Christofer Dutz created PLC4X-208:
-------------------------------------

             Summary: [S7] When trying to write to a S7 device and writing is 
not explicitly enabled, the PLC will respond with an error code
                 Key: PLC4X-208
                 URL: https://issues.apache.org/jira/browse/PLC4X-208
             Project: Apache PLC4X
          Issue Type: Task
          Components: Driver-S7
    Affects Versions: 0.8.0
            Reporter: Christofer Dutz
            Assignee: Christofer Dutz


The S7 will respond with:
 * Error Class: 0x83
 * Error Code: 0x04 

if the user tries a write request and this is not explicitly enabled, we can 
definitely handle this in a nicer way.

To fix the problem, you need to select the PLC in TIA, go into the Properties 
dialog, select "Protection". You will probably notice there's an Access Level 
Table, but you need to scroll down (even if it looks as if there is nothing). 
There check the box in: "Permit access with PUT/GET communications from remote 
partner...."

Would be cool if we could give our users a hint on this.



--