I have installed grounding systems for cell towers. They are all single
point ground. Several rods & buried coper cables terminate on a busbar along
with the antenna grounds, radio equipment grounds & electrical panel
grounds. I am, by no means an expert, my grounding and bonding expertise
comes more from an electrical safety aspect. The RF side (HF) as it relates
to the grounding system is a whole different field. If you install 20 rods
and 20 ground  radials to make your HF antenna work, a single point system
may be difficult to achieve In particular if the electrical service panel is
on the other side of the house than the ham station. I just know they need
to be bonded together to eliminate electrical potential.  All new
construction now the electrician must supply a grounding block connected to
the AC ground. So the phone, cable TV & Satellite equipment contractors can
terminate to. Robert

 

From: BVARC <[email protected]> On Behalf Of orin snook via BVARC
Sent: Wednesday, April 08, 2020 5:31 PM
To: 'BRAZOS VALLEY AMATEUR RADIO CLUB' <[email protected]>
Cc: orin snook <[email protected]>; Robert Polinski
<[email protected]>
Subject: Re: [BVARC] Antenna Mounting Options

 

As an "expert" in lightning, even publishing a paper some 40 years ago with
research and study before and after, it all goes back to Ben Franklin. 

1.      He invents the lightning rod to attract or "catch" the strike, thus
protecting the structure, further engineered for the 45 degree cone of
protection and positive vs. negative origination of the least resistant
path.
2.      He notes, "behold, the corona shows discharge of the charges, hence
dissipating the voltage potential and avoiding the strike."

I found then, as now, that a couple of companies guarantee your protected
facility will not be struck by lightning, or if so, no damage will be
incurred. 

This has been formalized into an "open source" like standard with a 3 prong
approach, used in virtually all hardened installations.



1.      The first leg is to eliminate voltage potential by tying all "wires"
to a single point, both inside and outside a sole and single entry point to
the facility. Inside, you see a halo of grounding buss for all ground
points. Outside, a single low impedance ground buss with a sole and single
lead of sufficient size entering the protected facility. For the discussion
of a low impedance lightning ground, the electrical green ground,
case/chassis/building structure grounds, water pipes, telephone and all
other items that are capable of carrying a lightning charge. Not unlike how
a Faraday cage would be constructed. 

The lightning strike serves to equalize the difference in sky vs. earth
ground potentials. This dissipation moves out from the actual strike point
in the earth in waves, as a stone in a pond, with hundreds of thousands of
volt potential difference short distances between the "waves". This is why
while standing, it can go up on leg and down the other. To eliminate this
potential, with a single point of contact again, when you feel the hair on
the back of your head raise, you drop to the ground with your hands on your
knees, minimizing the physical distance and magnitude of any voltage
potential between points of the ground. 

When gas, electrical service, cable all enter the facility at different
points, all need to be bonded and connected together at proper distances and
cadwelled.
2.      The next leg of the stool is to dissipate the charges pre-strike
with sharp point coronas. Multiple sharp points at the highest elevation,
often in an umbrella like skeleton, often massive. Porcupine like bundles of
50, 12 inch or so stainless spikes are available for hams that I have used
with success. In Houston, the charts show some 2-4 strikes predicted for
well grounded towers of a hundred feet above average terrain and my personal
experience has been about a strike every 2 years.
3.      Once the strike has occurred despite efforts, you ground the piss
out of it to drain the charge to a low impedance ground. Ground rods are
arranged in a line, a triangle or even around the entire structure at a
spacing distance equal to the length of the rod. An important issue in short
cut grounding is to fail to cadweld these bond connections. A clamp
corrodes, especially a hose clamp, gets loosened and changes impedance - not
good.
4.      Lastly, when EMP type protection is added, or for a more robust
lightning design, arrestors are added to coax center conductors for example,
to give the EMP or lightning an alternative path to ground instead of
through the connected, protected equipment. Spark gap, gas discharge and
others designed for the rise time of the voltage spike you are worried
about. I have used these with success:

https://www.dxengineering.com/search/department/grounding-and-lightning-prot
ection/product-line/polyphaser-coaxial-lightning-protectors?autoview=SKU
<https://www.dxengineering.com/search/department/grounding-and-lightning-pro
tection/product-line/polyphaser-coaxial-lightning-protectors?autoview=SKU&so
rtby=Default&sortorder=Ascending> &sortby=Default&sortorder=Ascending

I believe you will find these concepts in current state-of-the-art
discussions while unplugging the coax just might lead to things like ball
lightning phenomes. 

