Hi,

So here I disagree with you.
SunSpec is nothing more than a standardized way of giving meaning to modbus
registers for a certain class of devices.
It is still standard modbus to fetch that data.

> If I wanted to read 40000 to 410000 by chunks of 10, I could do it and
‘just make sense’ of the returned range.

So on the device I have this is simply not true: I cannot simply read any
set of registers and get the correct values.
I provided a packet trace here https://github.com/apache/plc4x/issues/743
so you can see for yourself what I'm getting.

This is the way the modbus server in this device has been written, I expect
more devices to have similar effects.

Niels




On Mon, Jan 16, 2023 at 6:21 PM Otto Fowler <[email protected]> wrote:

>  I believe you are having issues because of sunspec over modbus and not
> modbus ‘generically’
>
> If you wanted to read modbus as just registers, memory ranges and chunk
> that there is no reason that cannot be done.  If I wanted to read 40000 to
> 410000 by chunks of 10, I could do it and ‘just make sense’ of the returned
> range.
>
> I don’t think we should conflate *BASE* modbus functionality with how
> models or specs that ride on top of modbus operate.  I think *would*  more
> likely a bug in how the sunspec layer is being evaluated.
>
> Maybe a sunspec specific derivative of the modbus spec would be better.
>
> for information on how sunspec access may look :
>
> https://github.com/nmakel/solaredge_modbus/blob/master/src/solaredge_modbus/__init__.py
>
>
>
>
> From: Niels Basjes <[email protected]> <[email protected]>
> Reply: [email protected] <[email protected]> <[email protected]>
> Date: January 16, 2023 at 03:21:42
> To: [email protected] <[email protected]> <[email protected]>
> Subject:  Re: [Modbus] Handling 'too large' blocks of registers
>
> Hi,
>
> Yes this is exactly my idea as well.
> Splitting a request for >125 registers into multiple requests cannot be
> done in a generic reliable way.
> If you know the schema (i.e. meaning of the registers) then you can combine
> requests with multiple logical values into blocks of modbus registers that
> stay within the 125 register limit.
>
> Which implies the need for a (generic) way of defining logical values and
> the modbus registers from which they can be read (with all kinds of
> constraints about reading them).
> I would call this a modbus schema definition which can then be used to
> calculate the actual read/write operations.
>
> The effect would be that for every type of device a schema definition is to
> be created from which a client can be created/generated.
>
> Niels
>
>
>
>
>
> On Mon, Jan 16, 2023 at 8:50 AM Ben Hutcheson <[email protected]>
> wrote:
>
> > Hi Niels,
> >
> > As Łukasz pointed out, there are a thousand different combinations of how
> > Modbus requests can be arranged. I'm not sure there's a generic schema
> that
> > can be used to define it though.
> >
> > You talked originally about splitting large reads (>125 registers) up
> into
> > smaller registers. This logic would live in a class that implements the
> > BaseOptimizer. This is then defined within the ModbusTCPDriver class, we
> > are just using the SingleTagOptimizer for Modbus at the moment.
> >
> > If I were to implement this I would probably firstly try and combine tags
> > that are adjacent into one request until we either encounter a break in
> the
> > requested area or approach the limit of ~125 registers. This way it is
> > guaranteed that requests for individual requests are not broken into
> > smaller requests.
> >
> > Kind Regards
> >
> > Ben
> >
> >
> >
> >
> >
> > On Sun, Jan 15, 2023 at 6:58 PM Niels Basjes <[email protected]> wrote:
> >
> > > Hi Łukasz,
> > >
> > > At this point I tend towards the need for a tool that allows one to
> > define
> > > the schema of a modbus device with all available values and code to
> > convert
> > > them into usable stuff (like in java an actual String or Double).
> > > So far it seems this needs indeed flags indicating which values can and
> > > must be read combined (like the sync block in SunSpec).
> > > Then based on this a request for a set of functional values is
> converted
> > > into a set of modbus requests that follow these defined rules.
> > >
> > > Rules about an after connection delay and maximum requests per second
