     new 420e7e6a39 fix(plc4j/modbus): validate response function codes and 
make request-timeout cover queueing
420e7e6a39 is described below

commit 420e7e6a39eada49b96825ab243686fa6ba8ec43
Author: Sebastian Rühl <[email protected]>
AuthorDate: Tue Jul 7 13:51:54 2026 +0200

    fix(plc4j/modbus): validate response function codes and make 
request-timeout cover queueing
    
    Serial connections (RTU/ASCII) correlated responses by unit id only, so a
    late response from a timed-out request could complete the next request on
    the same unit. Responses are now also validated against the pending
    request's function code (exception frames answer any request; the generated
    error PDU carries no fc). Mismatches are logged and discarded while the
    pending request stays armed. Same-fc late responses remain
    indistinguishable — inherent to RTU, documented.
    
    The request timeout is now armed at submission instead of dispatch, making
    it a total wall-clock budget; requests that expire while queued fail fast
    with a TimeoutException and never reach the wire (small dispatch margin,
    documented in the config description).
---
 RELEASE_NOTES                                      |   4 +
 .../java/modbus/ascii/ModbusAsciiConnection.java   | 125 ++++++++++++++++-----
 .../ascii/config/ModbusAsciiConfiguration.java     |   2 +-
 .../plc4x/java/modbus/rtu/ModbusRtuConnection.java | 125 ++++++++++++++++-----
 .../modbus/rtu/config/ModbusRtuConfiguration.java  |   2 +-
 .../modbus/ascii/ModbusAsciiConnectionTest.java    |  31 +++--
 .../rtu/ModbusRtuConnectionRequestChainTest.java   |  74 +++++++++++-
 .../java/modbus/rtu/ModbusRtuConnectionTest.java   |  31 +++--
 .../transport/serial/SerialTransportInstance.java  |   3 +-
 .../transport/serial/SharedModeInstanceTest.java   |  29 +++++
 10 files changed, 344 insertions(+), 82 deletions(-)

diff --git a/RELEASE_NOTES b/RELEASE_NOTES
index a2424b1b12..5cf58c4c37 100644
--- a/RELEASE_NOTES
+++ b/RELEASE_NOTES
@@ -38,6 +38,10 @@ New Features
   unknown Modbus exception codes map to REMOTE_ERROR instead of failing;
   shared serial ports dispatch each connection's callbacks on their own
   thread, so one blocked callback no longer stalls the whole port.
+  Responses are additionally validated against the pending request's
+  function code (late responses from timed-out requests are discarded
+  instead of completing the wrong caller), and the request timeout now
+  covers the full time from submission, including queueing.
 
 Incompatible changes
 --------------------
diff --git 
a/plc4j/drivers/modbus/src/main/java/org/apache/plc4x/java/modbus/ascii/ModbusAsciiConnection.java
 
b/plc4j/drivers/modbus/src/main/java/org/apache/plc4x/java/modbus/ascii/ModbusAsciiConnection.java
index cc4d702310..c97e2f641a 100644
--- 
a/plc4j/drivers/modbus/src/main/java/org/apache/plc4x/java/modbus/ascii/ModbusAsciiConnection.java
+++ 
b/plc4j/drivers/modbus/src/main/java/org/apache/plc4x/java/modbus/ascii/ModbusAsciiConnection.java
@@ -64,7 +64,7 @@ public class ModbusAsciiConnection extends 
ConnectionBase<ModbusAsciiConfigurati
     private static final Logger LOGGER = 
LoggerFactory.getLogger(ModbusAsciiConnection.class);
 
     private ModbusAsciiMessageCodec messageCodec;
-    private final Map<Short, CompletableFuture<ModbusAsciiADU>> 
pendingRequests = new ConcurrentHashMap<>();
+    private final Map<Short, PendingRequest> pendingRequests = new 
ConcurrentHashMap<>();
 
     // Serializes request/response transactions. Modbus over serial is a
     // single-outstanding-transaction protocol; without this, concurrent
@@ -107,8 +107,8 @@ public class ModbusAsciiConnection extends 
ConnectionBase<ModbusAsciiConfigurati
         if (messageCodec != null) {
             messageCodec.close();
         }
-        pendingRequests.values().forEach(future ->
-            future.completeExceptionally(new PlcRuntimeException("Connection 
closed")));
+        pendingRequests.values().forEach(pending ->
+            pending.future.completeExceptionally(new 
PlcRuntimeException("Connection closed")));
         pendingRequests.clear();
         super.close();
         LOGGER.info("Modbus ASCII connection closed");
@@ -126,7 +126,7 @@ public class ModbusAsciiConnection extends 
ConnectionBase<ModbusAsciiConfigurati
         int pendingCount = pendingRequests.size();
         if (pendingCount > 0) {
             LOGGER.warn("Failing {} pending requests due to transport 
disconnect", pendingCount);
-            pendingRequests.values().forEach(future -> 
future.completeExceptionally(exception));
+            pendingRequests.values().forEach(pending -> 
pending.future.completeExceptionally(exception));
             pendingRequests.clear();
         }
     }
@@ -147,9 +147,31 @@ public class ModbusAsciiConnection extends 
ConnectionBase<ModbusAsciiConfigurati
     }
 
