Fred:
You are correct.  Its just one of the many glitches in the standard.  Column 
one applies until the maximum is reached where ever that might be.

There is a committee draft out for comment which takes the limit above 1000 
Watts for professional equipment.  It also clarifies the definition of 
professional equipment.

Dave George
Unisys
 ----------
From: owner-emc-pstc
To: emc-pstc discussion group
Subject: IEC1000-3-2
List-Post: [email protected]
Date: Wednesday, November 27, 1996 12:31PM

Return-Path: <[email protected]>
Received: from trsvr.tr.unisys.com by trpo1.tr.unisys.com id
    <[email protected]>; Wed, 27 Nov 96 15:12:39 EST
Received: from bbmail1.unisys.com by trsvr.tr.unisys.com (8.6.12/8.6.12) id
    UAA19463 ; Wed, 27 Nov 1996 20:05:56 GMT
Received: from ruebert.ieee.org (ruebert.ieee.org [199.172.136.3]) by
    bbmail1.unisys.com (8.7.3/8.6.12) with ESMTP id UAA16806; Wed, 27 Nov 
1996
    20:13:43 GMT
Received: (from daemon@localhost) by ruebert.ieee.org (8.7.5/8.7.3) id
    MAA08679 for emc-pstc-list; Wed, 27 Nov 1996 12:35:58 -0500 (EST)
Message-Id: <[email protected]>
List-Post: [email protected]
Date: Wed, 27 Nov 1996 12:31:31 -0800
From: Fred Waechter <[email protected]>
Organization: SMPS Consulting
X-Mailer: Mozilla 3.0Gold (Win16; U)
Mime-Version: 1.0
To: emc-pstc discussion group <[email protected]>
Subject: IEC1000-3-2
Content-Type: text/plain; charset=us-ascii
Content-Transfer-Encoding: 7bit
Sender: [email protected]
Precedence: bulk
Reply-To: Fred Waechter <[email protected]>
X-Resent-To: Multiple Recipients <[email protected]>
X-Listname: emc-pstc
X-List-Description: Product Safety Tech. Committee, EMC Society
X-Info: Help requests to  [email protected]
X-Info: [Un]Subscribe requests to  [email protected]
X-Moderator-Address: [email protected]
 ----------------------------------------------------------------------------  
 --
I am trying to understand the IEC1000-3-2 standard.

My equipment is classified as Class D.

Table 3 - Limits for Class D Equipment, has two columns for the limits,
one is maximum harmonic current per watt and the other is maximum
permissible harmonic current. The two columns don't appear to agree.

Since the maximum input power for Class D equipment is 600W, should the
maximum permissible harmonic current for the third harmonic not be
600x.0034 or 2.04A?  The table gives a maximum limit of 2.30A. The only
harmonic that agrees with my interpretation is the fifth. All the rest
are higher than when doing the calculation.

Am I missing something?

I do not have a copy of EN61000-3-2, what is the difference between the
two standards?

Thanks for you help.

Fred Waechter
SMPS Consulting
[email protected]

Reply via email to