so I just added a packet-size-estimator for AB-ETH ... hope that helps a little 
more.

Chris



Am 07.03.20, 12:23 schrieb "Christofer Dutz" <[email protected]>:

    Hi Etienne,
    
    well I just had a look at the driver ... it seems it's just not finished 
yet.
    The reason it doesn't parse the response is that it doesn't know how big it 
is ... I will try to implement a packetSizeEstimator for this, but it would 
really be great if someone who knows this protocol (Has some sort of 
specification as well as a device to test it on) could work on this.
    
    I'll try to guess what it could be .. but no idea if this gets you much 
further.
    
    We really should only put stuff outside the sandbox, if there's at least 
one person willing and able to maintain it ...
    
    Chris
    
    
    Am 06.03.20, 17:16 schrieb "Robinet, Etienne" <[email protected]>:
    
        Well from what I've seen, PLC4x is calling right the session register 
but
        can't handle the positive response (using AB-ETH)
        Using 0.6 EIP protocol, the Session is properly opened, but impossible 
to
        rightly access data as there is no way to mention which slot the plc is 
and
        the tag (from what I understood)
        
        Etienne
        
        Le ven. 6 mars 2020 à 17:03, Otto Fowler <[email protected]> a 
écrit :
        
        > I’ve used that to test session, list identities and get all attributes
        > calls from my code to cpppo.
        >
        > If you look at the documentation and the samples you can get cpppo 
talking
        > to cpppo and then see how the plc4x stuff compares doing the same 
tasks
        > maybe
        >
        >
        >
        >
        > On March 6, 2020 at 10:49:27, Robinet, Etienne ([email protected]) 
wrote:
        >
        > What could I test with this library exactly?
        >
        > I managed to establish a Session registration at ENIP level, but 
seems like
        > the app can not decode the answer (which has Success code 0 as 
expected).
        > Here is where it's stuck: https://i.imgur.com/ZDrSVTA.png
        >
        > The packetSize= -1 because the packageSizeEstimator is null (why?)
        >
        > Etienne
        >
        > Le ven. 6 mars 2020 à 15:53, Otto Fowler <[email protected]> a 
écrit
        > :
        >
        > > I would recommend using https://github.com/pjkundert/cpppo to test 
this
        > > stuff to some extent.
        > >
        > > Using the docker container works well too.
        > >
        > >
        > >
        > >
        > > On March 6, 2020 at 09:04:11, Christofer Dutz 
([email protected]
        > )
        > > wrote:
        > >
        > > Hi Robert,
        > >
        > > unfortunately I wasn't able to test the ported driver before as I 
don't
        > > have access to an Allen Bradley device.
        > > I do however recall that I brought up that the protocol looked 
familiar
        > to
        > > the EtherNet/IP protocol, however seems to have differences.
        > > So you should treat wireshark decodings with care.
        > >
        > > Regarding the error itself, this should use the TCP transport which 
uses
        > > the NioSocketChannel which should work with the NioEventLoop,
        > > so this error is strange. But it seems to have disappeared as you 
managed
        > > to get passed this issue.
        > >
        > > It now seems that the problems are related to an invalid request 
being
        > sent
        > > or a configuration error on the PLC (Don't know the AB-ETH protocol
        > > really).
        > >
        > > Perhaps Volker can help here. However from a look at the mspec for 
that
        > > protocol, I would assume it's only partially implemented, so 
perhaps you
        > > are unimplemented parts of this protocol.
        > >
        > > Chris
        > >
        > >
        > >
        > > Am 06.03.20, 13:00 schrieb "Robinet, Etienne" <[email protected]>:
        > >
        > > Hi,
        > > After some tweaking I managed to create a right "Register Session"
        > message
        > > (
        > > https://i.imgur.com/OR9RDdd.png), but I got an error response from 
the
        > PLC