     /**
-     * Correlation is by unit id only; requests are serialized per connection
-     * via {@link #sendRequest}, and per shared port each connection must own
-     * distinct unit ids.
+     * A dispatched request awaiting its response: the future plus the
+     * request's function code for response validation.
+     */
+    private static final class PendingRequest {
+        final byte functionFlag;
+        final CompletableFuture<ModbusAsciiADU> future;
+        PendingRequest(byte functionFlag, CompletableFuture<ModbusAsciiADU> 
future) {
+            this.functionFlag = functionFlag;
+            this.future = future;
+        }
+    }
+
+    /**
+     * Correlates a received frame to the pending request for its unit id.
+     * Validation: an exception frame (errorFlag) answers any pending
+     * request; a normal frame must carry the SAME function code as the
+     * pending request — mismatches (e.g. a late response arriving after
+     * its request timed out and a different operation took its place) are
+     * discarded without touching the pending entry.
+     * <p>
+     * Residual limitation: a late response with the SAME function code as
+     * the new request is physically indistinguishable — Modbus RTU/ASCII
+     * carry no transaction ids. Requests are serialized per connection and
+     * shared ports require distinct unit ids per connection, which bounds
+     * the exposure to same-fc retry patterns.
      */
     private void handleIncomingMessage(ModbusAsciiADU modbusMessage) {
         short address = modbusMessage.getAddress();
@@ -157,17 +179,61 @@ public class ModbusAsciiConnection extends 
ConnectionBase<ModbusAsciiConfigurati
             auditLog.write(AuditLogEventType.INCOMING_MESSAGE,
                 "Received Modbus ASCII response, address=" + address);
         }
-        CompletableFuture<ModbusAsciiADU> future = 
pendingRequests.remove(address);
-        if (future != null) {
-            future.complete(modbusMessage);
-        } else {
+        PendingRequest pending = pendingRequests.get(address);
+        if (pending == null) {
             LOGGER.warn("Received response for unknown address: {}", address);
+            return;
         }
+        boolean isException = modbusMessage.getPdu().getErrorFlag();
+        if (!isException && modbusMessage.getPdu().getFunctionFlag() != 
pending.functionFlag) {
+            LOGGER.warn("Discarding response for address {} with function code 
0x{} while waiting for 0x{} (late response from a timed-out request?)",
+                address,
+                Integer.toHexString(modbusMessage.getPdu().getFunctionFlag() & 
0xFF),
+                Integer.toHexString(pending.functionFlag & 0xFF));
+            return;
+        }
+        pendingRequests.remove(address, pending);
+        pending.future.complete(modbusMessage);
     }
 
     // Package-private for tests.
     CompletableFuture<ModbusAsciiADU> sendRequest(ModbusAsciiADU request, 
short address) {
         CompletableFuture<ModbusAsciiADU> responseFuture = new 
CompletableFuture<>();
+
+        // Total budget from submission: queueing + dispatch + response.
+        long timeoutMs = getConfiguration().getRequestTimeout();
+        // Explicit deadline, checked again in dispatchRequest(): the JVM-wide
+        // CompletableFuture delay scheduler is a single thread and only gets
+        // back around to an already-overdue timeout AFTER it finishes
+        // processing the previous request's own completion (cleanup +
+        // chain-continuation + submitting the next dispatch) — that hand-off
+        // to the async pool routinely wins the race against the scheduler
+        // catching up, so responseFuture.isDone() alone can still be false
+        // for a request whose enqueue-time budget has, in wall-clock terms,
+        // already run out.
+        long nowNanos = System.nanoTime();
+        long budgetNanos = TimeUnit.MILLISECONDS.toNanos(timeoutMs);
+        // A request with only a sliver of its budget left is not worth
+        // dispatching either — it has no realistic chance of a round trip
+        // completing before its own timeout fires anyway. Backing the
+        // dispatch deadline off by this margin also absorbs scheduling
+        // jitter between a predecessor's timeout firing (on the JVM-wide
+        // single-threaded delay scheduler, see above) and this request's
+        // own deadline — queued only a hair later, on the same clock —
+        // which would otherwise let a request that is, for all practical
+        // purposes, dead slip through a raw "has my deadline passed" check.
+        long minViableRemainingNanos = 
Math.min(TimeUnit.MILLISECONDS.toNanos(50), budgetNanos / 4);
+        long dispatchDeadlineNanos = nowNanos + budgetNanos - 
minViableRemainingNanos;
+        responseFuture.orTimeout(timeoutMs, TimeUnit.MILLISECONDS)
+            .whenComplete((result, error) -> {
+                if (error instanceof TimeoutException) {
+                    // Two-arg remove semantics preserved through the holder:
+                    // only clear the entry if it is still OUR request.
+                    pendingRequests.computeIfPresent(address,
+                        (key, pending) -> pending.future == responseFuture ? 
null : pending);
+                }
+            });
+
         CompletableFuture<?> previous;
         synchronized (requestChainLock) {
             previous = requestTail;
@@ -177,18 +243,30 @@ public class ModbusAsciiConnection extends 
ConnectionBase<ModbusAsciiConfigurati
         }
         if (previous.isDone()) {
             // Hot path: nothing queued — dispatch on the caller thread as 
before.
-            dispatchRequest(request, address, responseFuture);
+            dispatchRequest(request, address, responseFuture, 
dispatchDeadlineNanos);
         } else {
             // Queued: hop to the async pool so long bursts release the
             // completing thread's stack (a synchronous chain nests one
             // frame per queued request and can silently overflow).
-            previous.whenCompleteAsync((ignored, ignoredError) -> 
dispatchRequest(request, address, responseFuture));
+            previous.whenCompleteAsync((ignored, ignoredError) -> 
dispatchRequest(request, address, responseFuture, dispatchDeadlineNanos));
         }
         return responseFuture;
     }
 
