit regardless.
>
>I found nothing in the Code that would permit using two four foot rods and
>tieing them together. The angle driving or trench permits the full eight
>foot lenth to be used. Best to use one of those methods.
>
>Now for installing the rod. Don't grab a hammer and try to pound it all the
>way. Dig a hole out away from any building footings. Usually two feet. Make
>the hole about a least a foot deep and big enough you can fasten the clamp
>and wire on the rod. Shove the rod down by hand as far as you can, by
>pumping up and down. Pull the rod out of that hole, pour the hole full of
>wwater. Reinsert the rod after a little time of waiting or maybe refilling
>the hole if the water goes down quickly. Repeat the pumping up and down with
>the rod by hand until it stops going easy. Pull the rod out refill with
>water and keep repeating this process until re moval is too difficult then
>resort to the sledge hammer. Usually you can get the rod down at least four
>to six foot before you need the hammer. This technique is called watter
>jetting and is also used with other equipment for horizontal boring under
>highways and streets for utility lines and pipes.
>
>Another note if this generator is located close to the main service point on
>the house there may all ready be a rod buired under the meter. It might be
>easier to dig it up until the wire to it is found and you could split bolt
>to it.
>Luck to you,
>Ron
>----- Original Message -----
>From: Edward Przybylek
>To: BlindHandyMan
>Sent: Sunday, December 16, 2007 9:13 PM
>Subject: [BlindHandyMan] Generator Grounding Follow-UP
>
>Hi all,
>
>After all your replies, I decided to ground my new generator. Better safe
>then sorry. When the manual said that not grounding the generator could
>pose the threat of electricution, it made me decide it was the best course
>of action. I went to Home Depot to purchase the necessary supplies. I
>picked up a lenght of 10 gauge stranded copper wire and then went to search
>for the copper grounding rod. The thing you guys forgot to mention is that
>the freaking rod is 8 feet long. I asked the associate how much of the rod
>I should cut off the 8 foot length to pound into the ground. That's when he
>said "All 8 feet." My first response was "Are you for real!" My soil is 5%
>dirt and 95% rock. Getting 8 feet of anything that deep in my yard is going
>to be a task meant for the Gods and not a mere mortal like myself. The last
>time I pounded any kind of rod into my yard was a galvanized pipe to support
>a newly planted evergreen to help it make it through the winter. It went
>down approximately 3 feet and stopped dead. I mushroomed the top of the
>pipe with a four pound mallet but the pipe went no further. Now you expect
>me to pound an 8 foot copper rod into the ground! Yeah, right. What I'm
>anticipating is a very bent rod and a flurry of filthy words that till make
>the ladies in the neighbor hood blush wildly and hurry their children
>indoors. From now on, gentlemen, make sure you mention the finer points of
>a task before making recommendations. <big smile> Let you know how it
>goes.
>
>Take care,
>Ed
>
>[Non-text portions of this message have been removed]
>
>[Non-text portions of this message have been removed]
>
>[Non-text portions of this message have been removed]
>
>[Non-text portions of this message have been removed]
>
>
>No virus found in this incoming message.
>Checked by AVG Free Edition.
>Version: 7.5.503 / Virus Database: 269.17.4/1188 - Release Date: 
>12/17/2007 2:13 PM

Reply via email to