> > seem
> > > like something that should be at the modbus level (i.e. part of plc4x).
> > >
> > > Is there an existing project that does something like this?
> > >
> > > Niels
> > >
> > > On Sun, Jan 15, 2023 at 5:22 PM Łukasz Dywicki <[email protected]>
> > > wrote:
> > >
> > > > I am really glad you are moving it forward and fighting it!
> > > >
> > > > It is fairly difficult to get modbus code aligned and working
> > > > automatically because different devices behave differently with even
> > > > most basic requests.
> > > > I remember that one of electric meters I had to work with did support
> > > > read multiple registers but did not support going over "empty"
> indexes.
> > > > By empty I mean these which were not declared in the documentation,
> > > > even if it was still below 125 limit.
> > > >
> > > > Effectively I could draw three primary options to cover:
> > > > - read continuous (just keep expanding requests up to the limit)
> > > > - read blocks (group indexes into blocks up to limit, if they are
> > > > continuous)
> > > > - read single (read multiple registers is not supported)
> > > >
> > > > Some devices, especially older PLCs may also require extra delay
> after
> > > > data retrieval, so you have to wait between finishing one request and
> > > > starting another. Some inverters and official dongles made by fairly
> > > > large Chinese manufacturer, which brand I won't mention here, as well
> > as
> > > > primitive tcp/rtu bridges, may require "after connection delay" in
> > order
> > > > to establish rtu connection they use to serve tcp session.
> > > >
> > > > All this makes modbus option list rather long, compared to abilities
> it
> > > > gives!
> > > >
> > > > Cheers,
> > > > Łukasz
> > > >
> > > >
> > > > On 15.01.2023 17:05, Niels Basjes wrote:
> > > > > Hi,
> > > > >
> > > > > No, I'm reading many logical values where the needed registers
> > combined
> > > > > exceed the 125 mark.
> > > > > Assume my application needs a set of values and asks for such a
> block
> > > of
> > > > > registers.
> > > > > Then the modbus library that gets the request for 200 registers can
> > no
> > > > > longer reliably split it into multiple parts that yield the correct
> > > > value.
> > > > >
> > > > > What I understand of your S7 example (I do not know this device)
> > seems
> > > > like
> > > > > a device that offers a single value that exceeds the limits of
> modbus
> > > and
> > > > > thus I expect they made it so you can fetch it step by step.
> > > > >
> > > > > I'll see if I can do a wireshark dump for you.
> > > > >
> > > > > What should I make the issue say? I currently do not see this as a
> > bug
> > > or
> > > > > problem with plc4x.
> > > > >
> > > > > Niels
> > > > >
> > > > > On Sun, Jan 15, 2023 at 4:46 PM Christofer Dutz <
> > > > [email protected]>
> > > > > wrote:
> > > > >
> > > > >> Hi Niels,
> > > > >>
> > > > >> I think this might be related to what happens when reading Strings
> > in
> > > S7
> > > > >> without providing a length.
> > > > >> In this case each string is 255 charaters long and it already
> > exceeds
> > > > the
> > > > >> size-limit of 200 or so of a S7 1200.
> > > > >>
> > > > >> In S7 we use some code to split up multiple tags into multiple
> > > requests,
> > > > >> but rewriting the query to support automatic splitting of one
> single
> > > tag
> > > > >> into multiple requests is quite a bit more difficult.
> > > > >>
> > > > >> I thought you were reading multiple tags that in sum exceeded the
> > 125
> > > > >> registers and for that case simply something similar to the S7
> query
> > > > >> updater should also work for other protocols.
> > > > >>
> > > > >> Do I understand you correctly, that in your case you want to read
> > one
> > > > tag,
> > > > >> that is bigger?
> > > > >>
> > > > >> Chris
> > > > >>
> > > > >> From: Niels Basjes <[email protected]>
> > > > >> Date: Sunday, 15. January 2023 at 16:38
> > > > >> To: [email protected] <[email protected]>
> > > > >> Subject: [Modbus] Handling 'too large' blocks of registers
> > > > >> Hi,
> > > > >>
> > > > >> A few weeks ago some code of mine was merged to limit the number
> of
> > > > >> registers that can be requested in a single ModbusTag because
> asking
> > > for
> > > > >> more than 125 registers in a single request will always fail
