Hi,

thanks for the fast reply, here's a link to the dump (was polling every 5s) 
https://drive.google.com/file/d/14d21onEG_D8-dPCgAu6RBL3dzZMN8oqN/view?usp=sharing

Etienne
On 2020/02/21 14:53:26, Christofer Dutz <[email protected]> wrote: 
> Hi Etienne,
> 
> that error is coming from the S7 optimizer which takes care of splitting up 
> large plc4x requests into smaller ones, depending on the PDU size negotiated 
> with the PLC.
> 
> Could you please do a wireshark dump of the communication and send that to me 
> (this list doesn't accept attachments) ... or you upload it to some file 
> sharing service and post a link here.
> 
> Chris
> 
> 
> 
> Am 21.02.20, 15:30 schrieb "Etienne Robinet" <[email protected]>:
> 
>     Hi,
>     
>     after getting these results on reading fom the PLC, I tried writing. 
> After some test I managed to send a write request but here's what I am 
> getting as error: 
>     
>     java.util.concurrent.ExecutionException: 
> java.lang.ArrayIndexOutOfBoundsException: arraycopy: last source index 1 out 
> of bounds for byte[0]
>             at 
> java.util.concurrent.CompletableFuture.reportGet(CompletableFuture.java:395) 
> ~[?:?]
>             at 
> java.util.concurrent.CompletableFuture.get(CompletableFuture.java:1999) ~[?:?]
>             at 
> org.apache.plc4x.camel.Plc4XProducer.process(Plc4XProducer.java:68) ~[?:?]
>             at 
> org.apache.plc4x.camel.Plc4XProducer.process(Plc4XProducer.java:86) ~[?:?]
>             at 
> org.apache.camel.processor.SendProcessor.process(SendProcessor.java:148) 
> ~[!/:2.24.2]
>             at 
> org.apache.camel.processor.RedeliveryErrorHandler.process(RedeliveryErrorHandler.java:548)
>  [!/:2.24.2]
>             at 
> org.apache.camel.processor.CamelInternalProcessor.process(CamelInternalProcessor.java:201)
>  [!/:2.24.2]
>             at org.apache.camel.processor.Pipeline.process(Pipeline.java:138) 
> [!/:2.24.2]
>             at org.apache.camel.processor.Pipeline.process(Pipeline.java:101) 
> [!/:2.24.2]
>             at 
> org.apache.camel.processor.CamelInternalProcessor.process(CamelInternalProcessor.java:201)
>  [!/:2.24.2]
>             at 
> org.apache.camel.component.timer.TimerConsumer.sendTimerExchange(TimerConsumer.java:197)
>  [!/:2.24.2]
>             at 
> org.apache.camel.component.timer.TimerConsumer$1.run(TimerConsumer.java:79) 
> [!/:2.24.2]
>             at java.util.TimerThread.mainLoop(Timer.java:556) [?:?]
>             at java.util.TimerThread.run(Timer.java:506) [?:?]
>     Caused by: java.lang.ArrayIndexOutOfBoundsException: arraycopy: last 
> source index 1 out of bounds for byte[0]
>             at java.lang.System.arraycopy(Native Method) ~[?:?]
>             at 
> org.apache.plc4x.java.s7.netty.strategies.DefaultS7MessageProcessor.processNonBooleanWriteVarParameter(DefaultS7MessageProcessor.java:309)
>  ~[?:?]
>             at 
> org.apache.plc4x.java.s7.netty.strategies.DefaultS7MessageProcessor.processWriteVarParameter(DefaultS7MessageProcessor.java:226)
>  ~[?:?]
>             at 
> org.apache.plc4x.java.s7.netty.strategies.DefaultS7MessageProcessor.processRequest(DefaultS7MessageProcessor.java:98)
>  ~[?:?]
>             at 
> org.apache.plc4x.java.s7.netty.S7Protocol.write(S7Protocol.java:178) ~[?:?]
>             at 
> io.netty.channel.AbstractChannelHandlerContext.invokeWrite0(AbstractChannelHandlerContext.java:716)
>  ~[?:?]
>             at 
> io.netty.channel.AbstractChannelHandlerContext.invokeWrite(AbstractChannelHandlerContext.java:708)
>  ~[?:?]
>             at 
> io.netty.channel.AbstractChannelHandlerContext.write(AbstractChannelHandlerContext.java:791)
>  ~[?:?]
>             at 
> io.netty.channel.AbstractChannelHandlerContext.write(AbstractChannelHandlerContext.java:701)
>  ~[?:?]
>             at 
> io.netty.handler.codec.MessageToMessageEncoder.write(MessageToMessageEncoder.java:112)
>  ~[?:?]
>             at 
> io.netty.handler.codec.MessageToMessageCodec.write(MessageToMessageCodec.java:116)
>  ~[?:?]
>             at 
> io.netty.channel.AbstractChannelHandlerContext.invokeWrite0(AbstractChannelHandlerContext.java:716)
>  ~[?:?]
>             at 
> io.netty.channel.AbstractChannelHandlerContext.invokeWrite(AbstractChannelHandlerContext.java:708)
>  ~[?:?]
>             at 
> io.netty.channel.AbstractChannelHandlerContext.access$1700(AbstractChannelHandlerContext.java:56)
>  ~[?:?]
>             at 
> io.netty.channel.AbstractChannelHandlerContext$AbstractWriteTask.write(AbstractChannelHandlerContext.java:1102)
>  ~[?:?]
>             at 
> io.netty.channel.AbstractChannelHandlerContext$WriteAndFlushTask.write(AbstractChannelHandlerContext.java:1149)
>  ~[?:?]
>             at 
> io.netty.channel.AbstractChannelHandlerContext$AbstractWriteTask.run(AbstractChannelHandlerContext.java:1073)
>  ~[?:?]
>             at 
> io.netty.util.concurrent.AbstractEventExecutor.safeExecute(AbstractEventExecutor.java:163)
>  ~[?:?]
>             at 
> io.netty.util.concurrent.SingleThreadEventExecutor.runAllTasks(SingleThreadEventExecutor.java:416)
>  ~[?:?]
>             at io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:515) 
> ~[?:?]
>             at 
> io.netty.util.concurrent.SingleThreadEventExecutor$5.run(SingleThreadEventExecutor.java:918)
>  ~[?:?]
>             at 
> io.netty.util.internal.ThreadExecutorMap$2.run(ThreadExecutorMap.java:74) 
> ~[?:?]
>             at 
> io.netty.util.concurrent.FastThreadLocalRunnable.run(FastThreadLocalRunnable.java:30)
>  ~[?:?]
>             at java.lang.Thread.run(Thread.java:834) ~[?:?]
>     
>     Any ideas on that?
