Mario. wrote:
> Well, that explains a lot. One option is to convert the D into
> floating point (or fixed point with a decimal), but with an integrator
> - FIR filter. You need a FIFO buffer where you put the D value, you
> sum all the values in the FIFO, and if necessary divide it by the size
> of the FIFO.
> 
> For starters, we may begin with 16, 32 or 64-entry FIFO.
Up to this point, you are correct.  But, even a 16 point pilter 
would be too much history.  I am thinking that a 4-stage filter 
might be quite adequate to damp out the half-sampling rate noise.
  Just one
> rolling pointer and 16-entry table should do a lot. (similar to analog
> D/A converter)
> 
> The most sensitive input on a PID is the D term, so solving this is
> very important.
Yes.

Jon

-------------------------------------------------------------------------
This SF.net email is sponsored by: Microsoft
Defy all challenges. Microsoft(R) Visual Studio 2005.
http://clk.atdmt.com/MRT/go/vse0120000070mrt/direct/01/
_______________________________________________
Emc-developers mailing list
[email protected]
https://lists.sourceforge.net/lists/listinfo/emc-developers