Hello,
I am sorry I haven't gotten to ask my customer for the SLC500 hardware
so I couldn't test your code. I'll be at their location Monday of next
week and will get it then if possible. Connecting directly to the
frontport serial of a PLC5/25 would likely require the use of a null
modem cable (crossover). On a DB9 connector this basically means
connect 5 to 5  2 to 3 and 3 to 2 as viewed from cable's perspective.
Since it's RS232C you are dealing with RxD and TxD and common only.

That port should be able to ramp up transmission rate to something more
reasonable than 2400 Baud, unless you don't mind waiting. I'd at least
go for 19.2k baud, but I was pretty sure it could handle up to
115.2kbaud which I believe a Rpi should be able to handle too. In any
case, with serial transmission correct you should see continuous
activiy on the indicator lights of the PLC serial port and inside the
PLC system status words have indication of successful connection (ie
physical is good, protocol is correct) from the PLC POV. I don't have
my PLC info in front of me at this time but it is freely available from
Rockwell Automations website, I think they only require you create an
account to be able to download their information usually, especially
legacy controller info.

Good luck,

Stephen
On Fri, 2021-02-26 at 17:05 +0530, Gaurav P wrote:
> Thanks All ....I finally got a chance to test ...created test program
> but I
> am getting this error  , I have connected DF1 serial cable to RPI
> waveshare serial hat which has two serial error ....PLC 5 is running
> at
> baud rate of 2400 and its connected rpi on /dev/ttySC1 ....am I
> getting
> below error of some hardware issue ...how do specify baud rate and
> serial
> channel when I am creating connection ?
> 
> error Error creating channel.
> 
> 
> On Tue, Feb 23, 2021 at 1:30 PM Julian Feinauer <
> [email protected]> wrote:
> 
> > Hey,
> > 
> > as far as I see your code looks good Gaurav, lets try it and then
> > report :
> > )
> > 
> > Best
> > Julian
> > 
> > Von: Gaurav P <[email protected]>
> > Datum: Samstag, 20. Februar 2021 um 19:14
> > An: [email protected] <[email protected]>
> > Betreff: Re: DF1 protocol ...cant find documentation
> > Thanks Chris ... its working ...i added both entries in maven on
> > Monday
> > when I have access to the hardware (AB PLC/5 30) I will test and
> > report
> > back
> > 
> > But for the test case, I am was thinking
> > 
> >    1. Write a value to register like N71
> >    2. Read from register  and confirm value  N71
> > 
> > Kindly review the code below  for testing
> >   try (PlcConnection plcConnection = new
> > PlcDriverManager().getConnection("df1:serial:///ttySC1")) {
> > 
> >          *   //I want write to register N71 , is below code ok ?*
> >             PlcReadRequest request =
> > plcConnection.readRequestBuilder()
> >                     .addItem("N71", "5:INTEGER")
> >                     .build();
> > 
> >             PlcReadResponse response = request.execute().get(100,
> > TimeUnit.SECONDS);
> > 
> > // Check if this connection support reading of data.
> >             if (!plcConnection.getMetadata().canRead()) {
> >                 System.out.println("This connection doesn't support
> > reading.");
> >                 return "This connection doesn't support reading.";
> >             }else {
> > // TODO: get the actual read bytes from the response
> >                 System.out.println(response);
> >                 System.out.println("Response code was " +
> > response.getResponseCode("erster"));
> > 
> >                 System.out.println("Response I got was" +
> > response.getAllIntegers("N71"));
> >           *      //I want Read to register N71 , is below code ok
> > ?*
> >                 return
> > response.getAllIntegers("N71").iterator().next()+"";
> >             }
> > 
> > 
> > 
> > 
> > On Sat, Feb 20, 2021 at 10:52 PM Gaurav P <[email protected]> wrote:
> > 
> > > Hi Chirs ,
> > > Thanks I had suspected the same thing
> > > 
> > > I was able to make it work via adding an apache repository 
> > > (after I
> > > changed the maven snippet you  had given  from 
> > > pluginRepositories to
> > > repositories ) and DF1 guide
> > > <
> > https://docs.google.com/document/d/1FWmwJfXVD03MLtHVsJ0UizoA6D5KzU9JG4VRD-lInGI/edit#
> > <
> > https://docs.google.com/document/d/1FWmwJfXVD03MLtHVsJ0UizoA6D5KzU9JG4VRD-lInGI/edit
> > > > 
> > > (wip)
> > > 
> > > <repositories>
> > >   <repository>
> > >     <id>apache-snapshots</id>
> > >    
> > > <url>https://repository.apache.org/content/repositories/snapshots
> > </url>
> > >     <releases>
> > >       <enabled>false</enabled>
> > >     </releases>
> > >     <snapshots>
> > >       <enabled>true</enabled>
> > >     </snapshots>
> > >   </repository>
> > > </repositories>
> > > 
> > > 
> > > On Sat, Feb 20, 2021 at 10:07 PM Christofer Dutz <
> > > [email protected]> wrote:
> > > 
> > > > Hi,
> > > > 
> > > > the solution was quite simple:
> > > > 
> > > > First off all, we don't release stuff in the Sandbox. So
> > > > there's no
> > 0.8.0
> > > > version.