>     Here is the route I built:
>     
>     <blueprint xmlns="http://www.osgi.org/xmlns/blueprint/v1.0.0"; 
> default-activation="lazy">
>         <camelContext id="S7-PLC-Context" 
> xmlns="http://camel.apache.org/schema/blueprint"; streamCache="true" >
>             <route>
>                 <from uri="timer://foo?fixedRate=true&period=5000" />
>                 <setHeader  headerName="fieldName">
>                     <constant>default</constant>
>                 </setHeader>
>                 <setHeader headerName="fieldQuery">
>                     <constant>%DB1:4.0:STRING</constant>
>                 </setHeader>
>                 <setBody >
>                     <simple>Hello</simple>
>                 </setBody>
>                 <log message=" Sending to PLC:  ${body} at 
> ${date:now:HH:mm:ss}" loggingLevel="INFO" />
>                 <to uri="plc4x:s7://192.168.178.10/0/1" />
>             </route>
>         </camelContext>
>     </blueprint>
>     
>     
>     Etienne
>     On 2020/02/20 07:50:39, Julian Feinauer <[email protected]> 
> wrote: 
>     > Thank you Etienne, I will try to reproduce the issue and have a look.
>     > But dont know when I will find the time as I'm currently travelling : /
>     > 
>     > Julian
>     > 
>     > Am 19.02.20, 14:06 schrieb "Etienne Robinet" <[email protected]>:
>     > 
>     >     Hi,
>     >     I started the Jira issue: 
> https://issues.apache.org/jira/browse/PLC4X-177 
>     >     Using this XML:
>     >     
>     >     <route>
>     >                 <from uri="timer://foo?fixedRate=true&period=1000"/>
>     >                 <pollEnrich>
>     >                     
> <constant>plc4x:s7://192.168.178.10/0/1?address=%MW102:INT</constant>
>     >                 </pollEnrich>
>     >                 <log message=" Sending ${body}" loggingLevel="INFO" />
>     >                 <to uri="mock:test?retainLast=10" />
>     >     
>     >     
>     >     
>     >             </route>
>     >     
>     >      it creates a PollingConsumer and reads every 1s. The problem is 
> after every read, I get this warning 
>     >     
>     >     14:01:12.850 WARN [nioEventLoopGroup-2523-1] An exceptionCaught() 
> event was fired, and it reached at the tail of the pipeline. It usually means 
> the last handler in the pipeline did not handle the exception.
>     >     java.io.IOException: An existing connection was forcibly closed by 
> the remote host
>     >             at sun.nio.ch.SocketDispatcher.read0(Native Method) ~[?:?]
>     >             at 
> sun.nio.ch.SocketDispatcher.read(SocketDispatcher.java:43) ~[?:?]
>     >             at sun.nio.ch.IOUtil.readIntoNativeBuffer(IOUtil.java:276) 
> ~[?:?]
>     >             at sun.nio.ch.IOUtil.read(IOUtil.java:233) ~[?:?]
>     >             at sun.nio.ch.IOUtil.read(IOUtil.java:223) ~[?:?]
>     >             at 
> sun.nio.ch.SocketChannelImpl.read(SocketChannelImpl.java:358) ~[?:?]
>     >             at 
> io.netty.buffer.PooledByteBuf.setBytes(PooledByteBuf.java:247) 
> ~[!/:4.1.39.Final]
>     >             at 
> io.netty.buffer.AbstractByteBuf.writeBytes(AbstractByteBuf.java:1140) 
> ~[!/:4.1.39.Final]
>     >             at 
> io.netty.channel.socket.nio.NioSocketChannel.doReadBytes(NioSocketChannel.java:347)
>  ~[!/:4.1.39.Final]
>     >             at 
> io.netty.channel.nio.AbstractNioByteChannel$NioByteUnsafe.read(AbstractNioByteChannel.java:148)
>  [!/:4.1.39.Final]
>     >             at 
> io.netty.channel.nio.NioEventLoop.processSelectedKey(NioEventLoop.java:697) 
> [!/:4.1.39.Final]
>     >             at 
> io.netty.channel.nio.NioEventLoop.processSelectedKeysOptimized(NioEventLoop.java:632)
>  [!/:4.1.39.Final]
>     >             at 
> io.netty.channel.nio.NioEventLoop.processSelectedKeys(NioEventLoop.java:549) 
> [!/:4.1.39.Final]
>     >             at 
> io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:511) [!/:4.1.39.Final]
>     >             at 
> io.netty.util.concurrent.SingleThreadEventExecutor$5.run(SingleThreadEventExecutor.java:918)
>  [!/:4.1.39.Final]
>     >             at 
> io.netty.util.internal.ThreadExecutorMap$2.run(ThreadExecutorMap.java:74) 
> [!/:4.1.39.Final]
>     >             at 
> io.netty.util.concurrent.FastThreadLocalRunnable.run(FastThreadLocalRunnable.java:30)
>  [!/:4.1.39.Final]
>     >             at java.lang.Thread.run(Thread.java:834) [?:?]
>     >     
>     >     Seems like the connection is closed then opened again every time? 
> Here you can see that I manage to get the data tho: 
> https://i.imgur.com/K6TTwxA.png
>     >     
>     >     Etienne
>     >     On 2020/02/19 12:20:40, Julian Feinauer 
> <[email protected]> wrote: 
>     >     > Hi Etienne,
>     >     > 
>     >     > thanks fort he update.
>     >     > I think the Camel integration was never really used, so it could 
> be a bit unhandy, so to say : )
>     >     > Probably you create an Issue in Jira 
> https://issues.apache.org/jira/projects/PLC4X/issues where we track all 
> activites and can help you with improvements.
>     >     > 
>     >     > Best
>     >     > Julian
>     >     > 
>     >     > Am 19.02.20, 12:50 schrieb "Etienne Robinet" <[email protected]>:
>     >     > 
>     >     >     Hi all,
>     >     >     quick update, it worked on Camel inside Karaf with Julian's 
> code. I managed to read from output, memento and datablock wit hthe correct 
> adress input:
>     >     >     
>     >     >     <from 
> uri="plc4x:s7://192.168.178.10/0/1?address=%25DB1:4.0:STRING"/>
>     >     >     -"%25" gets encoded as "%" in XML
>     >     >     -I fetch in the DB1 at byte 4 starting at his bit 0 and the 
> data I want is a STRING.
>     >     >     -To read a memento, this also worked: address+%25MW102:INT
>     >     >     
>     >     >     Now I am going to investigate the polling consumer, as I want 
> to fetch the data from the PLC at a polling interval.
>     >     >     
>     >     >     Etienne
>     >     >     On 2020/02/18 16:49:31, Etienne Robinet <[email protected]> 
> wrote: 
>     >     >     > I managed to get the tool working. By that I mean I got to 
> to a read on my PLC, but seems like the connection is crashing afterwards.
>     >     >     > 17:46:56.556 [main] INFO  
> o.apache.plc4x.java.PlcDriverManager - Instantiating new PLC Driver Manager 
> with class loader jdk.internal.loader.ClassLoaders$AppClassLoader@78308db1
>     >     >     > 17:46:56.563 [main] INFO  
> o.apache.plc4x.java.PlcDriverManager - Registering available drivers...