-    private void dispatchRequest(ModbusAsciiADU request, short address, 
CompletableFuture<ModbusAsciiADU> responseFuture) {
-        pendingRequests.put(address, responseFuture);
+    private void dispatchRequest(ModbusAsciiADU request, short address, 
CompletableFuture<ModbusAsciiADU> responseFuture, long dispatchDeadlineNanos) {
+        if (responseFuture.isDone()) {
+            // Already completed (timeout or failure) while queued.
+            return;
+        }
+        if (System.nanoTime() >= dispatchDeadlineNanos) {
+            // Fail fast: the remaining budget is below the dispatch margin,
+            // so the request is semantically dead — don't make the caller
+            // wait for the orTimeout backstop.
+            responseFuture.completeExceptionally(new TimeoutException(
+                "Request timed out while queued (remaining budget below 
dispatch margin)"));
+            return;
+        }
+        pendingRequests.put(address, new 
PendingRequest(request.getPdu().getFunctionFlag(), responseFuture));
         try {
             if (auditLog.isEnabled()) {
                 auditLog.write(AuditLogEventType.OUTGOING_MESSAGE,
@@ -196,29 +274,16 @@ public class ModbusAsciiConnection extends 
ConnectionBase<ModbusAsciiConfigurati
             }
             messageCodec.send(request);
         } catch (MessageCodecException e) {
-            pendingRequests.remove(address);
+            pendingRequests.computeIfPresent(address, (key, pending) -> 
pending.future == responseFuture ? null : pending);
             responseFuture.completeExceptionally(new 
PlcRuntimeException("Failed to send request", e));
-            return;
         } catch (RuntimeException e) {
             // The responseFuture MUST complete no matter what: the request
             // chain's tail hangs off it, so an unchecked throw here (e.g.
             // from a custom AuditLog) would otherwise silently wedge every
             // subsequent request on this connection.
-            pendingRequests.remove(address, responseFuture);
+            pendingRequests.computeIfPresent(address, (key, pending) -> 
pending.future == responseFuture ? null : pending);
             responseFuture.completeExceptionally(e);
-            return;
         }
-
-        long timeoutMs = getConfiguration().getRequestTimeout();
-        responseFuture.orTimeout(timeoutMs, TimeUnit.MILLISECONDS)
-            .whenComplete((result, error) -> {
-                if (error instanceof TimeoutException) {
-                    // Two-arg remove: only clears our own entry, immune to
-                    // dependent-ordering (a late cleanup can never remove a
-                    // successor request's entry).
-                    pendingRequests.remove(address, responseFuture);
-                }
-            });
     }
 
     
////////////////////////////////////////////////////////////////////////////////////////////////////////////////////
diff --git 
a/plc4j/drivers/modbus/src/main/java/org/apache/plc4x/java/modbus/ascii/config/ModbusAsciiConfiguration.java
 
b/plc4j/drivers/modbus/src/main/java/org/apache/plc4x/java/modbus/ascii/config/ModbusAsciiConfiguration.java
index 9bba5b0aa0..4cc21b729c 100644
--- 
a/plc4j/drivers/modbus/src/main/java/org/apache/plc4x/java/modbus/ascii/config/ModbusAsciiConfiguration.java
+++ 
b/plc4j/drivers/modbus/src/main/java/org/apache/plc4x/java/modbus/ascii/config/ModbusAsciiConfiguration.java
@@ -30,7 +30,7 @@ public class ModbusAsciiConfiguration implements 
Configuration {
 
     @ConfigurationParameter("request-timeout")
     @IntDefaultValue(5_000)
-    @Description("Default timeout for all types of requests.")
+    @Description("Default timeout for all types of requests. The timeout 
covers the full time from submission including queueing; queued requests whose 
remaining budget falls below a small dispatch margin (at most a quarter of the 
timeout, capped at 50 ms) fail fast instead of being sent.")
     private int requestTimeout;
 
     @ConfigurationParameter("default-unit-identifier")
diff --git 
a/plc4j/drivers/modbus/src/main/java/org/apache/plc4x/java/modbus/rtu/ModbusRtuConnection.java
 
b/plc4j/drivers/modbus/src/main/java/org/apache/plc4x/java/modbus/rtu/ModbusRtuConnection.java
index f3c7165fa5..4a9e7b789a 100644
--- 
a/plc4j/drivers/modbus/src/main/java/org/apache/plc4x/java/modbus/rtu/ModbusRtuConnection.java
+++ 
b/plc4j/drivers/modbus/src/main/java/org/apache/plc4x/java/modbus/rtu/ModbusRtuConnection.java
@@ -64,7 +64,7 @@ public class ModbusRtuConnection extends 
ConnectionBase<ModbusRtuConfiguration>
     private static final Logger LOGGER = 
LoggerFactory.getLogger(ModbusRtuConnection.class);
 
     private ModbusRtuMessageCodec messageCodec;
-    private final Map<Short, CompletableFuture<ModbusRtuADU>> pendingRequests 
= new ConcurrentHashMap<>();
+    private final Map<Short, PendingRequest> pendingRequests = new 
ConcurrentHashMap<>();
 
     // Serializes request/response transactions. Modbus over serial is a
     // single-outstanding-transaction protocol; without this, concurrent
@@ -107,8 +107,8 @@ public class ModbusRtuConnection extends 
ConnectionBase<ModbusRtuConfiguration>
         if (messageCodec != null) {
             messageCodec.close();
         }
-        pendingRequests.values().forEach(future ->
-            future.completeExceptionally(new PlcRuntimeException("Connection 
closed")));
+        pendingRequests.values().forEach(pending ->
+            pending.future.completeExceptionally(new 
PlcRuntimeException("Connection closed")));
         pendingRequests.clear();
         super.close();
         LOGGER.info("Modbus RTU connection closed");
@@ -126,7 +126,7 @@ public class ModbusRtuConnection extends 
ConnectionBase<ModbusRtuConfiguration>
         int pendingCount = pendingRequests.size();
         if (pendingCount > 0) {
             LOGGER.warn("Failing {} pending requests due to transport 
disconnect", pendingCount);
-            pendingRequests.values().forEach(future -> 
future.completeExceptionally(exception));
+            pendingRequests.values().forEach(pending -> 
pending.future.completeExceptionally(exception));
             pendingRequests.clear();
         }
     }
@@ -147,9 +147,31 @@ public class ModbusRtuConnection extends 
ConnectionBase<ModbusRtuConfiguration>
     }
 
