Could it be the "A @42V" value? What kind of circuits do you have for each
PSU? The 6000W can either take two 120V-20A or a single 240V-20A if you need
the full 6000W.
I believe the 6500 uses power internally at 42V, so it makes sense that
the power supplies are putting out 42V power.
How are you feeding power to the chassis? If you're doing 2x208V or
2x240V circuits per power supply, then you should definitely be fully
energized.
Are both of the input lights lit on the front of thsat second power
supply?
Have you tested the circuits that feed the second power supply to verify
they're on and putting out the correct voltage?
jms
On 3/14/2017 5:42 AM, James Bensley wrote:
On 13 March 2017 at 15:02, "Rolf Hanßen" <[email protected]> wrote:
> Power-Capacity PS-Fan Output Oper
> PS Type Watts A @42V Status Status State
> ---- ------------------ ------- ------ ------ ------ -----
> 1 WS-CAC-6000W 5771.64 137.42 OK OK on
> 2 WS-CAC-6000W 3780.00 90.00 - - off
Why is one of these 6kW PSUs saying 4kW of power capacity? Since they
are the same model PSU I think the power capacity has to match on
them?
Cheers,
James.
_______________________________________________
cisco-nsp mailing list [email protected]
https://puck.nether.net/mailman/listinfo/cisco-nsp
archive at http://puck.nether.net/pipermail/cisco-nsp/
_______________________________________________
cisco-nsp mailing list [email protected]
https://puck.nether.net/mailman/listinfo/cisco-nsp
archive at http://puck.nether.net/pipermail/cisco-nsp/
_______________________________________________
cisco-nsp mailing list [email protected]
https://puck.nether.net/mailman/listinfo/cisco-nsp
archive at http://puck.nether.net/pipermail/cisco-nsp/