>     >     >     > 17:46:56.579 [main] INFO  
> o.apache.plc4x.java.PlcDriverManager - Registering driver for Protocol s7 
> (Siemens S7 (Basic))
>     >     >     > 17:46:56.588 [main] INFO  
> o.apache.plc4x.java.PlcDriverManager - Registering driver for Protocol ab-eth 
> (Allen Bradley ETH)
>     >     >     > 17:46:56.628 [main] INFO  
> o.apache.plc4x.java.PlcDriverManager - Registering driver for Protocol ads 
> (Beckhoff Twincat ADS)
>     >     >     > 17:46:56.638 [main] INFO  
> o.apache.plc4x.java.PlcDriverManager - Registering driver for Protocol eip 
> (EtherNet/IP (TCP))
>     >     >     > 17:46:56.655 [main] INFO  
> o.apache.plc4x.java.PlcDriverManager - Registering driver for Protocol modbus 
> (Modbus (TCP / Serial))
>     >     >     > 17:46:56.723 [main] INFO  
> o.apache.plc4x.java.PlcDriverManager - Registering driver for Protocol opcua 
> (OPC UA (TCP))
>     >     >     > 17:46:56.736 [main] INFO  
> o.apache.plc4x.java.PlcDriverManager - Registering driver for Protocol test 
> (PLC4X Test Protocol)
>     >     >     > 17:46:57.059 [main] INFO  
> o.a.p.j.s.connection.S7PlcConnection - Setting up S7 Connection with: 
> host-name 192.168.178.10, rack 0, slot 1, pdu-size 1024, max-amq-caller 8, 
> max-amq-callee 8
>     >     >     > 17:46:58.758 [nioEventLoopGroup-2-1] INFO  
> o.a.plc4x.java.s7.netty.S7Protocol - S7Connection established pdu-size 960, 
> max-amq-caller 3, max-amq-callee 3
>     >     >     > 17:46:58.776 [nioEventLoopGroup-2-1] INFO  
> o.a.plc4x.java.s7.netty.S7Protocol - Successfully connected to S7: S7_1500 
> wit PDU 960
>     >     >     > 17:46:58.800 [main] INFO  o.a.p.j.e.helloplc4x.HelloPlc4x - 
> Synchronous request ...
>     >     >     > 17:46:58.836 [main] INFO  o.a.p.j.e.helloplc4x.HelloPlc4x - 
> Value[value-0]: true
>     >     >     > 17:46:58.836 [main] INFO  o.a.p.j.e.helloplc4x.HelloPlc4x - 
> Asynchronous request ...
>     >     >     > 17:46:58.838 [nioEventLoopGroup-2-1] INFO  
> o.a.p.j.e.helloplc4x.HelloPlc4x - Value[value-0]: true
>     >     >     > 17:46:58.844 [nioEventLoopGroup-2-1] WARN  
> i.n.channel.DefaultChannelPipeline - An exceptionCaught() event was fired, 
> and it reached at the tail of the pipeline. It usually means the last handler 
> in the pipeline did not handle the exception.
>     >     >     > java.io.IOException: An existing connection was forcibly 
> closed by the remote host
>     >     >     >     at java.base/sun.nio.ch.SocketDispatcher.read0(Native 
> Method)
>     >     >     >     at 
> java.base/sun.nio.ch.SocketDispatcher.read(SocketDispatcher.java:43)
>     >     >     >     at 
> java.base/sun.nio.ch.IOUtil.readIntoNativeBuffer(IOUtil.java:276)
>     >     >     >     at java.base/sun.nio.ch.IOUtil.read(IOUtil.java:233)
>     >     >     >     at java.base/sun.nio.ch.IOUtil.read(IOUtil.java:223)
>     >     >     >     at 
> java.base/sun.nio.ch.SocketChannelImpl.read(SocketChannelImpl.java:358)
>     >     >     >     at 
> io.netty.buffer.PooledByteBuf.setBytes(PooledByteBuf.java:247)
>     >     >     >     at 
> io.netty.buffer.AbstractByteBuf.writeBytes(AbstractByteBuf.java:1140)
>     >     >     >     at 
> io.netty.channel.socket.nio.NioSocketChannel.doReadBytes(NioSocketChannel.java:347)
>     >     >     >     at 
> io.netty.channel.nio.AbstractNioByteChannel$NioByteUnsafe.read(AbstractNioByteChannel.java:148)
>     >     >     >     at 
> io.netty.channel.nio.NioEventLoop.processSelectedKey(NioEventLoop.java:697)
>     >     >     >     at 
> io.netty.channel.nio.NioEventLoop.processSelectedKeysOptimized(NioEventLoop.java:632)
>     >     >     >     at 
> io.netty.channel.nio.NioEventLoop.processSelectedKeys(NioEventLoop.java:549)
>     >     >     >     at 
> io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:511)
>     >     >     >     at 
> io.netty.util.concurrent.SingleThreadEventExecutor$5.run(SingleThreadEventExecutor.java:918)
>     >     >     >     at 
> io.netty.util.internal.ThreadExecutorMap$2.run(ThreadExecutorMap.java:74)
>     >     >     >     at 
> io.netty.util.concurrent.FastThreadLocalRunnable.run(FastThreadLocalRunnable.java:30)
>     >     >     >     at java.base/java.lang.Thread.run(Thread.java:834)
>     >     >     > Disconnected from the target VM, address: 
> '127.0.0.1:61672', transport: 'socket'
>     >     >     > 
>     >     >     > Process finished with exit code 0
>     >     >     > 
>     >     >     > This did the trick: I had o also enable PUT/GET on my PLC 
> (via TIA Portal).
>     >     >     > Etienne
>     >     >     > On 2020/02/18 14:08:11, Etienne Robinet <[email protected]> 
> wrote: 
>     >     >     > > Hi, I tried the HelloPLC4X Tool, but it seems like he 
> gets stuck. I'm still not sure about the arguments I am passing, here's the 
> log 
>     >     >     > > 
>     >     >     > > 15:05:42.838 [main] INFO  
> o.apache.plc4x.java.PlcDriverManager - Instantiating new PLC Driver Manager 
> with class loader jdk.internal.loader.ClassLoaders$AppClassLoader@78308db1
>     >     >     > > 15:05:42.874 [main] INFO  
> o.apache.plc4x.java.PlcDriverManager - Registering available drivers...