     /**
-     * Correlation is by unit id only; requests are serialized per connection
-     * via {@link #sendRequest}, and per shared port each connection must own
-     * distinct unit ids.
+     * A dispatched request awaiting its response: the future plus the
+     * request's function code for response validation.
+     */
+    private static final class PendingRequest {
+        final byte functionFlag;
+        final CompletableFuture<ModbusRtuADU> future;
+        PendingRequest(byte functionFlag, CompletableFuture<ModbusRtuADU> 
future) {
+            this.functionFlag = functionFlag;
+            this.future = future;
+        }
+    }
+
+    /**
+     * Correlates a received frame to the pending request for its unit id.
+     * Validation: an exception frame (errorFlag) answers any pending
+     * request; a normal frame must carry the SAME function code as the
+     * pending request — mismatches (e.g. a late response arriving after
+     * its request timed out and a different operation took its place) are
+     * discarded without touching the pending entry.
+     * <p>
+     * Residual limitation: a late response with the SAME function code as
+     * the new request is physically indistinguishable — Modbus RTU/ASCII
+     * carry no transaction ids. Requests are serialized per connection and
+     * shared ports require distinct unit ids per connection, which bounds
+     * the exposure to same-fc retry patterns.
      */
     private void handleIncomingMessage(ModbusRtuADU modbusMessage) {
         short address = modbusMessage.getAddress();
@@ -157,17 +179,61 @@ public class ModbusRtuConnection extends 
ConnectionBase<ModbusRtuConfiguration>
             auditLog.write(AuditLogEventType.INCOMING_MESSAGE,
                 "Received Modbus RTU response, address=" + address);
         }
-        CompletableFuture<ModbusRtuADU> future = 
pendingRequests.remove(address);
-        if (future != null) {
-            future.complete(modbusMessage);
-        } else {
+        PendingRequest pending = pendingRequests.get(address);
+        if (pending == null) {
             LOGGER.warn("Received response for unknown address: {}", address);
+            return;
         }
+        boolean isException = modbusMessage.getPdu().getErrorFlag();
+        if (!isException && modbusMessage.getPdu().getFunctionFlag() != 
pending.functionFlag) {
+            LOGGER.warn("Discarding response for address {} with function code 
0x{} while waiting for 0x{} (late response from a timed-out request?)",
+                address,
+                Integer.toHexString(modbusMessage.getPdu().getFunctionFlag() & 
0xFF),
+                Integer.toHexString(pending.functionFlag & 0xFF));
+            return;
+        }
+        pendingRequests.remove(address, pending);
+        pending.future.complete(modbusMessage);
     }
 
     // Package-private for tests.
     CompletableFuture<ModbusRtuADU> sendRequest(ModbusRtuADU request, short 
address) {
         CompletableFuture<ModbusRtuADU> responseFuture = new 
CompletableFuture<>();
+
+        // Total budget from submission: queueing + dispatch + response.
+        long timeoutMs = getConfiguration().getRequestTimeout();
+        // Explicit deadline, checked again in dispatchRequest(): the JVM-wide
+        // CompletableFuture delay scheduler is a single thread and only gets
+        // back around to an already-overdue timeout AFTER it finishes
+        // processing the previous request's own completion (cleanup +
+        // chain-continuation + submitting the next dispatch) — that hand-off
+        // to the async pool routinely wins the race against the scheduler
+        // catching up, so responseFuture.isDone() alone can still be false
+        // for a request whose enqueue-time budget has, in wall-clock terms,
+        // already run out.
+        long nowNanos = System.nanoTime();
+        long budgetNanos = TimeUnit.MILLISECONDS.toNanos(timeoutMs);
+        // A request with only a sliver of its budget left is not worth
+        // dispatching either — it has no realistic chance of a round trip
+        // completing before its own timeout fires anyway. Backing the
+        // dispatch deadline off by this margin also absorbs scheduling
+        // jitter between a predecessor's timeout firing (on the JVM-wide
+        // single-threaded delay scheduler, see above) and this request's
+        // own deadline — queued only a hair later, on the same clock —
+        // which would otherwise let a request that is, for all practical
+        // purposes, dead slip through a raw "has my deadline passed" check.
+        long minViableRemainingNanos = 
Math.min(TimeUnit.MILLISECONDS.toNanos(50), budgetNanos / 4);
+        long dispatchDeadlineNanos = nowNanos + budgetNanos - 
minViableRemainingNanos;
+        responseFuture.orTimeout(timeoutMs, TimeUnit.MILLISECONDS)
+            .whenComplete((result, error) -> {
+                if (error instanceof TimeoutException) {
+                    // Two-arg remove semantics preserved through the holder:
+                    // only clear the entry if it is still OUR request.
+                    pendingRequests.computeIfPresent(address,
+                        (key, pending) -> pending.future == responseFuture ? 
null : pending);
+                }
+            });
+
         CompletableFuture<?> previous;
         synchronized (requestChainLock) {
             previous = requestTail;
@@ -177,18 +243,30 @@ public class ModbusRtuConnection extends 
ConnectionBase<ModbusRtuConfiguration>
         }
         if (previous.isDone()) {
             // Hot path: nothing queued — dispatch on the caller thread as 
before.
-            dispatchRequest(request, address, responseFuture);
+            dispatchRequest(request, address, responseFuture, 
dispatchDeadlineNanos);
         } else {
             // Queued: hop to the async pool so long bursts release the
             // completing thread's stack (a synchronous chain nests one
             // frame per queued request and can silently overflow).
-            previous.whenCompleteAsync((ignored, ignoredError) -> 
dispatchRequest(request, address, responseFuture));
+            previous.whenCompleteAsync((ignored, ignoredError) -> 
dispatchRequest(request, address, responseFuture, dispatchDeadlineNanos));
         }
         return responseFuture;
     }
 
