soldom opened a new pull request, #2630:
URL: https://github.com/apache/plc4x/pull/2630
Closes #2629.
### Problem
The ADS connect handshake (`AdsTcpConnection.doConnectHandshake()` and
`onPing()`) sent its probe
requests — `ReadDeviceInfo`, online-version, symbol-version — to a hardcoded
AMS port
`DefaultAmsPorts.RUNTIME_SYSTEM_01` (851) with a hardcoded source port
`800`, ignoring the configured
`target-ams-port` / `source-ams-port`. Only the handshake was affected; the
symbol/datatype-table
reads and the read/write path already use
`getConfiguration().getTargetAmsPort()`.
Consequence: any PLC runtime not on 851 — a second PLC project (852), a
non-default port, or parallel
runtimes — failed to connect during the handshake with ADS error `0x6`
("target port not found"),
even with `target-ams-port` set correctly. Full analysis and a packet
capture are in #2629.
It may be intended to have the handshake port hardcoded to "System_01"
(851), but the reason escapes me
and it does break the above mentioned PLC setup use cases.
### Change
In
`plc4j/drivers/ads/src/main/java/org/apache/plc4x/java/ads/AdsTcpConnection.java`,
the four
handshake/ping request builders now use the configured ports, matching the
data path:
```diff
- getConfiguration().getTargetAmsNetId(),
DefaultAmsPorts.RUNTIME_SYSTEM_01.getValue(),
- getConfiguration().getSourceAmsNetId(), 800, ReturnCode.OK,
getInvokeId());
+ getConfiguration().getTargetAmsNetId(),
getConfiguration().getTargetAmsPort(),
+ getConfiguration().getSourceAmsNetId(),
getConfiguration().getSourceAmsPort(), ReturnCode.OK, getInvokeId());
```
No behavior change for the common case: `target-ams-port` already defaults
to 851.
### Testing
Verified against a real Beckhoff TwinCAT `3.1.4026` IPC:
- PLC runtime on AMS port **852**, nothing on 851 — **before:** connect
fails (`AdsErrorResponse`,
AMS error 0x6); **after:** connects and reads a live symbol successfully.
- A packet capture (Wireshark AMS dissector) confirms the handshake
`ReadDeviceInfo` is now sent to
the configured `target-ams-port` (852) instead of 851.
- Regression check: with the PLC on 851 the connection still works as before.
--