> > > > Secondly our SNAPSHOTS aren't available from Maven-Central. You
> > > > need to
> > > > add the Apache SNAPSHOT repo to your project.
> > > > 
> > > > In order to do this, please add this to your pom.
> > > > 
> > > >   <!-- Make Snapshots of Apache projects available -->
> > > >   <repositories>
> > > >     <repository>
> > > >       <id>apache-snapshots</id>
> > > >      
> > > > <url>https://repository.apache.org/content/repositories/snapshots
> > > > </url>
> > > >       <releases>
> > > >         <enabled>false</enabled>
> > > >       </releases>
> > > >       <snapshots>
> > > >         <enabled>true</enabled>
> > > >       </snapshots>
> > > >     </repository>
> > > >   </repositories>
> > > > 
> > > >   <!-- Make Snapshots of Apache plugins available -->
> > > >   <pluginRepositories>
> > > >     <pluginRepository>
> > > >       <id>apache-snapshots</id>
> > > >      
> > > > <url>https://repository.apache.org/content/repositories/snapshots
> > > > </url>
> > > >       <releases>
> > > >         <enabled>false</enabled>
> > > >       </releases>
> > > >       <snapshots>
> > > >         <enabled>true</enabled>
> > > >       </snapshots>
> > > >     </pluginRepository>
> > > >   </pluginRepositories>
> > > > 
> > > > That should help.
> > > > 
> > > > Chris
> > > > 
> > > > 
> > > > -----Ursprüngliche Nachricht-----
> > > > Von: Christofer Dutz <[email protected]>
> > > > Gesendet: Samstag, 20. Februar 2021 10:13
> > > > An: [email protected]
> > > > Betreff: Re: DF1 protocol ...cant find documentation
> > > > 
> > > > I'll have a look why this is not available.
> > > > 
> > > > Holen Sie sich Outlook für Android<https://aka.ms/ghei36>
> > > > 
> > > > ________________________________
> > > > From: Gaurav P <[email protected]>
> > > > Sent: Saturday, February 20, 2021 6:19:38 AM
> > > > To: [email protected] <[email protected]>
> > > > Subject: Re: DF1 protocol ...cant find documentation
> > > > 
> > > > Hi Chris ,
> > > > 
> > > > I also  tried with 0.8 , but no luck<dependency>
> > > > 
> > > >   <groupId>org.apache.plc4x.sandbox</groupId>
> > > >   <artifactId>test-java-df1-driver</artifactId>
> > > >   <version>0.8.0</version>
> > > > </dependency>
> > > > 
> > > > 
> > > > On Sat, Feb 20, 2021 at 7:15 AM Gaurav P <[email protected]> wrote:
> > > > 
> > > > > Hi Chris ,
> > > > > 
> > > > > I am not able to maven dependency for df1 driver Cannot
> > > > > resolve
> > > > > org.apache.plc4x.sandbox:test-java-df1-driver:0.9.0-SNAPSHOT
> > > > > 
> > > > > is it not hosted in maven central?