-    private void dispatchRequest(ModbusRtuADU request, short address, 
CompletableFuture<ModbusRtuADU> responseFuture) {
-        pendingRequests.put(address, responseFuture);
+    private void dispatchRequest(ModbusRtuADU request, short address, 
CompletableFuture<ModbusRtuADU> responseFuture, long dispatchDeadlineNanos) {
+        if (responseFuture.isDone()) {
+            // Already completed (timeout or failure) while queued.
+            return;
+        }
+        if (System.nanoTime() >= dispatchDeadlineNanos) {
+            // Fail fast: the remaining budget is below the dispatch margin,
+            // so the request is semantically dead — don't make the caller
+            // wait for the orTimeout backstop.
+            responseFuture.completeExceptionally(new TimeoutException(
+                "Request timed out while queued (remaining budget below 
dispatch margin)"));
+            return;
+        }
+        pendingRequests.put(address, new 
PendingRequest(request.getPdu().getFunctionFlag(), responseFuture));
         try {
             if (auditLog.isEnabled()) {
                 auditLog.write(AuditLogEventType.OUTGOING_MESSAGE,
@@ -196,29 +274,16 @@ public class ModbusRtuConnection extends 
ConnectionBase<ModbusRtuConfiguration>
             }
             messageCodec.send(request);
         } catch (MessageCodecException e) {
-            pendingRequests.remove(address);
+            pendingRequests.computeIfPresent(address, (key, pending) -> 
pending.future == responseFuture ? null : pending);
             responseFuture.completeExceptionally(new 
PlcRuntimeException("Failed to send request", e));
-            return;
         } catch (RuntimeException e) {
             // The responseFuture MUST complete no matter what: the request
             // chain's tail hangs off it, so an unchecked throw here (e.g.
             // from a custom AuditLog) would otherwise silently wedge every
             // subsequent request on this connection.
-            pendingRequests.remove(address, responseFuture);
+            pendingRequests.computeIfPresent(address, (key, pending) -> 
pending.future == responseFuture ? null : pending);
             responseFuture.completeExceptionally(e);
-            return;
         }
-
-        long timeoutMs = getConfiguration().getRequestTimeout();
-        responseFuture.orTimeout(timeoutMs, TimeUnit.MILLISECONDS)
-            .whenComplete((result, error) -> {
-                if (error instanceof TimeoutException) {
-                    // Two-arg remove: only clears our own entry, immune to
-                    // dependent-ordering (a late cleanup can never remove a
-                    // successor request's entry).
-                    pendingRequests.remove(address, responseFuture);
-                }
-            });
     }
 
     
////////////////////////////////////////////////////////////////////////////////////////////////////////////////////
diff --git 
a/plc4j/drivers/modbus/src/main/java/org/apache/plc4x/java/modbus/rtu/config/ModbusRtuConfiguration.java
 
b/plc4j/drivers/modbus/src/main/java/org/apache/plc4x/java/modbus/rtu/config/ModbusRtuConfiguration.java
index 1e6eca0eae..b5165dbcab 100644
--- 
a/plc4j/drivers/modbus/src/main/java/org/apache/plc4x/java/modbus/rtu/config/ModbusRtuConfiguration.java
+++ 
b/plc4j/drivers/modbus/src/main/java/org/apache/plc4x/java/modbus/rtu/config/ModbusRtuConfiguration.java
@@ -30,7 +30,7 @@ public class ModbusRtuConfiguration implements Configuration {
 
     @ConfigurationParameter("request-timeout")
     @IntDefaultValue(5_000)
-    @Description("Default timeout for all types of requests.")
+    @Description("Default timeout for all types of requests. The timeout 
covers the full time from submission including queueing; queued requests whose 
remaining budget falls below a small dispatch margin (at most a quarter of the 
timeout, capped at 50 ms) fail fast instead of being sent.")
     private int requestTimeout;
 
     @ConfigurationParameter("default-unit-identifier")
diff --git 
a/plc4j/drivers/modbus/src/test/java/org/apache/plc4x/java/modbus/ascii/ModbusAsciiConnectionTest.java
 
b/plc4j/drivers/modbus/src/test/java/org/apache/plc4x/java/modbus/ascii/ModbusAsciiConnectionTest.java
index 1ff97851e8..7dcccde7a4 100644
--- 
a/plc4j/drivers/modbus/src/test/java/org/apache/plc4x/java/modbus/ascii/ModbusAsciiConnectionTest.java
+++ 
b/plc4j/drivers/modbus/src/test/java/org/apache/plc4x/java/modbus/ascii/ModbusAsciiConnectionTest.java
@@ -34,6 +34,7 @@ import org.apache.plc4x.java.utils.auditlog.api.AuditLog;
 import org.junit.jupiter.api.BeforeEach;
 import org.junit.jupiter.api.Test;
 
+import java.lang.reflect.Constructor;
 import java.lang.reflect.Field;
 import java.lang.reflect.Method;
 import java.util.Arrays;
@@ -199,6 +200,21 @@ class ModbusAsciiConnectionTest {
         assertEquals(ModbusByteOrder.LITTLE_ENDIAN, method.invoke(connection, 
tag));
     }
 
+    /**
+     * pendingRequests holds {@code PendingRequest} (function-code-tagged)
+     * holders rather than raw futures; this reflects the holder in the
+     * same way production code does (byte functionFlag, CompletableFuture 
future).
+     */
+    private static Object newPendingRequest(byte functionFlag, 
CompletableFuture<ModbusAsciiADU> future) throws Exception {
+        Class<?> pendingRequestClass = 
Arrays.stream(ModbusAsciiConnection.class.getDeclaredClasses())
+            .filter(c -> c.getSimpleName().equals("PendingRequest"))
+            .findFirst()
+            .orElseThrow(() -> new IllegalStateException("PendingRequest 
nested class not found"));
+        Constructor<?> constructor = 
pendingRequestClass.getDeclaredConstructor(byte.class, CompletableFuture.class);
+        constructor.setAccessible(true);
+        return constructor.newInstance(functionFlag, future);
+    }
+
     @Test
     void testHandleIncomingMessage() throws Exception {
         Method method = 
ModbusAsciiConnection.class.getDeclaredMethod("handleIncomingMessage", 
ModbusAsciiADU.class);
@@ -207,11 +223,10 @@ class ModbusAsciiConnectionTest {
         Field pendingField = 
ModbusAsciiConnection.class.getDeclaredField("pendingRequests");
         pendingField.setAccessible(true);
         @SuppressWarnings("unchecked")
-        Map<Short, CompletableFuture<ModbusAsciiADU>> pendingRequests =
-            (Map<Short, CompletableFuture<ModbusAsciiADU>>) 
pendingField.get(connection);
+        Map<Short, Object> pendingRequests = (Map<Short, Object>) 
pendingField.get(connection);
 
         CompletableFuture<ModbusAsciiADU> future = new CompletableFuture<>();
-        pendingRequests.put((short) 1, future);
+        pendingRequests.put((short) 1, newPendingRequest((byte) 0x03, future));
 
