Hi,

I think we only had the status codes in there that we needed so far.
However it would be cool if the codes wouldn't differ for each connection type.
So how about adding a "CONNECTION_INVALID" code? 

I guess an OPC-UA Session is what other protocols consider a connection - right?

Just my thoughts to that.

Chris

-----Ursprüngliche Nachricht-----
Von: Torsten Uhr <[email protected]> 
Gesendet: Freitag, 22. Oktober 2021 12:46
An: [email protected]
Betreff: AW: AW: AW: ClassCastException: class 
org.apache.plc4x.java.opcua.readwrite.ServiceFault cannot be cast to class 
org.apache.plc4x.java.opcua.readwrite.ReadResponse

Hi Łukasz,

may be should extend PlcResponseCode to have a new value SESSION_INVALID. 
Optionally a method forOPCStatucCode( long opcCode ) could be there to get a 
suitable code fort he passed OPC code.
E.g. 2149908480 will map to SESSION_INVALID.

                        PlcResponseCode code = PlcResponseCode.INTERNAL_ERROR;
                        if (reply instanceof ServiceFault) {
                            ExtensionObjectDefinition header = ((ServiceFault) 
reply).getResponseHeader();
                            code = PlcResponseCode.forOPCStatucCode( 
((org.apache.plc4x.java.opcua.readwrite.ResponseHeader) 
header).getServiceResult().getStatusCode() );
                            LOGGER.error("Read request ended up with 
ServiceFault: {}", header);
                        } else {
                            LOGGER.error("Remote party returned an error '{}'", 
reply);
                        }

                        Map<String, ResponseItem<PlcValue>> status = new 
LinkedHashMap<>();
                        for (String key : request.getFieldNames()) {
                            status.put(key, new ResponseItem<>(code, null));
                        }
                        future.complete(new DefaultPlcReadResponse(request, 
status));
                        return;

But current solution works and is OK for me.

with best regards Torsten

SQL Projekt AG  ▪ Franklinstraße 25 a  ▪ 01069 Dresden

Telefon:        (0351) 87619-0
Telefax:        (0351) 87619-99
E-Mail:         [email protected]
Web:    www.sql-ag.de

Aufsichtsratsvorsitzender: Jürgen Bittner
Vorstand: Stefan Ehrlich, Jens Gärtner (Sprecher)
Handelsregister: HRB 38924 Amtsgericht Dresden Die Zertifizierungsstelle der 
TÜV SÜD Management Service GmbH bescheinigt, dass die SQL Projekt AG für den 
Geltungsbereich "Entwicklung und Vertrieb von Datenbank- und 
Integrationslösungen sowie Beratung, Training und Support auf dem Gebiet 
datenbankgestützter Softwareprodukte" ein Qualitätsmanagementsystem eingeführt 
hat und anwendet.


Diese E-Mail enthält vertrauliche und/oder rechtlich geschützte Informationen.
Wenn Sie nicht der richtige Adressat sind oder diese E-Mail irrtümlich erhalten 
haben, informieren Sie bitte sofort den Absender und vernichten Sie diese Mail. 
Das unerlaubte Kopieren sowie die unbefugte Weitergabe dieser Mail oder Inhalte 
ist nicht gestattet.

This e-mail may contain confidential and/or privileged information.
If you are not the intended recipient (or have received this e-mail in error) 
please notify the sender immediately and destroy this e-mail. Any unauthorized 
copying, disclosure or distribution of the material in this e-mail is strictly 
forbidden.

-----Ursprüngliche Nachricht-----
Von: Łukasz Dywicki <[email protected]>
Gesendet: Freitag, 22. Oktober 2021 11:18
An: [email protected]
Betreff: Re: AW: AW: ClassCastException: class 
org.apache.plc4x.java.opcua.readwrite.ServiceFault cannot be cast to class 
org.apache.plc4x.java.opcua.readwrite.ReadResponse

REMOTE_ERROR could be better, but to make it right we need to look into actual 
ServiceFault header and its result code. Possibly we will find there a better 
indication of what the error is.

If you will look at my last commit on develop you will find right place to put 
OPC <> PLC4X status mapping logic.