> > (because
> > > of
> > > > >> the way modbus works).
> > > > >> https://github.com/apache/plc4x/pull/721
> > > > >>
> > > > >> One of the comments was asking if it can be automated in a generic
> > way
> > > > to
> > > > >> split a "too large" request into multiple smaller requests.
> > > > >> So If I ask for a block of 200 registers then plc4x would simply
> > split
> > > > it
> > > > >> into multiple requests (like 125 and 75 for example, or 100 and
> 100)
> > > and
> > > > >> afterwards merge the resulting registers of the two requests back
> > > into a
> > > > >> single block of 200 registers for the upstream application to
> > analyze.
> > > > >>
> > > > >> I said I would look into this and this is what I found while doing
> > > some
> > > > >> experimenting with my real solar converter.
> > > > >> This device uses the SunSpec standard for defining meaning to
> modbus
> > > > >> registers.
> > > > >>
> > > > >> My current conclusion at this point is that it is impossible to
> > handle
> > > > this
> > > > >> at the modbus level and I'm looking for you guys to challenge me
> in
> > > > this.
> > > > >>
> > > > >> Why do I say this?
> > > > >> One of the logical values you can retrieve is the name of the
> > > > Manufacturer
> > > > >> and the Model of the device that are both stored as UTF-8 in a set
> > of
> > > 16
> > > > >> registers (i.e. usually 32 characters).
> > > > >>
> https://github.com/sunspec/models/blob/master/json/model_1.json#L27
> > > > >>
> https://github.com/sunspec/models/blob/master/json/model_1.json#L36
> > > > >>
> > > > >> I found that if I try to fetch only a part of this logical value I
> > get
> > > > >> either an error (INVALID_ADDRESS) or bad data.
> > > > >> When I fetch the entire value I get the 16 registers which hold
> the
> > > > correct
> > > > >> data.
> > > > >>
> > > > >> Output of my test program that fetches the Model of the device
> > (which
> > > > is in
> > > > >> my case "SB3.6-1AV-41" ).
> > > > >> ModbusTag[4x40021:UINT[16]]: 0x5342 0x332E 0x362D 0x3141 0x562D
> > > 0x3431
> > > > >> 0x0000 0x0000 0x0000 0x0000 0x0000 0x0000 0x0000 0x0000 0x0000
> > 0x0000
> > > > >> ModbusTag[4x40021:UINT[15]]: INVALID_ADDRESS
> > > > >> ModbusTag[4x40022:UINT[15]]: 0xFFFF 0xFFFF 0xFFFF 0xFFFF 0xFFFF
> > > 0xFFFF
> > > > >> 0xFFFF 0xFFFF 0xFFFF 0xFFFF 0xFFFF 0xFFFF 0xFFFF 0xFFFF 0xFFFF
> > > > >>
> > > > >> So if I retrieve the correct block I get it.
> > > > >> If I try to get 1 register less than I should I get an error.
> > > > >> If I try to get the registers starting from the 2nd register I get
> > > only
> > > > >> 0xFFFF (important: NO error and a PlcResponseCode.OK !!)
> > > > >>
> > > > >> I expect there to be many other modbus devices that have similar
> > > effects
> > > > >> when the logical value requires multiple registers.
> > > > >>
> > > > >> So for now I come to the conclusion that fetching only part of the
> > > > >> registers that make up a logical variable in general will not work
> > and
> > > > (in
> > > > >> some cases) cannot be detected to have failed.
> > > > >>
> > > > >> At this point my assessment is that the only way to handle this is
> > by
> > > > >> actually knowing the meaning of the block of registers (i.e. which
> > > must
> > > > be
> > > > >> read together in a single read) and work from there.
> > > > >>
> > > > >> Note that the current SunSpec definition also has the concept of a
> > > > 'sync'
> > > > >> group of points (logical values that consist of 1 or more
> registers)
> > > > which
> > > > >> are grouped in the specification with the intent of "indicating
> > > > >> that the points in the group must be read and written atomically",
> > > which
> > > > >> effectively means you cannot read them individually from the
> modbus
> > > > >> standpoint.
> > > > >>
> > > > >> Looking for your feedback on this.
> > > > >> Do you know of existing software to generically handle this ?
> > > > >>
> > > > >> --
> > > > >> Best regards / Met vriendelijke groeten,
> > > > >>
> > > > >> Niels Basjes
> > > > >>
> > > > >
> > > > >
> > > >
> > >
> > >
> > > --
> > > Best regards / Met vriendelijke groeten,
> > >
> > > Niels Basjes
> > >
> >
>
>
> -- br/>Best regards / Met vriendelijke groeten, <
>
> Niels Basjes
>


-- 
Best regards / Met vriendelijke groeten,

Niels Basjes

Reply via email to