David,

If you add ground rods, know that all ground rods should be tied back to the Utility ground rod by a large conductor (#6 wire is the minimum size). That is not only a requirement of NEC safety rules, but also a safety consideration for your station. All driven ground rods must be connected together unless the separation between the ground rods is 100 feet or more.

My own installation has grounds that are as much as 200 feet from the Utility Ground rod, but there are intermediate grounds that are less than 100 feet, so *all* are interconnected by large diameter conductors. This is primarily a consideration for AC fault conditions, but also part of my plan for lightning protection - perimeter wires around each building and all grounds interconnected with #6 or greater wire to give the charge from a lightning surge a large area to dissipate (hopefully without damage such as punching holes through the house foundation). All towers and masts are grounded to this system.

Your home safety demands that you tie all grounds together and tie into the utility ground system.

73,
Don W3FPR

On 4/16/2014 9:13 PM, David Cole wrote:
Hi Don,

Thank you for that info, I have powered everything, (except for the
amp), off a single largish UPS, that way the grounds are the same, and I
get a few minutes to kill power of the commercial power dies...

I will be adding a new ground rod to the house ground system, and
bonding that to the station ground later this week.

Thanks again for the info on grounds.

______________________________________________________________
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:[email protected]

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to [email protected]

Reply via email to