ottobackwards commented on code in PR #229:
URL: https://github.com/apache/plc4x-extras/pull/229#discussion_r1864435143


##########
plc4j/integrations/apache-nifi/nifi-plc4x-processors/src/main/java/org/apache/plc4x/nifi/BasePlc4xProcessor.java:
##########
@@ -301,17 +300,15 @@ protected void evaluateWriteResponse(final ComponentLog 
logger, Map<String, ? ex
                                if (tagsAtError == null) {
                                        tagsAtError = new ArrayList<>();
                                }
-                               logger.error("Not OK code when writing the data 
to PLC for tag " + tag 
-                                       + " with value  " + 
values.get(tag).toString() 
-                                       + " in addresss " + 
plcWriteResponse.getTag(tag).getAddressString());
+                               logger.warn("Not OK code when writing the data 
to PLC for tag {} with value {}", tag, values.get(tag));
                                
                        codeErrorPresent = true;
                        tagsAtError.add(tag);
                                                
                        }
                }
                if (codeErrorPresent) {
-                       throw new ProcessException("At least one error was 
found when while writting tags: " + tagsAtError.toString());
+            logger.warn("At least one error was found when while writting 
tags: {}" + tagsAtError);

Review Comment:
   You can do that, but the tests have to match?  or am I missing something?



-- 