Hi Patrick,

so was the problem actually a VisualStudio problem or something we can improve?

If you say: „PLC program only in the PLC itself“ … you’re not running the PLC4X 
program on a PLC? So you mean if you run the program from the commandline, it 
works and in VS it hangs?


Chris


Von: Patrick Boisclair <[email protected]>
Gesendet: Donnerstag, 17. Dezember 2020 17:23
An: [email protected]
Betreff: RE: Beckhoff with ADS protocol (0.0.8-SNAPSHOT)


Ok I found out what the problem is.



For a reason when the PLC program is running from Visual Studio (TwinCAT), for 
a reason with PLC4X it sometimes hangs.

If I shut down Visual Studio and run the PLC program only in the PLC itself.. 
works fine.






Patrick Boisclair
Analyste - Programmeur senior / Senior Analyst Programmer

[cid:[email protected]]<https://www.noovelia.com/>


462, rue des Forges, Trois-Rivières (Québec) G9A 2H5 CANADA
noovelia.com<https://www.noovelia.com>

[cid:[email protected]]
________________________________
De : Patrick Boisclair <[email protected]<mailto:[email protected]>>
Envoyé : 17 décembre 2020 09:59
À : [email protected]<mailto:[email protected]>
Objet : RE: Beckhoff with ADS protocol (0.0.8-SNAPSHOT)


Hi Chris,



I'll try to see what I can find with wireshark and send the info on the Jira 
issue.




Patrick Boisclair
Analyste - Programmeur senior / Senior Analyst Programmer

[cid:[email protected]]<https://www.noovelia.com/>


462, rue des Forges, Trois-Rivières (Québec) G9A 2H5 CANADA
noovelia.com<https://www.noovelia.com>

[cid:[email protected]]
________________________________
De : Christofer Dutz 
<[email protected]<mailto:[email protected]>>
Envoyé : 17 décembre 2020 09:45
À : [email protected]<mailto:[email protected]>
Objet : AW: Beckhoff with ADS protocol (0.0.8-SNAPSHOT)

Hi Patrick,

welcome to our list.

There is one big difference (if you are calling the code you posted in a loop):
Internally the driver automatically does the translation from a symbolic 
address to a handle and to use that handle to read and to give back the handle 
when closing the connection.

Perhaps if you run your loop just around this part:

request.execute().whenComplete((response, exception) -> {

                        Integer x = response.getInteger("value-1");

                        System.out.println("READ DONE: " + x.toString());

                    });


Then it would be a similar scenario.

If this isn’t solving the problem, could you possibly do a WireShark recording 
oft hat communication and attach that to a Jira issue on: 
https://issues.apache.org/jira/projects/PLC4X/
This would be the best way to help us find and possibly resolve the issue.


Hope that helps,

     Chris


Von: Patrick Boisclair <[email protected]<mailto:[email protected]>>
Gesendet: Donnerstag, 17. Dezember 2020 15:34
An: [email protected]<mailto:[email protected]>
Betreff: Beckhoff with ADS protocol (0.0.8-SNAPSHOT)


Hello everyone,



Im' able to connect to my beckhoff PLC, read a value, but sometimes the read 
just "hang". The code below works like half the time.

Some time, I run the program, it reads the value, sometimes it just hang on the 
"execute".



I dont know what Im doing wrong.

 PlcDriverManager driver = new PlcDriverManager();

        try {

            //

            PlcConnection connection = driver.getConnection(

                    
"ads:tcp://10.10.11.77?sourceAmsNetId=172.29.48.1.1.1&sourceAmsPort=36&targetAmsNetId=5.62.206.200.1.1&targetAmsPort=851");





            if (connection.isConnected()) {

                if (connection.getMetadata().canRead()) {

                    PlcReadRequest.Builder builder = 
connection.readRequestBuilder();

                    builder.addItem("value-1", "MAIN.Rand_1:DINT");



                    PlcReadRequest request = builder.build();



                    request.execute().whenComplete((response, exception) -> {

                        Integer x = response.getInteger("value-1");

                        System.out.println("READ DONE: " + x.toString());

                    });



                }

            }

        } catch (Exception e) {

            e.printStackTrace();

        }



    }





Dong the same in C# with the TwinCAT dll from beckhoff works flawlessly:

        int handle = tcClient.CreateVariableHandle("MAIN.Rand_1");

        for (int i = 0; i < 1000000; i++) {
          tcClient.Read(handle, dataStream);
          var v = binRead.ReadInt32().ToString();
          Console.WriteLine(v);
          dataStream.Position = 0;
        }



Patrick Boisclair
Analyste - Programmeur senior / Senior Analyst Programmer

[cid:[email protected]]<https://www.noovelia.com/>


462, rue des Forges, Trois-Rivières (Québec) G9A 2H5 CANADA
noovelia.com<https://www.noovelia.com>

[cid:[email protected]]