Kind regards,
Łukasz


On 22.10.2021 09:59, Torsten Uhr wrote:
> Hi Łukasz,
>
> thanks for the very quick response. It works as expected.
> Did You think the response code "REMOTE_ERROR" might more suite than 
> "INTERNAL_ERROR"?
>
> With best regards
>
> Torsten Uhr
> SQL Projekt AG  ▪ Franklinstraße 25 a  ▪ 01069 Dresden
>
> Telefon:      (0351) 87619-0
> Telefax:      (0351) 87619-99
> E-Mail:       [email protected]<mailto:[email protected]>
> Web:  www.sql-ag.de<http://www.sql-ag.de>
>
> Aufsichtsratsvorsitzender: Jürgen Bittner
> Vorstand: Stefan Ehrlich, Jens Gärtner (Sprecher)
> Handelsregister: HRB 38924 Amtsgericht Dresden Die 
> Zertifizierungsstelle der TÜV SÜD Management Service GmbH bescheinigt, 
> dass die SQL Projekt AG für den Geltungsbereich "Entwicklung und 
> Vertrieb von Datenbank- und Integrationslösungen sowie Beratung, Training und 
> Support auf dem Gebiet datenbankgestützter Softwareprodukte" ein 
> Qualitätsmanagementsystem eingeführt hat und anwendet.
>
>
> Diese E-Mail enthält vertrauliche und/oder rechtlich geschützte Informationen.
> Wenn Sie nicht der richtige Adressat sind oder diese E-Mail irrtümlich 
> erhalten haben, informieren Sie bitte sofort den Absender und vernichten Sie 
> diese Mail. Das unerlaubte Kopieren sowie die unbefugte Weitergabe dieser 
> Mail oder Inhalte ist nicht gestattet.
>
> This e-mail may contain confidential and/or privileged information.
> If you are not the intended recipient (or have received this e-mail in error) 
> please notify the sender immediately and destroy this e-mail. Any 
> unauthorized copying, disclosure or distribution of the material in this 
> e-mail is strictly forbidden.
>
> -----Ursprüngliche Nachricht-----
> Von: Łukasz Dywicki <[email protected]<mailto:[email protected]>>
> Gesendet: Donnerstag, 21. Oktober 2021 23:21
> An: [email protected]<mailto:[email protected]>
> Betreff: Re: AW: ClassCastException: class 
> org.apache.plc4x.java.opcua.readwrite.ServiceFault cannot be cast to 
> class org.apache.plc4x.java.opcua.readwrite.ReadResponse
>
> Thank you for test case.
>
> I've implemented basic fix for issue based on my sparse knowledge of OPC UA. 
> Issue was missing a callback call when server returned an error.
>
> I improved that, now you sohuld get at least failed answer back.
> Original reply is logged. I did not map yet status code from server.
>
> Pushed to developer for 0.10, please test.
>
> Best,
> Łukasz
>
>
> On 21.10.2021 14:03, Christofer Dutz wrote:
>> Hi Thorsten,
>>
>> first of all: Thank you for providing a Unit Test for demonstrating 
>> your problem ... that makes our lives a lot easier :-)
>>
>> I'm sure someone on the community will have a look at the issue soon. I'll 
>> try to ping the right people for that.
>>
>> Chris
>>
>> -----Ursprüngliche Nachricht-----
>> Von: Torsten Uhr 
>> <[email protected]<mailto:[email protected]>>
>> Gesendet: Donnerstag, 21. Oktober 2021 13:12
>> An: [email protected]<mailto:[email protected]>
>> Betreff: ClassCastException: class
>> org.apache.plc4x.java.opcua.readwrite.ServiceFault cannot be cast to 
>> class org.apache.plc4x.java.opcua.readwrite.ReadResponse
>>
>> Hi all,
>>
>> if I create an OPCUA connection (to milo) and wait 5 minutes before sending 
>> a read request the error attached below is logged and the read execution 
>> blocks infinitely.
>> I'm used codebase 0.9.0 and 0.10.0 snapshot.
>> Note: The wait simulates a connection created earlier and get from a 
>> connection pool in a managed environment like application server.
>> I think theres a timeout for pending connections on the server side. I would 
>> expect, that the driver should throw an exception rather blocking?
>>
>> [nioEventLoopGroup-2-1] WARN io.netty.channel.DefaultChannelPipeline - An 
>> exceptionCaught() event was fired, and it reached at the tail of the 
>> pipeline. It usually means the last handler in the pipeline did not handle 
>> the exception.
>> io.netty.handler.codec.DecoderException: java.lang.ClassCastException: class 
>> org.apache.plc4x.java.opcua.readwrite.ServiceFault cannot be cast to class 
>> org.apache.plc4x.java.opcua.readwrite.ReadResponse 
>> (org.apache.plc4x.java.opcua.readwrite.ServiceFault and 
>> org.apache.plc4x.java.opcua.readwrite.ReadResponse are in unnamed module of 
>> loader 'app')
>>           at 