>     >     >     > > 15:05:42.892 [main] INFO  
> o.apache.plc4x.java.PlcDriverManager - Registering driver for Protocol s7 
> (Siemens S7 (Basic))
>     >     >     > > 15:05:42.899 [main] INFO  
> o.apache.plc4x.java.PlcDriverManager - Registering driver for Protocol ab-eth 
> (Allen Bradley ETH)
>     >     >     > > 15:05:42.933 [main] INFO  
> o.apache.plc4x.java.PlcDriverManager - Registering driver for Protocol ads 
> (Beckhoff Twincat ADS)
>     >     >     > > 15:05:42.941 [main] INFO  
> o.apache.plc4x.java.PlcDriverManager - Registering driver for Protocol eip 
> (EtherNet/IP (TCP))
>     >     >     > > 15:05:42.956 [main] INFO  
> o.apache.plc4x.java.PlcDriverManager - Registering driver for Protocol modbus 
> (Modbus (TCP / Serial))
>     >     >     > > 15:05:42.980 [main] INFO  
> o.apache.plc4x.java.PlcDriverManager - Registering driver for Protocol opcua 
> (OPC UA (TCP))
>     >     >     > > 15:05:43.018 [main] INFO  
> o.apache.plc4x.java.PlcDriverManager - Registering driver for Protocol test 
> (PLC4X Test Protocol)
>     >     >     > > 15:05:43.553 [main] INFO  
> o.a.p.j.s.connection.S7PlcConnection - Setting up S7 Connection with: 
> host-name 192.168.178.10, rack 0, slot 1, pdu-size 1024, max-amq-caller 8, 
> max-amq-callee 8
>     >     >     > > 15:05:45.281 [nioEventLoopGroup-2-1] INFO  
> o.a.plc4x.java.s7.netty.S7Protocol - S7Connection established pdu-size 960, 
> max-amq-caller 3, max-amq-callee 3
>     >     >     > > 15:05:45.299 [nioEventLoopGroup-2-1] INFO  
> o.a.plc4x.java.s7.netty.S7Protocol - Successfully connected to S7: S7_1500 
> wit PDU 960
>     >     >     > > 15:05:45.321 [main] INFO  o.a.p.j.e.helloplc4x.HelloPlc4x 
> - Synchronous request ... <-----STUCKED
>     >     >     > > 
>     >     >     > > 
>     >     >     > > And here are the arguments I am passing:
>     >     >     > > --connection-string s7://192.168.178.10/0/1 
> --field-addresses %DB2:1.0:INT[1]
>     >     >     > > 
>     >     >     > > I also subscribed to the list ;-)
>     >     >     > > 
>     >     >     > > On 2020/02/18 13:28:24, Julian Feinauer 
> <[email protected]> wrote: 
>     >     >     > > > Hi Etienne,
>     >     >     > > > 
>     >     >     > > > first, you should try to just access it with the 
> HelloPlc4X Tool, just to check that everything works.
>     >     >     > > > And Second, please subscribe to the mailing list, 
> otherwise all your mails have to go through moderation : )
>     >     >     > > > 
>     >     >     > > > Julian
>     >     >     > > > 
>     >     >     > > > Am 18.02.20, 14:22 schrieb "Etienne Robinet" 
> <[email protected]>:
>     >     >     > > > 
>     >     >     > > >     Hi Julian, thanks for the fast reply!
>     >     >     > > >     
>     >     >     > > >     The route seems to be started, but I try to put the 
> body in log (to check) but with no sucess. Here is what I get with your code
>     >     >     > > >     
>     >     >     > > >     https://i.imgur.com/biB9ZpW.png
>     >     >     > > >     
>     >     >     > > >     After checking the code a bit, I tried to adapt my 
> route. I am trying to access a DB (number 2) on my PLC which has a 
> String(Hello) and an Int(5). I then try to show the body of the component on 
> the log to verify. Maybe my syntax of uri is again not correct?
>     >     >     > > >     
>     >     >     > > >     <from 
> uri="plc4x:s7://192.168.178.10/0/1?address=%25DB2:2.0:STRING[1]&dataType=java.lang.String"/>
>     >     >     > > >                 <log message=" Sending ${body}" 
> loggingLevel="INFO" />
>     >     >     > > >                 <to uri="mock:test?retainLast=10" />
>     >     >     > > >     
>     >     >     > > >     On 2020/02/18 12:28:53, Julian Feinauer 
> <[email protected]> wrote: 
>     >     >     > > >     > Hi Etienne,
>     >     >     > > >     > 
>     >     >     > > >     > fort he sake of easiness... could you do a short 
> test if it works, when you Replace the Content of PLC4XConsumer.java with the 
> following:
>     >     >     > > >     > 
>     >     >     > > >     > ```
>     >     >     > > >     > /*
>     >     >     > > >     >  Licensed to the Apache Software Foundation (ASF) 
> under one
>     >     >     > > >     >  or more contributor license agreements.  See the 
> NOTICE file
>     >     >     > > >     >  distributed with this work for additional 
> information
>     >     >     > > >     >  regarding copyright ownership.  The ASF licenses 
> this file
>     >     >     > > >     >  to you under the Apache License, Version 2.0 (the
>     >     >     > > >     >  "License"); you may not use this file except in 
> compliance
>     >     >     > > >     >  with the License.  You may obtain a copy of the 
> License at
>     >     >     > > >     > 
>     >     >     > > >     >    http://www.apache.org/licenses/LICENSE-2.0
>     >     >     > > >     > 
>     >     >     > > >     >  Unless required by applicable law or agreed to 
> in writing,
>     >     >     > > >     >  software distributed under the License is 
> distributed on an
>     >     >     > > >     >  "AS IS" BASIS, WITHOUT WARRANTIES OR CONDITIONS 
> OF ANY
>     >     >     > > >     >  KIND, either express or implied.  See the 
> License for the
>     >     >     > > >     >  specific language governing permissions and 
> limitations
>     >     >     > > >     >  under the License.