         ModbusAsciiADU responseAdu = new ModbusAsciiADU((short) 1,
             new ModbusPDUReadHoldingRegistersResponse(new byte[]{0x00, 0x2A}));
@@ -235,11 +250,10 @@ class ModbusAsciiConnectionTest {
         Field pendingField = 
ModbusAsciiConnection.class.getDeclaredField("pendingRequests");
         pendingField.setAccessible(true);
         @SuppressWarnings("unchecked")
-        Map<Short, CompletableFuture<ModbusAsciiADU>> pendingRequests =
-            (Map<Short, CompletableFuture<ModbusAsciiADU>>) 
pendingField.get(connection);
+        Map<Short, Object> pendingRequests = (Map<Short, Object>) 
pendingField.get(connection);
 
         CompletableFuture<ModbusAsciiADU> future = new CompletableFuture<>();
-        pendingRequests.put((short) 1, future);
+        pendingRequests.put((short) 1, newPendingRequest((byte) 0x03, future));
 
         connection.close();
 
@@ -252,11 +266,10 @@ class ModbusAsciiConnectionTest {
         Field pendingField = 
ModbusAsciiConnection.class.getDeclaredField("pendingRequests");
         pendingField.setAccessible(true);
         @SuppressWarnings("unchecked")
-        Map<Short, CompletableFuture<ModbusAsciiADU>> pendingRequests =
-            (Map<Short, CompletableFuture<ModbusAsciiADU>>) 
pendingField.get(connection);
+        Map<Short, Object> pendingRequests = (Map<Short, Object>) 
pendingField.get(connection);
 
         CompletableFuture<ModbusAsciiADU> future = new CompletableFuture<>();
-        pendingRequests.put((short) 1, future);
+        pendingRequests.put((short) 1, newPendingRequest((byte) 0x03, future));
 
         Method method = 
ModbusAsciiConnection.class.getDeclaredMethod("onTransportDisconnected", 
Throwable.class);
         method.setAccessible(true);
diff --git 
a/plc4j/drivers/modbus/src/test/java/org/apache/plc4x/java/modbus/rtu/ModbusRtuConnectionRequestChainTest.java
 
b/plc4j/drivers/modbus/src/test/java/org/apache/plc4x/java/modbus/rtu/ModbusRtuConnectionRequestChainTest.java
index 394d646602..3a93031132 100644
--- 
a/plc4j/drivers/modbus/src/test/java/org/apache/plc4x/java/modbus/rtu/ModbusRtuConnectionRequestChainTest.java
+++ 
b/plc4j/drivers/modbus/src/test/java/org/apache/plc4x/java/modbus/rtu/ModbusRtuConnectionRequestChainTest.java
@@ -18,9 +18,12 @@
  */
 package org.apache.plc4x.java.modbus.rtu;
 
+import org.apache.plc4x.java.modbus.readwrite.ModbusErrorCode;
 import org.apache.plc4x.java.modbus.readwrite.ModbusPDU;
+import org.apache.plc4x.java.modbus.readwrite.ModbusPDUError;
 import 
org.apache.plc4x.java.modbus.readwrite.ModbusPDUReadHoldingRegistersRequest;
 import 
org.apache.plc4x.java.modbus.readwrite.ModbusPDUReadHoldingRegistersResponse;
+import 
org.apache.plc4x.java.modbus.readwrite.ModbusPDUWriteSingleRegisterResponse;
 import org.apache.plc4x.java.modbus.readwrite.ModbusRtuADU;
 import org.apache.plc4x.java.modbus.rtu.config.ModbusRtuConfiguration;
 import org.apache.plc4x.java.modbus.types.ModbusByteOrder;
@@ -44,9 +47,11 @@ import java.util.function.BooleanSupplier;
 
 import static org.junit.jupiter.api.Assertions.assertArrayEquals;
 import static org.junit.jupiter.api.Assertions.assertEquals;
+import static org.junit.jupiter.api.Assertions.assertFalse;
 import static org.junit.jupiter.api.Assertions.assertNotNull;
 import static org.junit.jupiter.api.Assertions.assertNotSame;
 import static org.junit.jupiter.api.Assertions.assertThrows;
+import static org.junit.jupiter.api.Assertions.assertTrue;
 import static org.junit.jupiter.api.Assertions.fail;
 import static org.mockito.Mockito.mock;
 import static org.mockito.Mockito.when;
@@ -147,13 +152,80 @@ class ModbusRtuConnectionRequestChainTest {
         }
     }
 