>> io.netty.handler.codec.MessageToMessageDecoder.channelRead(MessageToMessageDecoder.java:98)
>>           at 
>> io.netty.handler.codec.MessageToMessageCodec.channelRead(MessageToMessageCodec.java:111)
>>           at 
>> io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:379)
>>           at 
>> io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:365)
>>           at 
>> io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(AbstractChannelHandlerContext.java:357)
>>           at 
>> io.netty.handler.codec.ByteToMessageDecoder.fireChannelRead(ByteToMessageDecoder.java:324)
>>           at 
>> io.netty.handler.codec.ByteToMessageDecoder.channelRead(ByteToMessageDecoder.java:296)
>>           at 
>> io.netty.handler.codec.ByteToMessageCodec.channelRead(ByteToMessageCodec.java:103)
>>           at 
>> io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:379)
>>           at 
>> io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:365)
>>           at 
>> io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(AbstractChannelHandlerContext.java:357)
>>           at 
>> io.netty.channel.DefaultChannelPipeline$HeadContext.channelRead(DefaultChannelPipeline.java:1410)
>>           at 
>> io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:379)
>>           at 
>> io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:365)
>>           at 
>> io.netty.channel.DefaultChannelPipeline.fireChannelRead(DefaultChannelPipeline.java:919)
>>           at 
>> io.netty.channel.nio.AbstractNioByteChannel$NioByteUnsafe.read(AbstractNioByteChannel.java:166)
>>           at 
>> io.netty.channel.nio.NioEventLoop.processSelectedKey(NioEventLoop.java:719)
>>           at 
>> io.netty.channel.nio.NioEventLoop.processSelectedKeysOptimized(NioEventLoop.java:655)
>>           at 
>> io.netty.channel.nio.NioEventLoop.processSelectedKeys(NioEventLoop.java:581)
>>           at io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:493)
>>           at 
>> io.netty.util.concurrent.SingleThreadEventExecutor$4.run(SingleThreadEventExecutor.java:986)
>>           at 
>> io.netty.util.internal.ThreadExecutorMap$2.run(ThreadExecutorMap.java:74)
>>           at 
>> io.netty.util.concurrent.FastThreadLocalRunnable.run(FastThreadLocalRunnable.java:30)
>>           at java.base/java.lang.Thread.run(Thread.java:834)
>> Caused by: java.lang.ClassCastException: class 
>> org.apache.plc4x.java.opcua.readwrite.ServiceFault cannot be cast to class 
>> org.apache.plc4x.java.opcua.readwrite.ReadResponse 
>> (org.apache.plc4x.java.opcua.readwrite.ServiceFault and 
>> org.apache.plc4x.java.opcua.readwrite.ReadResponse are in unnamed module of 
>> loader 'app')
>>           at 
>> org.apache.plc4x.java.opcua.protocol.OpcuaProtocolLogic.lambda$read$0(OpcuaProtocolLogic.java:177)
>>           at 
>> org.apache.plc4x.java.opcua.context.SecureChannel.lambda$4(SecureChannel.java:212)
>>           at 
>> org.apache.plc4x.java.spi.Plc4xNettyWrapper.decode(Plc4xNettyWrapper.java:175)
>>           at 
>> io.netty.handler.codec.MessageToMessageCodec$2.decode(MessageToMessageCodec.java:81)
>>           at 
>> io.netty.handler.codec.MessageToMessageDecoder.channelRead(MessageToMessageDecoder.java:88)
>>           ... 23 more
>>
>>
>> JUnit regeression test:
>>
>> import org.apache.plc4x.java.PlcDriverManager;
>> import org.apache.plc4x.java.api.PlcConnection;
>> import org.apache.plc4x.java.api.messages.PlcReadRequest;
>> import org.junit.Assert;
>> import org.junit.jupiter.api.Test;
>>
>> public class RegressionTest
>> {
>>      @Test
>>      public void Timeout()
>>      {
>>         String connectionString = 
>> "opcua:tcp://localhost:12686/milo?discovery=false";
>>         final int TIMEOUT = 300 * 1000;
>>
>>         try (PlcConnection plcConnection = new 
>> PlcDriverManager().getConnection( connectionString ))
>>         {
>>            Thread.sleep( TIMEOUT );
>>
>>            PlcReadRequest.Builder builder = 
>> plcConnection.readRequestBuilder();
>>            builder.addItem("value",
>> "ns=2;s=HelloWorld/ScalarTypes/String");
>>
>>            builder.build().execute().get();
>>         }
>>         catch( Throwable thr )
>>         {
>>            Assert.fail( thr.getMessage() );
>>         }
>>      }
>> }
>>
>>
>> With best regards
>> Torsten Uhr
>>

Reply via email to