>     >     >     > > >     >  */
>     >     >     > > >     > package org.apache.plc4x.camel;
>     >     >     > > >     > 
>     >     >     > > >     > import org.apache.camel.*;
>     >     >     > > >     > import org.apache.camel.spi.ExceptionHandler;
>     >     >     > > >     > import 
> org.apache.camel.support.LoggingExceptionHandler;
>     >     >     > > >     > import org.apache.camel.support.ServiceSupport;
>     >     >     > > >     > import 
> org.apache.camel.util.AsyncProcessorConverterHelper;
>     >     >     > > >     > import org.apache.plc4x.java.api.PlcConnection;
>     >     >     > > >     > import 
> org.apache.plc4x.java.api.exceptions.PlcException;
>     >     >     > > >     > import 
> org.apache.plc4x.java.api.messages.PlcSubscriptionResponse;
>     >     >     > > >     > import 
> org.apache.plc4x.java.api.messages.PlcUnsubscriptionRequest;
>     >     >     > > >     > import 
> org.apache.plc4x.java.api.messages.PlcUnsubscriptionResponse;
>     >     >     > > >     > import org.slf4j.Logger;
>     >     >     > > >     > import org.slf4j.LoggerFactory;
>     >     >     > > >     > 
>     >     >     > > >     > import java.util.Collection;
>     >     >     > > >     > import java.util.concurrent.*;
>     >     >     > > >     > 
>     >     >     > > >     > public class Plc4XConsumer extends ServiceSupport 
> implements Consumer {
>     >     >     > > >     >     private static final Logger LOGGER = 
> LoggerFactory.getLogger(Plc4XConsumer.class);
>     >     >     > > >     > 
>     >     >     > > >     >     private Plc4XEndpoint endpoint;
>     >     >     > > >     >     private AsyncProcessor processor;
>     >     >     > > >     >     private ExceptionHandler exceptionHandler;
>     >     >     > > >     >     private PlcConnection plcConnection;
>     >     >     > > >     >     private String fieldQuery;
>     >     >     > > >     >     private Class<?> dataType;
>     >     >     > > >     >     private PlcSubscriptionResponse 
> subscriptionResponse;
>     >     >     > > >     > 
>     >     >     > > >     >     private ScheduledExecutorService 
> executorService = Executors.newSingleThreadScheduledExecutor();
>     >     >     > > >     >     private ScheduledFuture<?> future;
>     >     >     > > >     > 
>     >     >     > > >     >     public Plc4XConsumer(Plc4XEndpoint endpoint, 
> Processor processor) throws PlcException {
>     >     >     > > >     >         this.endpoint = endpoint;
>     >     >     > > >     >         this.dataType = endpoint.getDataType();
>     >     >     > > >     >         this.processor = 
> AsyncProcessorConverterHelper.convert(processor);
>     >     >     > > >     >         this.exceptionHandler = new 
> LoggingExceptionHandler(endpoint.getCamelContext(), getClass());
>     >     >     > > >     >         String plc4xURI = 
> endpoint.getEndpointUri().replaceFirst("plc4x:/?/?", "");
>     >     >     > > >     >         this.plcConnection = 
> endpoint.getPlcDriverManager().getConnection(plc4xURI);
>     >     >     > > >     >         this.fieldQuery = endpoint.getAddress();
>     >     >     > > >     >     }
>     >     >     > > >     > 
>     >     >     > > >     >     @Override
>     >     >     > > >     >     public String toString() {
>     >     >     > > >     >         return "Plc4XConsumer[" + endpoint + "]";
>     >     >     > > >     >     }
>     >     >     > > >     > 
>     >     >     > > >     >     @Override
>     >     >     > > >     >     public Endpoint getEndpoint() {
>     >     >     > > >     >         return endpoint;
>     >     >     > > >     >     }
>     >     >     > > >     > 
>     >     >     > > >     >     public ExceptionHandler getExceptionHandler() 
> {
>     >     >     > > >     >         return exceptionHandler;
>     >     >     > > >     >     }
>     >     >     > > >     > 
>     >     >     > > >     >     public void 
> setExceptionHandler(ExceptionHandler exceptionHandler) {
>     >     >     > > >     >         this.exceptionHandler = exceptionHandler;
>     >     >     > > >     >     }
>     >     >     > > >     > 
>     >     >     > > >     >     @Override
>     >     >     > > >     >     protected void doStart() throws 
> InterruptedException, ExecutionException {
>     >     >     > > >     >         // TODO: Is it correct to only support 
> one field?
>     >     >     > > >     >         future = executorService.schedule(() -> {
>     >     >     > > >     >             plcConnection.readRequestBuilder()
>     >     >     > > >     >                 .addItem("default", fieldQuery)
>     >     >     > > >     >                 .build()
>     >     >     > > >     >                 .execute()
>     >     >     > > >     >                 .thenAccept(response -> {
>     >     >     > > >     >                     LOGGER.debug("Received {}", 
> response);
>     >     >     > > >     >                     try {
>     >     >     > > >     >                         Exchange exchange = 
> endpoint.createExchange();
>     >     >     > > >     >                         
> exchange.getIn().setBody(unwrapIfSingle(response.getAllObjects("default")));
>     >     >     > > >     >                         
> processor.process(exchange);
>     >     >     > > >     >                     } catch (Exception e) {
>     >     >     > > >     >                         
> exceptionHandler.handleException(e);
>     >     >     > > >     >                     }
>     >     >     > > >     >                 });
>     >     >     > > >     >         }, 3, TimeUnit.SECONDS);
>     >     >     > > >     >     }
>     >     >     > > >     > 
>     >     >     > > >     >     @Override
>     >     >     > > >     >     protected void doStop() throws 
> InterruptedException, ExecutionException, TimeoutException {
>     >     >     > > >     >         // First stop the polling process
>     >     >     > > >     >         if (future != null) {
>     >     >     > > >     >             future.cancel(true);
>     >     >     > > >     >         }
>     >     >     > > >     >         // TODO: Handle the response ...
>     >     >     > > >     >         try {
>     >     >     > > >     >             plcConnection.close();
>     >     >     > > >     >         } catch (Exception e) {
>     >     >     > > >     >             LOGGER.error("Error closing 
> connection", e);
>     >     >     > > >     >         }
>     >     >     > > >     >     }
>     >     >     > > >     > 
>     >     >     > > >     >     private Object unwrapIfSingle(Collection 
> collection) {
>     >     >     > > >     >         if (collection.isEmpty()) {
>     >     >     > > >     >             return null;
>     >     >     > > >     >         }
>     >     >     > > >     >         if (collection.size() == 1) {
>     >     >     > > >     >             return collection.iterator().next();
>     >     >     > > >     >         }
>     >     >     > > >     >         return collection;
>     >     >     > > >     >     }
>     >     >     > > >     > 
>     >     >     > > >     > }
>     >     >     > > >     > ```
>     >     >     > > >     > 
>     >     >     > > >     > Julian
>     >     >     > > >     > 
>     >     >     > > >     > 
>     >     >     > > >     > Am 18.02.20, 13:22 schrieb "Julian Feinauer" 
> <[email protected]>:
>     >     >     > > >     > 
>     >     >     > > >     >     Hi Etienne,
>     >     >     > > >     >     
>     >     >     > > >     >     oh, sorry, indeed. The Code in the Camel 
> module is right, but does not work for Siemens S7.
>     >     >     > > >     >     Let me try to write you an updated version in 
> another branch ASAP then you can check it.
>     >     >     > > >     >     
>     >     >     > > >     >     Sorry!
>     >     >     > > >     >     Julian
>     >     >     > > >     >     
>     >     >     > > >     >     Am 18.02.20, 12:56 schrieb "Etienne Robinet" 
> <[email protected]>:
>     >     >     > > >     >     
>     >     >     > > >     >         I just cloned the rel/0.6 branch from 
> git, until now I didn't change anything.
>     >     >     > > >     >         Regards,,
>     >     >     > > >     >         Etienne
>     >     >     > > >     >         
>     >     >     > > >     >         On 2020/02/18 11:10:39, Julian Feinauer 
> <[email protected]> wrote: 
>     >     >     > > >     >         > Did you post your code somewhere? I 
> cant find it.. just post it somewhere and I will have a look!
>     >     >     > > >     >         > 
>     >     >     > > >     >         > Julian
>     >     >     > > >     >         > 
>     >     >     > > >     >         > Am 18.02.20, 11:28 schrieb "Etienne 
> Robinet" <[email protected]>:
>     >     >     > > >     >         > 
>     >     >     > > >     >         >     Hi Julian,
>     >     >     > > >     >         >     thanks for the advice, but where 
> should I change the code to apply your modification? Is it in the doStart() 
> methode of de PLC4XConsumer?
>     >     >     > > >     >         >     Regards,
>     >     >     > > >     >         >     
>     >     >     > > >     >         >     Etienne
>     >     >     > > >     >         >     
>     >     >     > > >     >         >     On 2020/02/18 08:55:22, Julian 
> Feinauer <[email protected]> wrote: 
>     >     >     > > >     >         >     > Hi Etienne,
>     >     >     > > >     >         >     > 
>     >     >     > > >     >         >     > thank you for your investigation.
