On Tue, 14 Mar 2017, Laurent Dumont wrote:

Could it be the "A @42V" value? What kind of circuits do you have for each PSU? The 6000W can either take two 120V-20A or a single 240V-20A if you need the full 6000W.

I believe the 6500 uses power internally at 42V, so it makes sense that the power supplies are putting out 42V power.

How are you feeding power to the chassis? If you're doing 2x208V or 2x240V circuits per power supply, then you should definitely be fully energized.

Are both of the input lights lit on the front of thsat second power supply?

Have you tested the circuits that feed the second power supply to verify they're on and putting out the correct voltage?

jms

On 3/14/2017 5:42 AM, James Bensley wrote:
 On 13 March 2017 at 15:02, "Rolf Hanßen" <[email protected]> wrote:
>                           Power-Capacity PS-Fan Output Oper
>  PS   Type               Watts   A @42V Status Status State
>  ---- ------------------ ------- ------ ------ ------ -----
>  1    WS-CAC-6000W       5771.64 137.42 OK     OK     on
>  2    WS-CAC-6000W       3780.00 90.00  -      -      off
 Why is one of these 6kW PSUs saying 4kW of power capacity? Since they
 are the same model PSU I think the power capacity has to match on
 them?

 Cheers,
 James.
 _______________________________________________
 cisco-nsp mailing list  [email protected]
 https://puck.nether.net/mailman/listinfo/cisco-nsp
 archive at http://puck.nether.net/pipermail/cisco-nsp/

_______________________________________________
cisco-nsp mailing list  [email protected]
https://puck.nether.net/mailman/listinfo/cisco-nsp
archive at http://puck.nether.net/pipermail/cisco-nsp/

_______________________________________________
cisco-nsp mailing list  [email protected]
https://puck.nether.net/mailman/listinfo/cisco-nsp
archive at http://puck.nether.net/pipermail/cisco-nsp/

Reply via email to