> > > > > 
> > > > > On Fri, Feb 19, 2021 at 6:58 PM Christofer Dutz
> > > > > <[email protected]>
> > > > > wrote:
> > > > > 
> > > > > > Hi Gaurav,
> > > > > > 
> > > > > > you haven't added a dependency to the driver, but to the
> > > > > > protocol
> > > > > > specificaton instead.
> > > > > > This is something we use internally to generate the driver
> > > > > > code in
> > > > > > various languages. You need to add a dependency to
> > > > > > 
> > > > > > <dependency>
> > > > > >     <groupId>org.apache.plc4x.sandbox</groupId>
> > > > > >     <artifactId>test-java-df1-driver</artifactId>
> > > > > >     <version>0.9.0-SNAPSHOT</version> </dependency>
> > > > > > 
> > > > > > Chris
> > > > > > 
> > > > > > -----Ursprüngliche Nachricht-----
> > > > > > Von: Gaurav P <[email protected]>
> > > > > > Gesendet: Freitag, 19. Februar 2021 14:20
> > > > > > An: [email protected]
> > > > > > Betreff: Re: DF1 protocol ...cant find documentation
> > > > > > 
> > > > > > Thanks Chris , Steven
> > > > > > 
> > > > > > I tried the code below but I am getting following error
> > > > > > *error Unable
> > > > > > to find driver for protocol 'df1'*
> > > > > > 
> > > > > > I checked in maven DF1 is added ...what can be the issue ?
> > > > > > 
> > > > > > 
> > > > > > 
> > > > > > try (PlcConnection plcConnection = new
> > > > > > PlcDriverManager().getConnection("df1:serial:///ttySC1")) {
> > > > > >     PlcReadRequest request =
> > > > > > plcConnection.readRequestBuilder()
> > > > > >             .addItem("ind4", "5:INTEGER")
> > > > > >             .build();
> > > > > > 
> > > > > > 
> > > > > > <dependency>
> > > > > >   <groupId>org.apache.plc4x</groupId>
> > > > > >   <artifactId>plc4x-protocols-df1</artifactId>
> > > > > >   <version>0.8.0</version>
> > > > > > </dependency>
> > > > > > 
> > > > > > 
> > > > > > On Fri, Feb 19, 2021 at 6:20 PM Christofer Dutz <
> > > > > > [email protected]>
> > > > > > wrote:
> > > > > > 
> > > > > > > Hi Gaurav,
> > > > > > > 
> > > > > > > that's generally just something used during development
> > > > > > > ... It
> > > > > > > wasn't intended to be used as a standalone application.
> > > > > > > If you want to use it to experiment, you have to replace
> > > > > > > the
> > > > > > > connection string (currently "df1:serial:///COM4" with
> > > > > > > something
> > > > > > > for your case and then add/adjust the items added to the
> > > > > > > Read
> > > > Request.
> > > > > > > 
> > > > > > > Chris
> > > > > > > 
> > > > > > > 
> > > > > > > -----Ursprüngliche Nachricht-----
> > > > > > > Von: Gaurav P <[email protected]>
> > > > > > > Gesendet: Freitag, 19. Februar 2021 13:16
> > > > > > > An: [email protected]
> > > > > > > Betreff: Re: DF1 protocol ...cant find documentation
> > > > > > > 
> > > > > > > Hi Team /Lucas ...
> > > > > > > Thanks  for comments ...
> > > > > > > 
> > > > > > > Should I use this program to test to PLC 500
> > > > > > > 
> > > > > > > 
> > > > > > > 
> > https://github.com/apache/plc4x/blob/develop/sandbox/test-java-df1-
> > > > > > > dri
> > > > > > > ver/src/test/java/org/apache/plc4x/protocol/df1/EndToEndT
> > > > > > > est.java
> > > > > > > 
> > > > > > > 
> > > > > > > Also how do I specify address ?