>     >     >     > > >     >         >     > I just locked at your log and it 
> seems that connection works fine and some messages are exchanged BUT you try 
> to subscribe to a Value which is currently not supported.
>     >     >     > > >     >         >     > Try to just use the 
> "readRequestBuilder().addItem("", "").build().execute().get()" approach to 
> send a single request, that should work.
>     >     >     > > >     >         >     > 
>     >     >     > > >     >         >     > Best
>     >     >     > > >     >         >     > Julian
>     >     >     > > >     >         >     > 
>     >     >     > > >     >         >     > Am 18.02.20, 09:39 schrieb 
> "Etienne Robinet" <[email protected]>:
>     >     >     > > >     >         >     > 
>     >     >     > > >     >         >     >     Hello,
>     >     >     > > >     >         >     >     with the help of some 
> colleague we managed to find how to fix the issue so that the DriverManager 
> can find the actual s7 protocol.
>     >     >     > > >     >         >     >     All I had to do is to create 
> a maven project (karaf-blueprint) archetype and do as follow:
>     >     >     > > >     >         >     >     
>     >     >     > > >     >         >     >     1. Inside the pom, add the 
> S7PlcDriver under "imports"
>     >     >     > > >     >         >     >     2. create a service under 
> main/java/resources/META-INF/services/xxx.xxx.PlcDriver containing the 
> implementation (S7PlcDriver) and license
>     >     >     > > >     >         >     >     3. Create a simple XML 
> blueprint (with a real address this time connected to a real PLC)
>     >     >     > > >     >         >     >     <blueprint 
> xmlns="http://www.osgi.org/xmlns/blueprint/v1.0.0"; default-activation="lazy">
>     >     >     > > >     >         >     >     
>     >     >     > > >     >         >     >         <camelContext 
> id="PLC-Context" xmlns="http://camel.apache.org/schema/blueprint"; 
> streamCache="true">
>     >     >     > > >     >         >     >     
>     >     >     > > >     >         >     >     
>     >     >     > > >     >         >     >             <route id="Route1">
>     >     >     > > >     >         >     >     
>     >     >     > > >     >         >     >                 <from 
> uri="plc4x:s7://192.168.178.10/1/1"/>
>     >     >     > > >     >         >     >                 <log message=" 
> Sending ${body}" loggingLevel="INFO" />
>     >     >     > > >     >         >     >                 <to 
> uri="mock:test?retainLast=10" />
>     >     >     > > >     >         >     >     
>     >     >     > > >     >         >     >             </route>
>     >     >     > > >     >         >     >     
>     >     >     > > >     >         >     >         </camelContext>
>     >     >     > > >     >         >     >     
>     >     >     > > >     >         >     >     </blueprint>
>     >     >     > > >     >         >     >     
>     >     >     > > >     >         >     >     So now I have the next issue, 
> I can see from the log that a connection is established but it tells me that 
> the connection doesn't support connection. Am I missing a parameter or what 
> could be the issue?
>     >     >     > > >     >         >     >     
>     >     >     > > >     >         >     >     Here the log:
>     >     >     > > >     >         >     >     
>     >     >     > > >     >         >     >     
> https://i.imgur.com/KgWz8DF.png
>     >     >     > > >     >         >     >     
>     >     >     > > >     >         >     >     On 2020/02/17 12:11:56, 
> Christofer Dutz <[email protected]> wrote: 
>     >     >     > > >     >         >     >     > Hi all,
>     >     >     > > >     >         >     >     > 
>     >     >     > > >     >         >     >     > having a more detailed look 
> at the log-trace, it seems the DriverManager isn't able to find the S7 driver 
> at all ...
>     >     >     > > >     >         >     >     > But I guess if it even was 
> available, as Cesar pointed out, the field address is that of the mock driver 
> and not of the S7 so this will not work.
>     >     >     > > >     >         >     >     > Also are you connecting to 
> localhost, which is also probably not what you want. Unless you are running a 
> S7 simulator on your machine.
>     >     >     > > >     >         >     >     > 
>     >     >     > > >     >         >     >     > Depending of if you're 
> using a released version of the s7 driver the connection URL is correct, 
> however if you switch to the new S7 driver it would look like this:  s7://{ip 
> or host}
>     >     >     > > >     >         >     >     > Not the "/1/1" are now 
> missing.
>     >     >     > > >     >         >     >     > 
>     >     >     > > >     >         >     >     > Chris
>     >     >     > > >     >         >     >     > 
>     >     >     > > >     >         >     >     > 
>     >     >     > > >     >         >     >     > 
>     >     >     > > >     >         >     >     > 
>     >     >     > > >     >         >     >     > Am 17.02.20, 13:04 schrieb 
> "Cesar Garcia" <[email protected]>:
>     >     >     > > >     >         >     >     > 
>     >     >     > > >     >         >     >     >     Hi,
>     >     >     > > >     >         >     >     >     
>     >     >     > > >     >         >     >     >     The PLC address does 
> not look correct, can you confirm that it really
>     >     >     > > >     >         >     >     >     points to a real PLC or 
> an S7 simulator?
>     >     >     > > >     >         >     >     >     
>     >     >     > > >     >         >     >     >     <from 
> uri="plc4x:s7:localhost/1/1"/>
>     >     >     > > >     >         >     >     >     
>     >     >     > > >     >         >     >     >     Best regards,
>     >     >     > > >     >         >     >     >     
>     >     >     > > >     >         >     >     >     
>     >     >     > > >     >         >     >     >     El vie., 14 feb. 2020 a 
> las 18:34, Etienne Robinet (<[email protected]>)
>     >     >     > > >     >         >     >     >     escribió:
>     >     >     > > >     >         >     >     >     
>     >     >     > > >     >         >     >     >     > Hello everyone,
>     >     >     > > >     >         >     >     >     > I've spent some days 
> trying to figure out how to make PLC4X work inside a
>     >     >     > > >     >         >     >     >     > karaf container in 
> combination with camel blueprints for routing.
