Hi,

I definitely think that all the drivers should be returning the same format
as each other for each data type, I think that is more important than the
format they are returned in.

However, generally from what I have seen BYTE, WORD, etc... datatypes get
returned as basically unsigned integer or byteish types, then it is up to
the user to represent that however they wish. If I write one byte I would
expect when reading it, using the same data type, it would return 1 byte
not an array of 8 bits.

IEC 61131-3 v2 2003 has a few references in there about how they should be
handled. It would be interesting to get a hold of the 2013 revision though.

This shows that they should be handled as integer values

>   1.3.43 integer literal: literal which directly represents a value of
> type SINT, INT, DINT, LINT, BOOL, BYTE, WORD, DWORD, or LWORD, as defined
> in 2.3.1.
>

This then mentions they should be handled as bit string

>   17 BYTE Bit string of length 8 8 j,g


A bit string the gets defined as

>   1.3.11 bit string: data element consisting of one or more bits.


All a bit vague.

For OPCUA, when writing values to a server (Assuming BYTE types, and binary
encoding) they should be writing them in groups of 8 bits with the length
specifier indicating the number of groups of 8 bits, not the number of bits.
At the moment when reading them they get returned as java byte values.

Ben

On Sun, Feb 6, 2022 at 4:40 AM Christofer Dutz <[email protected]>
wrote:

> Hi all,
>
> while working on the tests for the Proxy protocol, I stumbled in some pits
> regarding the encoding of the BitString values.
>
> So, the IEC61131ValueHandler didn't utilize the BitString PlcValue types,
> but use the PlcBYTE, which is generally identical to PlcUSINT.
> I know some drivers correctly used the bit strings for the IEC types (as
> the IEC spec describes them) ... after fixing this I noticed some other
> drivers going red (Modbus, OPC-UA, ...)
> I fixed the issue in the Modbus test-suite as this was not 100% correct,
> but with OPC-UA I'm a bit unsure (However it does use the
> IEC61131ValueHandler too) ... I am not sure if here the same naming
> convention is expected as here, I can see this:
>
> case "BYTE":
> case "BITARR8":
> case "USINT":
> case "UINT8":
> case "BIT8":
>     List<Short> tmpBYTE = new ArrayList<>(length);
>     for (int i = 0; i < length; i++) {
>         tmpBYTE.add((short) valueObject.getIndex(i).getByte());
>     }
>
> If you ask me, BYTE and BITARR8 should be BitStrings too (Especially
> BITARR8 ... and obviously also the 16, 32 and 64 bit versions)
>
> Would it be ok to streamline this throughout our drivers?
>
> Chris
>