End of rant, back to lurking.
73,
KB5F
orin

 

  _____  

From: BVARC <[email protected] <mailto:[email protected]> > on
behalf of Robert Polinski via BVARC <[email protected]
<mailto:[email protected]> >
Sent: Wednesday, April 8, 2020 4:50 PM
To: 'BRAZOS VALLEY AMATEUR RADIO CLUB' <[email protected]
<mailto:[email protected]> >
Cc: Robert Polinski <[email protected]
<mailto:[email protected]> >
Subject: Re: [BVARC] Antenna Mounting Options 

 

The National Electrical Code (NEC) requires any supplemental grounding rods
(and antenna or station ground rods meet this category) to be bonded
together with #6 copper wire. Should be as short as possible with no sharp
bends. If run through metallic conduit, it must be bonded to the pipe at
both ends. (otherwise the pipe will act like a choke ) A #12 is better than
nothing & will at least prevent shock potential between grounds but would
not help alot with a close lightning strike. All equipment should have good
lightning arresters (polyphaser 1 brand, DX eng another) on the antenna, all
well grounded and bonded. Hams will pay $3500-4000 for a radio and not want
to spend $100 to protect it. I know, you all disconnect your radios from
power & ant EVERY time you are not using them, no worries here, as you drive
home from work, and see that dark cloud forming over were you live!! LOL
Robert KD5YVQ

 

From: BVARC <[email protected] <mailto:[email protected]> > On
Behalf Of Will Gray via BVARC
Sent: Wednesday, April 08, 2020 3:51 PM
To: BRAZOS VALLEY AMATEUR RADIO CLUB <[email protected]
<mailto:[email protected]> >
Cc: Will Gray <[email protected] <mailto:[email protected]> >
Subject: Re: [BVARC] Antenna Mounting Options

 

Submarine, North Sea, big helo , rain storm: nasty setup, the kind of event
that generate great sea stories (they are all true, though change a bit when
told over the years).   Likely the static charge from the helo rotes caused
the strike.   I would go for #4 or #6 solid copper wire for the ground
circuit.  Tie your ground to the utility inlet ground, water pipes and gas
pipes.  depending on the setup, might want to add a couple more of those 8'
ground rods. Still there is no guarantee but it improves the odds.

 

Will, KB7QL

 

On Wed, Apr 8, 2020 at 3:36 PM Ron Bosch via BVARC <[email protected]
<mailto:[email protected]> > wrote:

Will, et al,

To agree with you in a backhand kind of way, I have, in fact, seen lightning
hit a submarine while at sea in a rain storm in the North Atlantic, although
the lightning in question came off of a line hanging from a Sea Stallion,
and was VERY Impressive to a 20 year old ELT whose job it was to make sure
the deck was radiologically clear prior to a med evac.  To bring it back to
topic, though... Having just gotten back into HAM radio after a 10 year
absence, I have recently acquired some new and expensive toys.  The
"current" grounding set up is a 12 GA wire run from my station to the ground
rod put in as part of the repaneling of my electrical into the house. The
ground rod in question is an ~8 foot copper rod driven into the ground with
about 6 inches showing above ground level.  I bonded the 12 GA wire to the
rod with a hose clamp.  Do you all think that sufficient to protect my brand
new ID-4100 and IC-7100?

 

Ron

KE4DRF

 

Judging by personal experience, the next public health crisis after COVID 19
is likely to be cirrhosis.

 

Ron Bosch

 

"..any man who may be asked what he did .. to make his life worthwhile, I
think can respond with a good deal of pride and satisfaction" 'I served in
the United States Navy."

John F. Kennedy

 

When I was young and bold and strong,
Oh, right was right, and wrong was wrong!
My plume on high, my flag unfurled,
I rode away to right the world. 
'Come out, you dogs, and fight!' said I,
And wept there was but once to die.

But I am old; and good and bad
Are woven in a crazy plaid.

Dorothy Parker

"The best lack all conviction, while the worst are full of passionate
intensity"

Wm Butler Yeats

"Believing with you that religion is a matter which lies solely between man
and his God, that he owes account to none other for his faith or his
worship, that the legislative powers of government reach actions only, and
not opinions, I contemplate with sovereign reverence that act of the whole
American people which declared that their legislature should "make no law
respecting an establishment of religion, or prohibiting the free exercise
thereof", thus building a wall of separation between church and State."

Thomas Jefferson


 "Fix reason firmly in her seat, and call to her tribunal every fact, every
opinion. Question with boldness even the existence of a god; because, if
there be one, he must more approve the homage of reason, than that of
blindfolded fear."