+    @Test
+    void mismatchedFunctionCodeIsDiscardedAndPendingSurvives() throws 
Exception {
+        ScriptedAsyncTransport transport = new ScriptedAsyncTransport();
+        ModbusRtuConnection connection = newConnectedConnection(transport);
+
+        CompletableFuture<ModbusRtuADU> pendingRead = connection.sendRequest(
+            readHoldingRegistersRequestAdu(1, 0x0000, 1), (short) 1); // fc 
0x03
+
+        // A write-echo frame (fc 0x06) for the same unit must NOT complete it.
+        transport.deliver(wireBytes(new ModbusRtuADU((short) 1,
+            new ModbusPDUWriteSingleRegisterResponse(0x0010, 0x1234))));
+        transport.runDataListener();
+        assertFalse(pendingRead.isDone(), "mismatched fc must be discarded, 
pending must survive");
+
+        // The genuine 0x03 response still completes it.
+        transport.deliver(readResponseFrame(1, new byte[]{0x11, 0x22}));
+        transport.runDataListener();
+        assertArrayEquals(new byte[]{0x11, 0x22},
+            extractRegisterBytes(pendingRead.get(2, TimeUnit.SECONDS)));
+    }
+
+    @Test
+    void exceptionResponseCompletesAnyPendingRequest() throws Exception {
+        ScriptedAsyncTransport transport = new ScriptedAsyncTransport();
+        ModbusRtuConnection connection = newConnectedConnection(transport);
+
+        CompletableFuture<ModbusRtuADU> pendingRead = connection.sendRequest(
+            readHoldingRegistersRequestAdu(1, 0x0000, 1), (short) 1);
+
+        transport.deliver(wireBytes(new ModbusRtuADU((short) 1,
+            new ModbusPDUError(ModbusErrorCode.ILLEGAL_DATA_ADDRESS))));
+        transport.runDataListener();
+
+        ModbusRtuADU response = pendingRead.get(2, TimeUnit.SECONDS);
+        assertTrue(response.getPdu().getErrorFlag(), "exception frames answer 
any pending request");
+    }
+
+    @Test
+    void requestTimedOutWhileQueuedNeverReachesTheWire() throws Exception {
+        ScriptedAsyncTransport transport = new ScriptedAsyncTransport();
+        // Short request timeout so the queued request's total budget expires
+        // while the head transaction is still outstanding.
+        ModbusRtuConnection connection = newConnectedConnection(transport, 
200);
+
+        // Head request dispatches and stays pending (never answered).
+        CompletableFuture<ModbusRtuADU> head = connection.sendRequest(
+            readHoldingRegistersRequestAdu(1, 0x0000, 1), (short) 1);
+        awaitTrue(() -> transport.writeCount() == 1, 2, TimeUnit.SECONDS);
+
+        // Second request queues behind it and must time out WHILE QUEUED.
+        CompletableFuture<ModbusRtuADU> queued = connection.sendRequest(
+            readHoldingRegistersRequestAdu(1, 0x0010, 1), (short) 1);
+        assertThrows(ExecutionException.class, () -> queued.get(2, 
TimeUnit.SECONDS),
+            "queued request must time out from its enqueue-time clock");
+
+        // Head times out too (same 200ms clock); the chain then dispatches the
+        // dead queued request — which must be SKIPPED: no second wire write.
+        assertThrows(ExecutionException.class, () -> head.get(2, 
TimeUnit.SECONDS));
+        Thread.sleep(200); // give the chain's async dispatch a beat
+        assertEquals(1, transport.writeCount(),
+            "a request that died in the queue must never reach the wire");
+    }
+
     /**
      * Builds a connection wired to the given fake transport, and drives it
      * through the same construction/connect path as {@code 
ModbusRtuConnectionTest}.
      */
     private static ModbusRtuConnection 
newConnectedConnection(ScriptedAsyncTransport transport) throws Exception {
+        return newConnectedConnection(transport, 5000);
+    }
+
+    private static ModbusRtuConnection 
newConnectedConnection(ScriptedAsyncTransport transport, int requestTimeoutMs) 
throws Exception {
         ModbusRtuConfiguration config = new ModbusRtuConfiguration();
-        config.setRequestTimeout(5000);
+        config.setRequestTimeout(requestTimeoutMs);
         config.setDefaultUnitIdentifier(1);
         config.setPingAddress("4x00001:BOOL");
         config.setDefaultPayloadByteOrder(ModbusByteOrder.BIG_ENDIAN);
diff --git 
a/plc4j/drivers/modbus/src/test/java/org/apache/plc4x/java/modbus/rtu/ModbusRtuConnectionTest.java
 
b/plc4j/drivers/modbus/src/test/java/org/apache/plc4x/java/modbus/rtu/ModbusRtuConnectionTest.java
index ebcc39f7b1..2035fd269a 100644
--- 
a/plc4j/drivers/modbus/src/test/java/org/apache/plc4x/java/modbus/rtu/ModbusRtuConnectionTest.java
+++ 
b/plc4j/drivers/modbus/src/test/java/org/apache/plc4x/java/modbus/rtu/ModbusRtuConnectionTest.java
@@ -34,6 +34,7 @@ import org.apache.plc4x.java.utils.auditlog.api.AuditLog;
 import org.junit.jupiter.api.BeforeEach;
 import org.junit.jupiter.api.Test;
 
+import java.lang.reflect.Constructor;
 import java.lang.reflect.Field;
 import java.lang.reflect.Method;
 import java.util.Arrays;
@@ -211,6 +212,21 @@ class ModbusRtuConnectionTest {
         assertEquals(ModbusByteOrder.LITTLE_ENDIAN, method.invoke(connection, 
tag));
     }
 
+    /**
+     * pendingRequests holds {@code PendingRequest} (function-code-tagged)
+     * holders rather than raw futures; this reflects the holder in the
+     * same way production code does (byte functionFlag, CompletableFuture 
future).
+     */
+    private static Object newPendingRequest(byte functionFlag, 
CompletableFuture<ModbusRtuADU> future) throws Exception {
+        Class<?> pendingRequestClass = 
Arrays.stream(ModbusRtuConnection.class.getDeclaredClasses())
+            .filter(c -> c.getSimpleName().equals("PendingRequest"))
+            .findFirst()
+            .orElseThrow(() -> new IllegalStateException("PendingRequest 
nested class not found"));
+        Constructor<?> constructor = 
pendingRequestClass.getDeclaredConstructor(byte.class, CompletableFuture.class);
+        constructor.setAccessible(true);
+        return constructor.newInstance(functionFlag, future);
+    }
+
     @Test
     void testHandleIncomingMessage() throws Exception {
         Method method = 
ModbusRtuConnection.class.getDeclaredMethod("handleIncomingMessage", 
ModbusRtuADU.class);
@@ -219,11 +235,10 @@ class ModbusRtuConnectionTest {
         Field pendingField = 
ModbusRtuConnection.class.getDeclaredField("pendingRequests");
         pendingField.setAccessible(true);
         @SuppressWarnings("unchecked")
-        Map<Short, CompletableFuture<ModbusRtuADU>> pendingRequests =
-            (Map<Short, CompletableFuture<ModbusRtuADU>>) 
pendingField.get(connection);
+        Map<Short, Object> pendingRequests = (Map<Short, Object>) 
pendingField.get(connection);
 
         CompletableFuture<ModbusRtuADU> future = new CompletableFuture<>();
-        pendingRequests.put((short) 1, future);
+        pendingRequests.put((short) 1, newPendingRequest((byte) 0x03, future));
 
