If your homeplug adaptors are on opposing power line phases, then you may be able to get a vast improvement by making some minor changes to the wiring in your breaker panel.
To figure out if they're on the same phase, first identify the breakers for the outlets that the homeplug adaptors are connected to. Then measure with an AC voltmeter across two of those breakers*. If you get about 0V, they are on the same phase (good). If you get about 240V, they are on different phases. To change the phase that a circuit is on, swap it with the wire going to the breaker immediately below it. (miniature "dual" breakers count as the same breaker here). Swap wires as needed until all circuits powering homeplug devices measure 0V against each other. An electrician can do this for you in a few minutes. * you can also figure it out visually by counting spaces, but using a voltmeter is faster and more reliable. -- seanadams ------------------------------------------------------------------------ seanadams's Profile: http://forums.slimdevices.com/member.php?userid=3 View this thread: http://forums.slimdevices.com/showthread.php?t=50082 _______________________________________________ discuss mailing list [email protected] http://lists.slimdevices.com/lists/listinfo/discuss