Thomas Jefferson in a letter to Peter Carr


A Government founded upon justice, and recognizing the equal rights of all
men; claiming no higher authority for existence, or sanction for its laws,
than nature, reason, and the regularly ascertained will of the people;
steadily refusing to put its sword and purse in the service of any religious
creed or family, is a standing offense to most of the Governments of the
world, and to some narrow and bigoted people among ourselves.

Frederick Douglass




 

 

On Wed, Apr 8, 2020 at 11:53 AM Will Gray via BVARC <[email protected]
<mailto:[email protected]> > wrote:

Lightning is interesting.  The strike begins when the electrons that have
been scrubbed from the air  by rain or snow are deposited on the ground
(generally).  A negative charge builds where the earth acts like the plate
of a capacitor.  With no other path the charge gets great enough to find the
path of least resistance back to the atmosphere overhead or nearby from
where the electrons were scrubbed by failing rain.  If the area is well
grounded, the electrons are dissipated in the the earth, if insulated (why
lightning strikes concrete runways) the charge builds.  If your house,
ground, trees, or anything is insulated allowing the charge to build, the
strike will occur when the charge is great enough.  In my years at sea in he
Navy, I never saw a lightning strike hit the surface of the water or the
ship, no matter how heavy the rain.  The salt water as a conductor
dissipated the charge.  Aircraft flying in rain build up a charge and may be
struck, damaging them with burn marks and even scoring bearings in the
engines.  Aircraft have static wicks to bleed off the charge just as trucks
have straps to bleed off the charge so the 7,000 gallons of gasoline in a
tanker truck doesn't  go up in flames from a lightning strike or lesser
static discharge.

 

Will Gray, KB&QL

 

On Wed, Apr 8, 2020 at 11:38 AM Robert Polinski via BVARC <[email protected]
<mailto:[email protected]> > wrote:

Much what is said is true, but I will add a few points. Forty some years ago
I worked for a 2 way radio co. We had the Yellow Cab contract. I was at
Yellow Cab on Hays street in north Houston. I was replacing 2 radios in the
radio shack at the base of the 450ft tower that had been removed and taken
to the shop for repair. As I got setup to replace the radios in the rack,
there were 4 radios & 4 standby radios in the rack. They used 4 VHF channels
at that time. There was a thunderstorm approaching outside. The radio shack
was just a small 8x 12 building a the tower base. The radios were DC remote
controlled from the dispatch office located 100 ft away. I waited for the
storm to pass before installing the repaired radios, as I did not want the
touch the rack a long as the storm was near. As I sat on the floor of the
shack looking out the door, it was raining real hard. I then saw lightning
strike the power lines behind the mechanic shop about 300ft away. It blew a
AC receptacle on the wall behind me off the wall. Damaged 2 of the 4 radio
power supplies, 1 DC remote. I had disconnected all the standby equipment
before the storm to facilitate the installation of the replacement radios.
To make a long story short (LOL) The lightning hit the power line 300ft away
from a 450ft tower. No lightning came down the tower. So just being high in
the air, does not necessarily make it a lightning rod. 

  What is important is bonding everything together. If all equipment in your
shack is at the same potential, the lightning current will not have anywhere
to flow. I can charge the case of your K3 with 10,000v but if there is no
current flow no damage will occur. If lightning hits the power line and the
ground rod at your shack is a better path than the AC ground at your meter
the current will travel thru your rig to get to the rod. If you bond the
shack/antenna ground with the AC ground with a #6 wire. Since both are at
the same potential, there will be no current flow & no damage. ( this
bonding is required by the NEC) See Mike Holt on you tube to understand
this. Robert KD5YVQ  

 

From: BVARC <[email protected] <mailto:[email protected]> > On
Behalf Of Eddie Runner via BVARC
Sent: Wednesday, April 08, 2020 9:53 AM
To: Mark Brantana via BVARC <[email protected] <mailto:[email protected]> >
Cc: Eddie Runner <[email protected] <mailto:[email protected]> >
Subject: Re: [BVARC] Antenna Mounting Options

 

Mark, it is true, lightning does what it wants to do.

 

I have had outside antennas of all types including towers , long wires,
dipoles, cb antennas, shortwave, Ham of all kinds, over the past 50 years,
I have had houses with ground rods and houses without ground rods and even
when I had ground rods some antennas would sometimes not be grounded... (one
house I had 19 antennas up at one time)..  

 

I have a rule, if there is a threat of lightning, I AM NOT GONNA TOUCH THAT
COAX..

 

So that means I NEVER disconnect my coax when a storm comes..
NEVER...NEVER...

 

As far as I can remember I have never had lightning damage on any radio
gear..  