         ModbusRtuADU responseAdu = new ModbusRtuADU((short) 1,
             new ModbusPDUReadHoldingRegistersResponse(new byte[]{0x00, 0x2A}));
@@ -248,11 +263,10 @@ class ModbusRtuConnectionTest {
         Field pendingField = 
ModbusRtuConnection.class.getDeclaredField("pendingRequests");
         pendingField.setAccessible(true);
         @SuppressWarnings("unchecked")
-        Map<Short, CompletableFuture<ModbusRtuADU>> pendingRequests =
-            (Map<Short, CompletableFuture<ModbusRtuADU>>) 
pendingField.get(connection);
+        Map<Short, Object> pendingRequests = (Map<Short, Object>) 
pendingField.get(connection);
 
         CompletableFuture<ModbusRtuADU> future = new CompletableFuture<>();
-        pendingRequests.put((short) 1, future);
+        pendingRequests.put((short) 1, newPendingRequest((byte) 0x03, future));
 
         connection.close();
 
@@ -265,11 +279,10 @@ class ModbusRtuConnectionTest {
         Field pendingField = 
ModbusRtuConnection.class.getDeclaredField("pendingRequests");
         pendingField.setAccessible(true);
         @SuppressWarnings("unchecked")
-        Map<Short, CompletableFuture<ModbusRtuADU>> pendingRequests =
-            (Map<Short, CompletableFuture<ModbusRtuADU>>) 
pendingField.get(connection);
+        Map<Short, Object> pendingRequests = (Map<Short, Object>) 
pendingField.get(connection);
 
         CompletableFuture<ModbusRtuADU> future = new CompletableFuture<>();
-        pendingRequests.put((short) 1, future);
+        pendingRequests.put((short) 1, newPendingRequest((byte) 0x03, future));
 
         Method method = 
ModbusRtuConnection.class.getDeclaredMethod("onTransportDisconnected", 
Throwable.class);
         method.setAccessible(true);
diff --git 
a/plc4j/transports/serial/src/main/java/org/apache/plc4x/java/transport/serial/SerialTransportInstance.java
 
b/plc4j/transports/serial/src/main/java/org/apache/plc4x/java/transport/serial/SerialTransportInstance.java
index 00e2bf2be8..7f951fced3 100644
--- 
a/plc4j/transports/serial/src/main/java/org/apache/plc4x/java/transport/serial/SerialTransportInstance.java
+++ 
b/plc4j/transports/serial/src/main/java/org/apache/plc4x/java/transport/serial/SerialTransportInstance.java
@@ -54,6 +54,7 @@ public class SerialTransportInstance extends 
BaseTransportInstance<SerialTranspo
     // subscriber rings (64 KiB) so burst tolerance is consistent.
     private static final int DEFAULT_BUFFER_SIZE = 65536;
     private static final byte[] EMPTY_BYTES = new byte[0];
+    private static final java.util.concurrent.atomic.AtomicLong 
DISPATCH_THREAD_COUNTER = new java.util.concurrent.atomic.AtomicLong();
 
     private final SharedSerialPortManager sharedSerialPortManager;
     private final SerialPort port;
@@ -188,7 +189,7 @@ public class SerialTransportInstance extends 
BaseTransportInstance<SerialTranspo
                 };
                 tempSharedPort.addSubscriber(this.sharedSubscriber);
                 this.sharedDispatchExecutor = 
Executors.newSingleThreadExecutor(runnable -> {
-                    Thread thread = new Thread(runnable, 
"Serial-Shared-Dispatch-" + port);
+                    Thread thread = new Thread(runnable, 
"Serial-Shared-Dispatch-" + port + "-" + 
DISPATCH_THREAD_COUNTER.incrementAndGet());
                     thread.setDaemon(true);
                     return thread;
                 });
diff --git 
a/plc4j/transports/serial/src/test/java/org/apache/plc4x/java/transport/serial/SharedModeInstanceTest.java
 
b/plc4j/transports/serial/src/test/java/org/apache/plc4x/java/transport/serial/SharedModeInstanceTest.java
index 2d31f8f424..a5723d6981 100644
--- 
a/plc4j/transports/serial/src/test/java/org/apache/plc4x/java/transport/serial/SharedModeInstanceTest.java
+++ 
b/plc4j/transports/serial/src/test/java/org/apache/plc4x/java/transport/serial/SharedModeInstanceTest.java
@@ -185,6 +185,35 @@ class SharedModeInstanceTest {
         verify(mockPort).closePort();
     }
 
+    @Test
+    void eachSharedInstanceGetsAUniquelyNamedDispatchThread() throws Exception 
{
+        MockPortFactory factory = new MockPortFactory();
+        SharedSerialPortManager manager = new SharedSerialPortManager(factory);
+
+        SerialTransportInstance first = new SerialTransportInstance(
+            manager, "COMSHARED", config(), AuditLog.builder().build());
+        SerialTransportInstance second = new SerialTransportInstance(
+            manager, "COMSHARED", config(), AuditLog.builder().build());
+
+        try {
+            AtomicReference<String> firstThread = new AtomicReference<>();
+            AtomicReference<String> secondThread = new AtomicReference<>();
+            first.registerDataListener(() -> firstThread.compareAndSet(null, 
Thread.currentThread().getName()));
+            second.registerDataListener(() -> secondThread.compareAndSet(null, 
Thread.currentThread().getName()));
+
+            factory.broadcast(new byte[]{0x01, 0x02, 0x03, 0x04});
+            awaitTrue(() -> firstThread.get() != null && secondThread.get() != 
null, 5, TimeUnit.SECONDS);
+
+            
assertTrue(firstThread.get().startsWith("Serial-Shared-Dispatch-"), 
firstThread.get());
+            
assertTrue(secondThread.get().startsWith("Serial-Shared-Dispatch-"), 
secondThread.get());
+            assertNotEquals(firstThread.get(), secondThread.get(),
+                "two instances on one port must have distinct dispatch 
threads");
+        } finally {
+            first.close();
+            second.close();
+        }
+    }
+
     /**
      * Regression test for shared-mode dispatch isolation: the shared reader
      * thread iterates all subscribers' onData() inline 
(SharedPort.readFromPort()).


Reply via email to