Your grounding plan sounds fine, *if* and only if you connect that
separate ground rod to the utility entrance ground rod using a #6 or #4
copper wire - that wire should be buried several inches and run outside
your dwelling foundation.
That connection is a NEC requirement and is necessary for safety. All
ground rods *must* be connected together unless they are more than 100
feet apart.
You cannot create an RF ground by connecting to a ground rod. It is
only for AC safety and a measure of lightning protection.
OCF antennas can be difficult to tame for RF in the shack. Use of a
very good quality common mode choke at the feedpoint (in addition to the
4:1 balun) may help.
73,
Don W3FPR
On 9/26/2015 1:41 PM, ae...@carolinaheli.com wrote:
The plan I'm thinking of so far.
1. Run an 8 gauge dedicated power feeder from my main panel (on the
opposite side of the house) to the shack with a 20A breaker. The 8Ga is to
lower ground losses.
2. Install a ground rod outside my shack and run a heavy gauge to the
shack to bond with the dedicated power line ground.
3. Ground all gear in the shack to the dedicated power ground.
4. ?? maybe do a run of 14-2 romex with all three leads bonded together up
to the mast, install a mast antenna switch and ground it with the 14-2.
______________________________________________________________
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net
This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to arch...@mail-archive.com