 

Back in the 80s there was some speculation that lightning may have come in 

through the phone line and destroyed 2 modems ( I used to run BBS's)..

 

I have seen a few times where lightning hit TOWERS or POWER PANELS on 

homes, some were hams and some were just people with no antennas...

 

I have seen gear supposedly hit by lightning.. Maybe some was, maybe some
just blew the finals

cause the guy forgot to hook up the coax he unhooked the last time he heard
thunder.. ha ha

 

But even all the times we know about, it is still fairly unlikely.. and if
the lightnng has your

name on it.. ???

 

Good luck..  it is all VOODDOO..ha ha

 

Eddie (NU5K)

 

On Wednesday, April 8, 2020, 06:16:29 AM CDT, Mark Brantana via BVARC
<[email protected] <mailto:[email protected]> > wrote: 

 

 

Since folks are hunkered down anyways, here is a problem.  I am improving my
emergency radio capability by adding a 2-m radio to my home office. Who
knows where this thing is going, and I think this is a good time to prepare.
I would like your thoughts or experience with the following.

 

I am looking to mount a 2-m antenna on my roof.  Currently I have a TV
antenna attached with a j-pole just below the chimney output.  I have a
single-story house.  My plan has been to extend the j-pole about 4 ft higher
to get better TV reception, and mount the antenna just above it.  I do have
to watch out for offending the HOA.

 

My property has power lines running parallel with the back of the house, and
these power lines are about 35 feet high and 35 feet laterally away from the
chimney.   

 

I am concerned about a couple of things:

1.      Some day I may want to start a fire in the fireplace, and I do not
want the heat to get to the antennas.  This is why I have the TV antenna
mounted below the top of the chimney.
2.      I would like to avoid arching or lightning strikes, though I think
it is quite common for most of us to have power lines around to contend
with.  Two thoughts here:

a.      Of course, I will ground it all.
b.      I wonder if the power lines might protect the lower antennas since
lightning may hit them first.  I mention this since the first thought was
that the power lines might add to the lightning risk, not detract.
c.      That said, lightning does what it wants, and even a nearby lightning
strike, as opposed to a direct strike, will do significant damage.

 

On that last point, I will share a short story.  When in Louisiana many
years ago, we got into a discussion about how lightning had destroyed a lot
of equipment in a member's shack.  This included, as I recall, about 3-5
computers, and about as many radios.  This was all sitting on a metal table.
Due to the lightning storm, the Ham had disconnected all of the antennas.
Lightning hit his tower and made the 2" jump to the table.  The rest was
history.  But, that was not the story I wanted to tell.  That was the
discussion we were having.  Another Ham broke in and told us that he had a
tower at one end of his house which was operational, and he had just that
day mounted a short marine antenna at the other end of the house on his
chimney.  It was a dark and stormy night the previous evening, and the
lightning passed the tower to hit the yet unconnected marine antenna.  So,
lightning does not follow the rules.

 

OK, so I diverged.  I really would like to know what experience and advice
you can offer me on my project.  The power lines make me nervous, and I
really wish my best mounting option were not in the heat zone of the
chimney.

 

Mark

N5PRD

 

 

                

 

________________________________________________
Brazos Valley Amateur Radio Club

BVARC mailing list
[email protected] <mailto:[email protected]> 
http://mail.bvarc.org/mailman/listinfo/bvarc_bvarc.org

________________________________________________
Brazos Valley Amateur Radio Club

BVARC mailing list
[email protected] <mailto:[email protected]> 
http://mail.bvarc.org/mailman/listinfo/bvarc_bvarc.org




 

-- 

431 Forest Circle

Ruston, LA 71270-2642

H:318-251-2219

C:318-265-2976 (text)

[email protected] <mailto:[email protected]> 

 

________________________________________________
Brazos Valley Amateur Radio Club

BVARC mailing list
[email protected] <mailto:[email protected]> 
http://mail.bvarc.org/mailman/listinfo/bvarc_bvarc.org

________________________________________________
Brazos Valley Amateur Radio Club

BVARC mailing list
[email protected] <mailto:[email protected]> 
http://mail.bvarc.org/mailman/listinfo/bvarc_bvarc.org




 

-- 

431 Forest Circle

Ruston, LA 71270-2642

H:318-251-2219

C:318-265-2976 (text)

[email protected] <mailto:[email protected]> 

 

________________________________________________
Brazos Valley Amateur Radio Club

BVARC mailing list
[email protected]
http://mail.bvarc.org/mailman/listinfo/bvarc_bvarc.org

Reply via email to