        > > (
        > > https://i.imgur.com/2Zm1op3.png).
        > > Do you know what the Request should be?
        > >
        > > Etienne
        > >
        > > Le ven. 6 mars 2020 à 10:47, Julian Feinauer <
        > [email protected]
        > > >
        > > a écrit :
        > >
        > > > Hi,
        > > >
        > > > you already help with your bug reports and the feedback you give!
        > > >
        > > > Julian
        > > >
        > > > Am 06.03.20, 10:45 schrieb "Robinet, Etienne" <[email protected]>:
        > > >
        > > > Hi Julian,
        > > > thanks for the fast response. I would be really glad if I could 
help a
        > > > bit
        > > > on that, as far as I can.
        > > >
        > > > Etienne
        > > >
        > > > Le ven. 6 mars 2020 à 10:43, Julian Feinauer <
        > > > [email protected]>
        > > > a écrit :
        > > >
        > > > > Hi Etienne,
        > > > >
        > > > > sorry that you have that much issues. Perhaps @Volker Emmert can
        > > > comment
        > > > > on that as he implemented the driver together with @Christofer 
Dutz.
        > > > >
        > > > > Julian
        > > > >
        > > > > Am 06.03.20, 10:37 schrieb "Etienne Robinet" 
<[email protected]>:
        > > > >
        > > > > Really sorry for double-post, but I managed to establish a
        > > > connection
        > > > > by changing the port from 2222 to 44818 (
        > > > >
        > > >
        > >
        > >
        >
        > 
https://literature.rockwellautomation.com/idc/groups/literature/documents/qr/comm-qr001_-en-e.pdf
        > > > > )
        > > > >
        > > > > I also change the url to : ab-eth:tcp://163.243.183.250
        > > > > And this is where the application freezes now:
        > > > >
        > > > > ab-eth:tcp://163.243.183.250
        > > > > 10:34:49.867 [main] TRACE o.a.p.j.s.c.DefaultNettyPlcConnection 
-
        > > > > Channel was created, firing ChannelCreated Event
        > > > > 10:34:49.875 [nioEventLoopGroup-2-1] DEBUG
        > > > > o.a.p.j.a.p.AbEthProtocolLogic - Sending COTP Connection Request
        > > > > 10:34:49.909 [nioEventLoopGroup-2-1] TRACE
        > > > > o.a.plc4x.java.spi.Plc4xNettyWrapper - Adding Response Handler 
...
        > > > > 10:34:49.909 [nioEventLoopGroup-2-1] TRACE
        > > > > o.a.plc4x.java.spi.Plc4xNettyWrapper - Sending to wire
        > > > >
        > > >
        > >
        > >
        >
        > 
CIPEncapsulationConnectionRequest[sessionHandle=0,status=0,senderContext={0,0,0,0,0,0,0,0},options=0]
        >
        > >
        > > > > 10:34:49.920 [nioEventLoopGroup-2-1] DEBUG
        > > > > o.a.plc4x.java.spi.Plc4xNettyWrapper - Forwarding request to plc
        > > > >
        > > >
        > >
        > >
        >
        > 
CIPEncapsulationConnectionRequest[sessionHandle=0,status=0,senderContext={0,0,0,0,0,0,0,0},options=0]
        >
        > >
        > > > > 10:34:49.926 [nioEventLoopGroup-2-1] DEBUG
        > > > io.netty.util.Recycler -
        > > > > -Dio.netty.recycler.maxCapacityPerThread: 4096
        > > > > 10:34:49.926 [nioEventLoopGroup-2-1] DEBUG
        > > > io.netty.util.Recycler -
        > > > > -Dio.netty.recycler.maxSharedCapacityFactor: 2
        > > > > 10:34:49.926 [nioEventLoopGroup-2-1] DEBUG
        > > > io.netty.util.Recycler -
        > > > > -Dio.netty.recycler.linkCapacity: 16
        > > > > 10:34:49.926 [nioEventLoopGroup-2-1] DEBUG
        > > > io.netty.util.Recycler -
        > > > > -Dio.netty.recycler.ratio: 8
        > > > > 10:34:49.935 [nioEventLoopGroup-2-1] DEBUG
        > > > > io.netty.buffer.AbstractByteBuf - 
-Dio.netty.buffer.checkAccessible:
        > > > true
        > > > > 10:34:49.935 [nioEventLoopGroup-2-1] DEBUG
        > > > > io.netty.buffer.AbstractByteBuf - 
-Dio.netty.buffer.checkBounds: true
        > > > > 10:34:49.935 [nioEventLoopGroup-2-1] DEBUG
        > > > > i.n.util.ResourceLeakDetectorFactory - Loaded default
        > > > ResourceLeakDetector:
        > > > > io.netty.util.ResourceLeakDetector@385a14ab
        > > > > 10:34:49.966 [nioEventLoopGroup-2-1] DEBUG
        > > > > o.a.p.j.s.GeneratedDriverByteToMessageCodec - Sending bytes to 
PLC