> > > > > > > 
> > > > > > >  PlcReadRequest request =
> > > > > > > plcConnection.readRequestBuilder()
> > > > > > > 
> > > > > > >                 .addItem("hurz", "5:INTEGER") ->>>>*is
> > > > > > > this address
> > > > > > > of register ???*
> > > > > > > 
> > > > > > >                 .build();
> > > > > > > 
> > > > > > > 
> > > > > > > On Fri, Feb 19, 2021 at 5:12 PM Gaurav P <[email protected]>
> > > > > > > wrote:
> > > > > > > 
> > > > > > > > Hi Team,
> > > > > > > > 
> > > > > > > > I followed the link which was shared by Lukas and Chris
> > > > > > > > and
> > > > > > > > managed to dish out the guide with sample code , which
> > > > > > > > I would be
> > > > > > > > testing AB PLC 500
> > > > > > > > 
> > > > > > > > *
> > https://docs.google.com/document/d/1FWmwJfXVD03MLtHVsJ0UizoA6D5K
> > > > > > > > zU9
> > > > > > > > JG
> > > > > > > > 4VRD-lInGI/edit?usp=sharing
> > > > > > > > <
> > https://docs.google.com/document/d/1FWmwJfXVD03MLtHVsJ0UizoA6D5K
> > > > > > > > zU9 JG 4VRD-lInGI/edit?usp=sharing>  * I have some
> > > > > > > > questions in
> > > > > > > > the above document (marked read), it would be great if
> > > > > > > > can get
> > > > > > > > comments, a post that will compile and run in RPI
> > > > > > > > connect to PLC
> > > > > > > > 
> > > > > > > > Thanks
> > > > > > > > 
> > > > > > > > On Fri, Feb 19, 2021 at 3:25 PM Stephen Snow
> > > > > > > > <[email protected]>
> > > > > > wrote:
> > > > > > > > 
> > > > > > > > > I can get this tested on both serial and ethernet/ip.
> > > > > > > > > I also
> > > > > > > > > have ther
> > > > > > > > > DF1 protocol manual.
> > > > > > > > > 
> > > > > > > > > Stephen
> > > > > > > > > On Fri, 2021-02-19 at 15:22 +0530, Gaurav P wrote:
> > > > > > > > > > Thanks Chris ... I have access to an ancient AB PLC
> > > > > > > > > > 5/260  and
> > > > > > > > > > will start testing and report back to you
> > > > > > > > > > .....transport link
> > > > > > > > > > would be serial ...hope it wont be any issue  After
> > > > > > > > > > I go
> > > > > > > > > > through the docs , hope its not too complex , I
> > > > > > > > > > maybe able to
> > > > > > > > > > maintain and test driver
> > > > > > > > > > 
> > > > > > > > > > On Fri, Feb 19, 2021 at 1:07 PM Christofer Dutz
> > > > > > > > > > <[email protected]>
> > > > > > > > > > wrote:
> > > > > > > > > > 
> > > > > > > > > > > Hi Gaurav,
> > > > > > > > > > > 
> > > > > > > > > > > also from my side, welcome :-)
> > > > > > > > > > > 
> > > > > > > > > > > I think the DF1 was one of the first tob e
> > > > > > > > > > > created with the
> > > > > > > > > > > new code-generation framework.
> > > > > > > > > > > However due to lack of hardware to test on, it's
> > > > > > > > > > > still
> > > > > > > > > > > located in the "Sandbox" and got a "test" prefix
> > > > > > > > > > > on it.
> > > > > > > > > > > 
> > > > > > > > > > >     <dependency>
> > > > > > > > > > >        
> > > > > > > > > > > <groupId>org.apache.plc4x.sandbox</groupId>
> > > > > > > > > > >         <artifactId>test-java-df1-
> > > > > > > > > > > driver</artifactId>
> > > > > > > > > > >         <version>0.9.0-SNAPSHOT</version>
> > > > > > > > > > >     </dependency>
> > > > > > > > > > > 
> > > > > > > > > > > Also I think it supports all features that were
> > > > > > > > > > > needed by
> > > > > > > > > > > the folks that implemented it, but probably not
> > > > > > > > > > > much more
> > > > than that.
> > > > > > > > > > > 
> > > > > > > > > > > So please test it. If you need it to do more and
> > > > > > > > > > > you've got
> > > > > > > > > > > a device you can test it with, we'd be happy to
> > > > > > > > > > > help you
> > with
> > > > that.