>     >     >     > > >     >         >     >     >     > I've downloaded the 
> latest release (0.5.0) and built it with maven. I then
>     >     >     > > >     >         >     >     >     > installed the 
> driver-s7-feature and plc4j-apache-camel bundle into my
>     >     >     > > >     >         >     >     >     > container and got 
> following bundles running:
>     >     >     > > >     >         >     >     >     >
>     >     >     > > >     >         >     >     >     > >PLC4J: API
>     >     >     > > >     >         >     >     >     > >PLC4J: Driver: S7
>     >     >     > > >     >         >     >     >     > >PLC4J: Protocol: 
> Driver-Base: Base
>     >     >     > > >     >         >     >     >     > >PLC4J: Protocol: 
> Driver-Base: TCP
>     >     >     > > >     >         >     >     >     > >PLC4J: Protocol: ISO 
> on TCP
>     >     >     > > >     >         >     >     >     > >PLC4J: Protocol: ISO 
> TP
>     >     >     > > >     >         >     >     >     > >PLC4J: Protocol: S7
>     >     >     > > >     >         >     >     >     > >PLC4j: Utils: Driver 
> Base: Java
>     >     >     > > >     >         >     >     >     > >PLC4J: Integrations: 
> Apache Camel
>     >     >     > > >     >         >     >     >     >
>     >     >     > > >     >         >     >     >     > After trying a simple 
> route with this consumer component:
>     >     >     > > >     >         >     >     >     > <from 
> uri="plc4x:s7:localhost/1/1"/> (the address is for testing purpose)
>     >     >     > > >     >         >     >     >     > I get the following 
> error:
>     >     >     > > >     >         >     >     >     > Error occurred during 
> starting CamelContext: PLC-Context
>     >     >     > > >     >         >     >     >     > 
> org.apache.camel.FailedToCreateRouteException: Failed to create route
>     >     >     > > >     >         >     >     >     > Route1: 
> Route(Route1)[[From[plc4x:s7:localhost/1/1]] -> [To[mock:tes...
>     >     >     > > >     >         >     >     >     > because of Unable to 
> find driver for protocol 's7'
>     >     >     > > >     >         >     >     >     >
>     >     >     > > >     >         >     >     >     > I've tested numerous 
> version of PLC4X and got the same results, so I think
>     >     >     > > >     >         >     >     >     > I might be close to 
> fix it!
>     >     >     > > >     >         >     >     >     > Any help would be 
> appreciated!
>     >     >     > > >     >         >     >     >     >
>     >     >     > > >     >         >     >     >     > Here the full log
>     >     >     > > >     >         >     >     >     >
>     >     >     > > >     >         >     >     >     > 16:30:45.578 INFO 
> [Blueprint Event Dispatcher: 1] Attempting to start
>     >     >     > > >     >         >     >     >     > CamelContext: 
> PLC-Context
>     >     >     > > >     >         >     >     >     > 16:30:45.579 INFO 
> [Blueprint Event Dispatcher: 1] Apache Camel 2.24.2
>     >     >     > > >     >         >     >     >     > (CamelContext: 
> PLC-Context) is starting
>     >     >     > > >     >         >     >     >     > 16:30:45.580 INFO 
> [Blueprint Event Dispatcher: 1] StreamCaching is enabled
>     >     >     > > >     >         >     >     >     > on CamelContext: 
> PLC-Context
>     >     >     > > >     >         >     >     >     > 16:30:45.580 INFO 
> [Blueprint Event Dispatcher: 1] JMX is enabled
>     >     >     > > >     >         >     >     >     > 16:30:45.600 INFO 
> [Blueprint Event Dispatcher: 1] Instantiating new PLC
>     >     >     > > >     >         >     >     >     > Driver Manager with 
> class loader
>     >     >     > > >     >         >     >     >     > 
> BundleDelegatingClassLoader(plc4j-route.xml [67])
>     >     >     > > >     >         >     >     >     > 16:30:45.600 INFO 
> [Blueprint Event Dispatcher: 1] Registering available
>     >     >     > > >     >         >     >     >     > drivers...
>     >     >     > > >     >         >     >     >     > 16:30:45.601 TRACE 
> [Blueprint Event Dispatcher: 1] FindResource:
>     >     >     > > >     >         >     >     >     > 
> META-INF/services/org.apache.plc4x.java.spi.PlcDriver
>     >     >     > > >     >         >     >     >     > 16:30:45.627 INFO 
> [Blueprint Event Dispatcher: 1] StreamCaching in use
>     >     >     > > >     >         >     >     >     > with spool directory:
>     >     >     > > >     >         >     >     >     > 
> C:\karaf\bin\..\data\tmp\camel\camel-tmp-00f849ac-0ccf-4b12-822d-dda62267eb6c
>     >     >     > > >     >         >     >     >     > and rules: [Spool > 
> 128K body size]
>     >     >     > > >     >         >     >     >     > 16:30:45.629 INFO 
> [Blueprint Event Dispatcher: 1] Apache Camel 2.24.2
>     >     >     > > >     >         >     >     >     > (CamelContext: 
> PLC-Context) is shutting down
>     >     >     > > >     >         >     >     >     > 16:30:45.639 INFO 
> [Blueprint Event Dispatcher: 1] Apache Camel 2.24.2
>     >     >     > > >     >         >     >     >     > (CamelContext: 
> PLC-Context) uptime 0.060 seconds
>     >     >     > > >     >         >     >     >     > 16:30:45.640 INFO 
> [Blueprint Event Dispatcher: 1] Apache Camel 2.24.2
>     >     >     > > >     >         >     >     >     > (CamelContext: 
> PLC-Context) is shutdown in 0.011 seconds
>     >     >     > > >     >         >     >     >     > 16:30:45.640 WARN 
> [Blueprint Event Dispatcher: 1] Changing Camel state for
>     >     >     > > >     >         >     >     >     > bundle 67 to Failure
>     >     >     > > >     >         >     >     >     > 16:30:45.641 ERROR 
> [Blueprint Event Dispatcher: 1] Error occurred during
>     >     >     > > >     >         >     >     >     > starting 
> CamelContext: PLC-Context
>     >     >     > > >     >         >     >     >     > 
> org.apache.camel.FailedToCreateRouteException: Failed to create route
>     >     >     > > >     >         >     >     >     > Route1: 
> Route(Route1)[[From[plc4x:s7:localhost/1/1]] -> [To[mock:tes...
