And as I mentioned: Due to this limitation of connections, the connection pool 
currently only handles one instance per target, so there isn't any transferring 
of subscriptions needed. However, I do need to figure out how to re-subscribe 
in case a connection goes bad.

Chris

-----Original Message-----
From: Christofer Dutz <[email protected]> 
Sent: Freitag, 21. Januar 2022 10:13
To: [email protected]
Subject: RE: More possible problems with connection pools

Hi Niclas,

I think the very special problem we have here is the limitation of the number 
of concurrent connections PLCs usually provide ... my S7 1200 allows 3 
concurrent connections. My KNX gateway (which is one of the better models 
allowing multiple concurrent connections) only allows 4 connections. 

So, we really need to find a balance between the number of connections and the 
features we offer. 

In the case of KNX we even have the situation that, as soon as you connect to 
the gateway, you become part of the KNX network and everything happening on 
that is automatically forwarded to the clients. So, it's sort of: As soon as 
you connect, you subscribe to everything. The actual subscriptions I then 
handle by filtering this stream of incoming events by all subscriptions. But I 
know this will probably be different for other protocols (like Cesar's S7 
Events)

So, in general, I would agree with your assumption, but in this case, I would 
try to use one connection for as much as possible. Assuming a S7-1200 is used 
and it has an HMI and the company has some sort of control-system. Then already 
2 of the 3 available connections are used. In case of KNX: You usually need to 
keep one connection free for the engineering software, one for us and usually 
if you need any form of bridge or converter that also consumes at least one 
connection.

Chris



-----Original Message-----
From: Niclas Hedhman <[email protected]>
Sent: Freitag, 21. Januar 2022 09:43
To: [email protected]
Subject: Re: More possible problems with connection pools

On 2022-01-21 09:19, Christofer Dutz wrote:
> So instead of having the subscriber having to keep the connection to 
> keep the subscription alive, I would opt for adding subscriptions to 
> the connection and keeping them valid, even after the connection is 
> returned to the pool. Yes, this causes subscriptions from multiple 
> places in your application to get mixed up and potentially one part 
> could interfere with another one (Like unsubscribe a subscription a 
> different part subscribed for). But I think from an API perspective 
> this would probably be the best option for the normal use-cases.

I have had this exact issue (well, not KNX) a long time ago and I would like to 
provide a recommendation;

   * Don't put subscription on Request/Reply connections.

it will down the line complicate matters, with re-subscriptions when a 
request/reply fail for small modest reasons, the connection is torn down, and 
the subscriptions needing to be re-established, and possible clients 
unsubscribing while that is going on. AND dynamic allocation of connections 
becomes harder too, as one has to move subscriptions from one connection to 
another to be able to delete a connection from the pool.

Try to put subscription in separate API/interface.


Cheers
Niclas

Reply via email to