Fred:
     
     The IEC 801-2 standard specifically details how the EUT is to be 
     placed for testing.  The ground coupling planes are connected to earth 
     ground differently for the 1984 and 1991 versions of IEC 801-2.  The 
     1984 standard includes only a horizontal coupling plane connected 
     directly to earth ground.  The 1991 version adds a vertical coupling 
     plane, and both are connected to earth ground through two in line 
     resistors of 470 kOhms by separate wires.  In either case, the test 
     setup calls out distances between the EUT and the coupling planes and 
     should remain consistent from test house to test house for the same 
     version of the standard.
     
     If I understand your situation correctly, the connection to ground 
     that you are referring to is how your equipment (the EUT) is grounded. 
     I believe that the standard states that the EUT shall be configured 
     per the manufacturer's instructions/specifications.  Therefore, if you 
     specify that the EUT may be connected to no earth ground, an external 
     ground stud, or some other way, it should comply with each possible 
     configuration (or the worst possible configuration).
     
     In my experience, I have seen equipment fail the ESD test when the 
     ground was being supplied through an I/O cable from support equipment 
     and pass once this cable was removed.  As you stated, the ESD will 
     look for the shortest path to ground.  Therefore, grounding the metal 
     case of the EUT directly to earth ground (AC ground or ground stud) in 
     most cases will be better than a ground path that will travel through 
     some of your circuitry.  However, it is also possible to have a 
     non-conductive enclosure that may not accept the discharge.
     
     Just my two cents worth.  Good luck.
     
     Ken Shadoff
     
     The above opinions are my own.


______________________________ Reply Separator _________________________________
Subject: IEC801-2
Author:  Fred Waechter <[email protected]> at ~internet
List-Post: [email protected]
Date:    12/9/96 12:06 PM


This is in relation to testing a Class II, 2 wire system to the European 
IEC801-2 electrostatic discharge requirements.
     
The system is used in an environment that may have no earth ground, or 
earth may be tied back at the substation, or earth may be tied at 
multiple points along the AC neutral, or an earth ground rod me be 
available at the users end installation.
     
On application of an ESD pulse to this system, the energy in the ESD 
pulse will try to find the shortest path to earth ground.
     
1. Is there a preferred test method to insure conformity of testing 
between test laboratories, and also the users end installation as their 
methods of earthing may certainly differ?
     
2. Would different methods of earthing result in differing results due 
to differing amounts of system discharge before the next ESD pulse is 
applied to the system?
     
These questions were prompted by  results obtained at two different test 
laboratories.
     
The systems passed when tested at an independent test lab. in Taiwan. 
The same units failed when tested by a lab. in the U.S.
     
Thanks for your help.
     

Reply via email to