>     >     >     > > >     >         >     >     >     > because of Unable to 
> find driver for protocol 's7'
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> org.apache.camel.impl.RouteService.warmUp(RouteService.java:147)
>     >     >     > > >     >         >     >     >     > ~[!/:2.24.2]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> org.apache.camel.impl.DefaultCamelContext.doWarmUpRoutes(DefaultCamelContext.java:3954)
>     >     >     > > >     >         >     >     >     > ~[!/:2.24.2]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> org.apache.camel.impl.DefaultCamelContext.safelyStartRouteServices(DefaultCamelContext.java:3861)
>     >     >     > > >     >         >     >     >     > ~[!/:2.24.2]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> org.apache.camel.impl.DefaultCamelContext.doStartOrResumeRoutes(DefaultCamelContext.java:3647)
>     >     >     > > >     >         >     >     >     > ~[!/:2.24.2]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> org.apache.camel.impl.DefaultCamelContext.doStartCamel(DefaultCamelContext.java:3488)
>     >     >     > > >     >         >     >     >     > ~[!/:2.24.2]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> org.apache.camel.impl.DefaultCamelContext$4.call(DefaultCamelContext.java:3247)
>     >     >     > > >     >         >     >     >     > ~[!/:2.24.2]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> org.apache.camel.impl.DefaultCamelContext$4.call(DefaultCamelContext.java:3243)
>     >     >     > > >     >         >     >     >     > ~[!/:2.24.2]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> org.apache.camel.impl.DefaultCamelContext.doWithDefinedClassLoader(DefaultCamelContext.java:3266)
>     >     >     > > >     >         >     >     >     > ~[!/:2.24.2]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> org.apache.camel.impl.DefaultCamelContext.doStart(DefaultCamelContext.java:3243)
>     >     >     > > >     >         >     >     >     > ~[!/:2.24.2]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> org.apache.camel.support.ServiceSupport.start(ServiceSupport.java:72)
>     >     >     > > >     >         >     >     >     > ~[!/:2.24.2]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> org.apache.camel.impl.DefaultCamelContext.start(DefaultCamelContext.java:3159)
>     >     >     > > >     >         >     >     >     > ~[!/:2.24.2]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> org.apache.camel.blueprint.BlueprintCamelContext.start(BlueprintCamelContext.java:255)
>     >     >     > > >     >         >     >     >     > ~[!/:2.24.2]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> org.apache.camel.blueprint.BlueprintCamelContext.maybeStart(BlueprintCamelContext.java:297)
>     >     >     > > >     >         >     >     >     > ~[!/:2.24.2]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> org.apache.camel.blueprint.BlueprintCamelContext.blueprintEvent(BlueprintCamelContext.java:188)
>     >     >     > > >     >         >     >     >     > [!/:2.24.2]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> org.apache.aries.blueprint.container.BlueprintEventDispatcher$3.call(BlueprintEventDispatcher.java:190)
>     >     >     > > >     >         >     >     >     > [!/:1.10.2]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> org.apache.aries.blueprint.container.BlueprintEventDispatcher$3.call(BlueprintEventDispatcher.java:188)
>     >     >     > > >     >         >     >     >     > [!/:1.10.2]
>     >     >     > > >     >         >     >     >     >         at 
> java.util.concurrent.FutureTask.run(FutureTask.java:264) [?:?]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> java.util.concurrent.Executors$RunnableAdapter.call(Executors.java:515)
>     >     >     > > >     >         >     >     >     > [?:?]
>     >     >     > > >     >         >     >     >     >         at 
> java.util.concurrent.FutureTask.run(FutureTask.java:264) [?:?]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> java.util.concurrent.Executors$RunnableAdapter.call(Executors.java:515)
>     >     >     > > >     >         >     >     >     > [?:?]
>     >     >     > > >     >         >     >     >     >         at 
> java.util.concurrent.FutureTask.run(FutureTask.java:264) [?:?]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> java.util.concurrent.ScheduledThreadPoolExecutor$ScheduledFutureTask.run(ScheduledThreadPoolExecutor.java:304)
>     >     >     > > >     >         >     >     >     > [?:?]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> java.util.concurrent.ThreadPoolExecutor.runWorker(ThreadPoolExecutor.java:1128)
>     >     >     > > >     >         >     >     >     > [?:?]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> java.util.concurrent.ThreadPoolExecutor$Worker.run(ThreadPoolExecutor.java:628)
>     >     >     > > >     >         >     >     >     > [?:?]
>     >     >     > > >     >         >     >     >     >         at 
> java.lang.Thread.run(Thread.java:834) [?:?]
>     >     >     > > >     >         >     >     >     > Caused by: 
> org.apache.plc4x.java.api.exceptions.PlcConnectionException:
>     >     >     > > >     >         >     >     >     > Unable to find driver 
> for protocol 's7'
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> org.apache.plc4x.java.PlcDriverManager.getDriver(PlcDriverManager.java:98)
>     >     >     > > >     >         >     >     >     > ~[?:?]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> org.apache.plc4x.java.PlcDriverManager.getConnection(PlcDriverManager.java:71)
>     >     >     > > >     >         >     >     >     > ~[?:?]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> org.apache.plc4x.camel.Plc4XConsumer.<init>(Plc4XConsumer.java:57) ~[?:?]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> org.apache.plc4x.camel.Plc4XEndpoint.createConsumer(Plc4XEndpoint.java:72)
>     >     >     > > >     >         >     >     >     > ~[?:?]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> org.apache.camel.impl.EventDrivenConsumerRoute.addServices(EventDrivenConsumerRoute.java:69)
>     >     >     > > >     >         >     >     >     > ~[!/:2.24.2]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> org.apache.camel.impl.DefaultRoute.onStartingServices(DefaultRoute.java:107)
>     >     >     > > >     >         >     >     >     > ~[!/:2.24.2]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> org.apache.camel.impl.RouteService.doWarmUp(RouteService.java:172)
>     >     >     > > >     >         >     >     >     > ~[!/:2.24.2]
>     >     >     > > >     >         >     >     >     >         at
>     >     >     > > >     >         >     >     >     > 
> org.apache.camel.impl.RouteService.warmUp(RouteService.java:145)
>     >     >     > > >     >         >     >     >     > ~[!/:2.24.2]
>     >     >     > > >     >         >     >     >     >         ... 24 more
>     >     >     > > >     >         >     >     >     >
>     >     >     > > >     >         >     >     >     >
>     >     >     > > >     >         >     >     >     >
>     >     >     > > >     >         >     >     >     
>     >     >     > > >     >         >     >     >     -- 
>     >     >     > > >     >         >     >     >     *CEOS Automatización, 
> C.A.*
>     >     >     > > >     >         >     >     >     *GALPON SERVICIO 
> INDUSTRIALES Y NAVALES FA, C.A.,*
>     >     >     > > >     >         >     >     >     *PISO 1, OFICINA 2, AV. 
> RAUL LEONI, SECTOR GUAMACHITO,*
>     >     >     > > >     >         >     >     >     
>     >     >     > > >     >         >     >     >     *FRENTE A LA ASOCIACION 
> DE GANADEROS,BARCELONA,EDO. ANZOATEGUI*
>     >     >     > > >     >         >     >     >     *Ing. César García*
>     >     >     > > >     >         >     >     >     *Cel: 0416-681.03.99*
>     >     >     > > >     >         >     >     >     
>     >     >     > > >     >         >     >     >     *Cel: 0414-760.98.95*
>     >     >     > > >     >         >     >     >     
>     >     >     > > >     >         >     >     >     *Hotline Técnica 
> SIEMENS: 0800 1005080*
>     >     >     > > >     >         >     >     >     
>     >     >     > > >     >         >     >     >     *Email: 
> [email protected]
>     >     >     > > >     >         >     >     >     
> <[email protected]>*
>     >     >     > > >     >         >     >     >     
>     >     >     > > >     >         >     >     > 
>     >     >     > > >     >         >     >     > 
>     >     >     > > >     >         >     >     
>     >     >     > > >     >         >     > 
>     >     >     > > >     >         >     > 
>     >     >     > > >     >         >     
>     >     >     > > >     >         > 
>     >     >     > > >     >         > 
>     >     >     > > >     >         
>     >     >     > > >     >     
>     >     >     > > >     >     
>     >     >     > > >     > 
>     >     >     > > >     > 
>     >     >     > > >     
>     >     >     > > > 
>     >     >     > > > 
>     >     >     > > 
>     >     >     > 
>     >     >     
>     >     > 
>     >     > 
>     >     
>     > 
>     > 
>     
> 
> 

Reply via email to