> > > > > > > > > > > 
> > > > > > > > > > > Chris
> > > > > > > > > > > 
> > > > > > > > > > > 
> > > > > > > > > > > -----Ursprüngliche Nachricht-----
> > > > > > > > > > > Von: Lukas Ott <[email protected]>
> > > > > > > > > > > Gesendet: Freitag, 19. Februar 2021 07:33
> > > > > > > > > > > An: [email protected]
> > > > > > > > > > > Betreff: Re: DF1 protocol ...cant find
> > > > > > > > > > > documentation
> > > > > > > > > > > 
> > > > > > > > > > > Hi Gaurav,
> > > > > > > > > > > 
> > > > > > > > > > > Welcome to the list :-),
> > > > > > > > > > > 
> > > > > > > > > > > Yes it really is supported. Here you ll find some
> > > > > > > > > > > more
> > > > details:
> > > > > > > > > > > 
> > https://plc4x.apache.org/developers/code-gen/protocol/df1.ht
> > > > > > > > > > > ml
> > > > > > > > > > > 
> > > > > > > > > > > The best way to get started you can find here:
> > > > > > > > > > > https://plc4x.apache.org/users/getting-started/plc4j.html
> > > > > > > > > > > to understand more read here:
> > > > > > > > > > > 
> > https://plc4x.apache.org/users/getting-started/general-conce
> > > > > > > > > > > pts
> > > > > > > > > > > .h
> > > > > > > > > > > tml
> > > > > > > > > > > 
> > > > > > > > > > > For release 0.6 you ll find the java code here:
> > > > > > > > > > > 
> > > > > > > > > > > 
> > > > > > > > > 
> > https://github.com/apache/plc4x/blob/rel/0.6/protocols/df1/src/m
> > > > > > > > > ain /j
> > > > > > > > > ava/org/apache/plc4x/protocol/df1/Df1Protocol.java
> > > > > > > > > > > 
> > > > > > > > > > > 
> > > > > > > > > > > Example code you ll find here:
> > > > > > > > > > > https://github.com/apache/plc4x/tree/develop/plc4j/examples
> > > > > > > > > > > 
> > > > > > > > > > > Currently not sure if we ported DF1 to release
> > > > > > > > > > > 0.8
> > > > > > > > > > > 
> > > > > > > > > > > Cheers,
> > > > > > > > > > > otluk
> > > > > > > > > > > 
> > > > > > > > > > > Am Fr., 19. Feb. 2021 um 03:41 Uhr schrieb Gaurav
> > > > > > > > > > > P <
> > > > > > [email protected]>:
> > > > > > > > > > > 
> > > > > > > > > > > > Hi Team ,
> > > > > > > > > > > > I am new to PLC4x , trying to integrate with
> > > > > > > > > > > > DF1 but cant
> > > > > > > > > > > > find any documentation ....
> > > > > > > > > > > > https://plc4x.apache.org/users/protocols/df1.html
> > > > > > > > > > > > 
> > > > > > > > > > > > is it really supported? if yes where can I get
> > > > > > > > > > > > documentation and an example code
> > > > > > > > > > > > --
> > > > > > > > > > > > B*e * the *Ch*ange
> > > > > > > > > > > > 
> > > > > > > > > > > 
> > > > > > > > > > 
> > > > > > > > > > 
> > > > > > > > > 
> > > > > > > > > 
> > > > > > > > > 
> > > > > > > > 
> > > > > > > > --
> > > > > > > > B*e * the *Ch*ange
> > > > > > > > 
> > > > > > > 
> > > > > > > 
> > > > > > > --
> > > > > > > B*e * the *Ch*ange
> > > > > > > 
> > > > > > 
> > > > > > 
> > > > > > --
> > > > > > B*e * the *Ch*ange
> > > > > > 
> > > > > 
> > > > > 
> > > > > --
> > > > > B*e * the *Ch*ange
> > > > > 
> > > > 
> > > > 
> > > > --
> > > > B*e * the *Ch*ange
> > > > 
> > > 
> > > 
> > > --
> > > B*e * the *Ch*ange
> > > 
> > 
> > 
> > --
> > B*e * the *Ch*ange
> > 
> 
> 


Reply via email to