        > > > for
        > > > > message
        > > > >
        > > >
        > >
        > >
        >
        > 
CIPEncapsulationConnectionRequest[sessionHandle=0,status=0,senderContext={0,0,0,0,0,0,0,0},options=0]
        >
        > >
        > > > > as data 01010000000000000000000000000000000000000000000000000000
        > > > > 10:34:49.972 [nioEventLoopGroup-2-1] TRACE
        > > > > o.a.p.j.s.GeneratedDriverByteToMessageCodec - Receiving bytes,
        > > > trying to
        > > > > decode Message...
        > > > >
        > > > > BR,
        > > > >
        > > > > Etienne
        > > > >
        > > > > On 2020/03/06 09:30:22, Etienne Robinet <[email protected]>
        > > > wrote:
        > > > > > Hi all,
        > > > > > I wanted to ask how far we are on the AB-ETH driver? I have a
        > > > > LOGIXS5580 Series PLC to test, and when I try to run the 
HelloWorld
        > > > example
        > > > > I get following error:
        > > > > >
        > > > > > 10:24:44.771 [nioEventLoopGroup-2-1] INFO
        > > > > o.a.p.j.s.c.NettyChannelFactory - Unable to connect, shutting 
down
        > > > worker
        > > > > thread.
        > > > > > org.apache.plc4x.java.api.exceptions.PlcConnectionException:
        > > > Error
        > > > > creating channel.
        > > > > > at
        > > > >
        > > >
        > >
        > >
        >
        > 
org.apache.plc4x.java.spi.connection.NettyChannelFactory.createChannel(NettyChannelFactory.java:115)
        >
        > >
        > > > > > at
        > > > >
        > > >
        > >
        > >
        >
        > 
org.apache.plc4x.java.spi.connection.DefaultNettyPlcConnection.connect(DefaultNettyPlcConnection.java:89)
        >
        > >
        > > > > > at
        > > > >
        > > >
        > >
        > >
        >
        > 
org.apache.plc4x.java.PlcDriverManager.getConnection(PlcDriverManager.java:74)
        >
        > >
        > > > > > at
        > > > >
        > > >
        > >
        > >
        >
        > 
org.apache.plc4x.java.examples.helloplc4x.HelloPlc4x.main(HelloPlc4x.java:45)
        >
        > >
        > > > > > Caused by: java.lang.IllegalStateException: incompatible event
        > > > loop
        > > > > type: io.netty.channel.nio.NioEventLoop
        > > > > > at
        > > > >
        > > >
        > >
        > >
        >
        > 
io.netty.channel.AbstractChannel$AbstractUnsafe.register(AbstractChannel.java:462)
        >
        > >
        > > > > > at
        > > > >
        > > >
        > >
        > >
        >
        > 
io.netty.channel.SingleThreadEventLoop.register(SingleThreadEventLoop.java:87)
        >
        > >
        > > > > > at
        > > > >
        > > >
        > >
        > >
        >
        > 
io.netty.channel.SingleThreadEventLoop.register(SingleThreadEventLoop.java:81)
        >
        > >
        > > > > > at
        > > > >
        > > >
        > >
        > >
        >
        > 
io.netty.channel.MultithreadEventLoopGroup.register(MultithreadEventLoopGroup.java:86)
        >
        > >
        > > > > > at
        > > > >
        > > >
        > >
        > >
        >
        > 
io.netty.bootstrap.AbstractBootstrap.initAndRegister(AbstractBootstrap.java:322)
        >
        > >
        > > > > > at
        > > > > 
io.netty.bootstrap.Bootstrap.doResolveAndConnect(Bootstrap.java:159)
        > > > > > at io.netty.bootstrap.Bootstrap.connect(Bootstrap.java:143)
        > > > > > at
        > > > >
        > > >
        > >
        > >
        >
        > 
org.apache.plc4x.java.spi.connection.NettyChannelFactory.createChannel(NettyChannelFactory.java:99)
        >
        > >
        > > > > > ... 3 more
        > > > > >
        > > > > > Any ideas on where this comes from? In Studio5000 the PLC is
        > > > on the
        > > > > slot 4 and I am connected to a swtich on IP: 163.243.183.250 and
        > > > here's the
        > > > > plc4x uri: "ab-eth://163.243.183.250/".
        > > > > >
        > > > > > BR,
        > > > > >
        > > > > > Etienne
        > > > > >
        > > > >
        > > > >
        > > > >
        > > >
        > > >
        > > >
        > >
        >
        
    
    