Hi Markus,

BYTE, WORD and DWORD are intentionally implemented that way as in the IEC??? 
Spec that is how they are defined.
So if you read a USINT, SINT or BYTE should not matter on the protocol level, 
In the PLCValue objects however it defines how the data is represented. So, a 
BYTE being a bit-string should result in a PlcList with 8 PlcBool elements, 
while one of the others should be a numeric value. 

This would not be a bug, but a design decision we did to be compliant with the 
specs.

So in your case, you would need to either initialize a List of PlcBool values 
and write that, or you write the BYTE variable with an USINT or SINT value. 

Chris


-----Original Message-----
From: Markus Franke <[email protected]> 
Sent: Dienstag, 30. November 2021 13:41
To: [email protected]
Subject: AW: Supported Datatypes for S7-1200 with PLC4J

Hi Christofer,

thanks for your clarifications regarding the limitations of the current PLC4J 
implementation on S7.

Regarding the bitfield datatypes such as BYTE, WORD and DWORD, so far I was 
only able to read/write those bit-by-bit.

Suppose datablock 100, address 817 contains a BYTE variable. I was only able to 
write to the individual bits by using the following address format

%DB100.DBX817.0:BOOL
...
%DB100.DBX817.7:BOOL

Trying to write the whole BYTE with a single operation like

%DB100.DBB817:BYTE

gives me a

---snip---
Exception in thread "main" java.lang.ClassCastException: class 
org.apache.plc4x.java.spi.values.PlcBYTE cannot be cast to class 
org.apache.plc4x.java.spi.values.PlcList 
(org.apache.plc4x.java.spi.values.PlcBYTE and 
org.apache.plc4x.java.spi.values.PlcList are in unnamed module of loader 'app') 
at 
org.apache.plc4x.java.s7.readwrite.io.DataItemIO.staticSerialize(DataItemIO.java:291)
at 
org.apache.plc4x.java.s7.readwrite.io.DataItemIO.staticSerialize(DataItemIO.java:275)
at 
org.apache.plc4x.java.s7.readwrite.protocol.S7ProtocolLogic.serializePlcValue(S7ProtocolLogic.java:862)
at 
org.apache.plc4x.java.s7.readwrite.protocol.S7ProtocolLogic.write(S7ProtocolLogic.java:288)
at 
org.apache.plc4x.java.spi.optimizer.BaseOptimizer.lambda$optimizedWrite$2(BaseOptimizer.java:114)
at 
org.apache.plc4x.java.spi.optimizer.BaseOptimizer.send(BaseOptimizer.java:151)
at 
org.apache.plc4x.java.spi.optimizer.BaseOptimizer.optimizedWrite(BaseOptimizer.java:114)
at 
org.apache.plc4x.java.spi.connection.AbstractPlcConnection.write(AbstractPlcConnection.java:159)
at 
org.apache.plc4x.java.spi.messages.DefaultPlcWriteRequest.execute(DefaultPlcWriteRequest.java:65)
at Siemens.main(Siemens.java:61)
---snap---

Similarily, for reading I receive the individual bits of the BYTE one-by-one. 
However, I guess this is expected behaviour as we are dealing with a bit-field 
datatype, right?

Best regards,
Markus

________________________________
Von: Christofer Dutz <[email protected]>
Gesendet: Dienstag, 30. November 2021 12:59
An: [email protected] <[email protected]>
Betreff: RE: Supported Datatypes for S7-1200 with PLC4J

Hi,

let me jump in here ;)

I know with strings there are currently issues. Especially with smaller S7 
devices (which have smaller PDU Sizes).
The problem here is, that the default length of one string already exceeds the 
PDU size of the S7 1200 devices I have.
So, you always must provide a max string length. As soon as you do that, 
strings are unfortunately handled slightly differently.

To support normal strings with their full length, the Query optimizer in S7 
would need to be extended with the ability to split up individual items into 
multiple parts. This is something I haven't done yet.

To support normal strings on larger S7 devices (Where the PDU Size allows 
fitting them into the request), we probably need more testing and for that I 
would at least need access to such a device.

LREAL is unfortunately not supported on the S7-1200 devices that I have, and 
therefore I could never really test that. Same with the Time datatypes.

So, all in all, I thank you for your list of things we need to improve. I 
promise that we will work on this.

However, I can't give you an ETA on which I personally will be able to work on 
this, as I'm currently working on other things. Perhaps someone in the 
community can jump in. Or even you might be interested in helping. If you think 
you are able to do that, I am more than willing to help mentor you.

Chris



-----Original Message-----
From: Markus Franke <[email protected]>
Sent: Dienstag, 30. November 2021 09:34
To: [email protected]
Subject: AW: Supported Datatypes for S7-1200 with PLC4J

Hi Cesar,

so far my experiences are as follows:

​datatype    read    write
=========================
BOOL        ok      ok
BYTE        ok      ok(only bitwise)
WORD        ok      ok(only bitwise)
DWORD       ok      ok(only bitwise)
SINT        ok      ok
USINT       ok      ok
INT         ok      ok
UINT        ok      ok
DINT        ok      ok
UDINT       ok      ok
REAL        ok      ok
LREAL       nok     nok
CHAR        ok      nok
WCHAR       ok      nok
STRING      nok     nok
WSTRING     nok     nok
TIME        ok      nok
DATE        ok      nok
TIME_OF_DAY ok      nok

So it seems like writing is currently unsupported for quite a few datatypes.
Also reading (W)STRING and LREAL seems to be an issue currently.

Any comments on this?

Thanks in advance,
Markus


________________________________
Von: Cesar Garcia <[email protected]>
Gesendet: Montag, 29. November 2021 17:38
An: Apache PLC4X <[email protected]>
Betreff: Re: Supported Datatypes for S7-1200 with PLC4J

Hi Markus,

Can you put an example of the required formats?

Best regards,

El lun, 29 nov 2021 a las 11:27, Markus Franke (<[email protected]>)
escribió:

> Dear all,
>
> I am currently connecting to a S7-1200 by using PLC4J 0.9.0.
>
> As I have problems with reading/writing certain datatypes from a 
> datablock, I was wondering whether there are currently any restriction 
> what kind of datatypes are actually supported for reading/writing with 
> this hardware setup?
>
> Thanks and best regards,
> Markus
>


--
*CEOS Automatización, C.A.*
*GALPON SERVICIO INDUSTRIALES Y NAVALES FA, C.A.,* *PISO 1, OFICINA 2, AV. RAUL 
LEONI, SECTOR GUAMACHITO,*

*FRENTE A LA ASOCIACION DE GANADEROS,BARCELONA,EDO. ANZOATEGUI* *Ing. César 
García*

*Cel: +58 414-760.98.95*

*Hotline Técnica SIEMENS: 0800 1005080*

*Email: [email protected]
<[email protected]>*

Reply via email to